It's -22C outside and the chiller and DX systems are operating? The heat 
should be on, not the cooling systems. What type of zone is served by 
these cooling systems where cooling is needed on such a cold day? What's 
the zone temps? Have you changed the example file in any way?

jai191 wrote:
>
> I am getting the following errors when running the DOE benchmark files
> for Secondary School. Any suggestions!
>
> Warning ** CHILLER:ELECTRIC:EIR "COOLSYS1 CHILLER": Air Cooled
> Condenser Inlet Temperature below 0 C warning continues...
> ************* ** ~~~ ** Max=-2.775558E-017 Min=-22.8
> ************* ** Warning ** Coil:Cooling:DX:SingleSpeed "PSZ-
> AC_4:8_COOLC DXCOIL" - Low condenser dry-bulb temperature error
> continues...
> ************* ** ~~~ ** Max=-1.110223E-016 Min=-21.1
> ************* ** Warning ** Coil:Cooling:DX:SingleSpeed "PSZ-
> AC_2:6_COOLC DXCOIL" - Low condenser dry-bulb temperature error
> continues...
> ************* ** ~~~ ** Max=-0.1 Min=-21.1
>
> Thank You!
> Jay
>
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/