I think the "reheat" element is originally associated with cooling for humidly control, and should be reserved for that use, if possible. The other heat exchanger is "pre-heat" coil for heat recovery from the relief air.. Heating coil and Re-heat coil do not normally used together. A fan coil unit may have an auxiliary heating element in the terminal for use during season change over period, especially in the two pipe fan-coil system. (example FanCoilVAV:Reheat) This is where the word re-heat coil may not be so good. In my Condo., when the heating is off at the end of Spring, before the cooling comes on in Summer, the heater provide heating at unusual cold nights. For humidity control, the re-heat coil may be installed upstream at the AHU, during the cooling period. The heater for use with heat pump in Winter is called the supplementary heater in EPlus. There are crankcase heater and sump heater as well, for the compressor. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: wfbuhl@xxxxxxx Date: Tue, 31 Mar 2009 13:51:35 -0800 Subject: Re: [EnergyPlus_Support] problem about reheat coil and heating coil
"Reheat coil" (kind of a bad name) is simply a heating coil in a
terminal unit. Its action affects a single thermal zone. A "heating coil" is in the central air duct and affects all of the supply air. It is upstream from the reheat coils. The "reheat coil" is controlled by the zone thermostat. The "heating coil" is controlled by the supply air temperature setpoin and the heating coil controller. Fred Buhl yangchen19851226 wrote: > What is the difference of reheat coil and heating coil in VAV system?Which device is in the upstream? > > > > ------------ > > The primary EnergyPlus web site is found at: > http://www.energypl > > The group web site is: > http://groups. > > Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site. > > EnergyPlus Documentation is searchable. Open EPlusMainMenu. > Yahoo! Groups Links > > > > Internet Explorer 8 makes surfing easier. Get it now! __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |