[EnergyPlus_Support] HVAC capacity - autosize and fixed



 

Dear all,

 

We noticed that the HVAC capacity is changing according to different COP by using the autosize option for Cooling Coil Capacity. For example, for the same HVAC: if the COP is 2,94 the result  in the eio file for the total capacity  is 62726Watts and, if that cop is decreased to 2,39 the capacity becomes 94906Watts.

 

Then, we tried to fix the capacity to change only the COP value. But we got a severe error:

Sizing: COIL:DX:COOLINGBYPASSFACTOREMPIRICAL "AC_ZN_1 COOLING COIL": Rated air volume flow rate per watt of rated total cooling capacity is out of range.

 

We also tried to put the minimum, average and maximum value of rated air volume rate (times the capacity as required) but we got the same severe error.

 

Our questions are:

-          Why the capacity is changing according to cop? Should not it be according to zone loads and design days??

-          If no rated air volume flow is accepted, how do we use the HVAC Cooling Coil Capacity without autosize option?

 

Thanks,

Labeee team.



__._,_.___


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___