Hi Pregas,
Yes and No. E+ cannot size the ground loop in its current capabilities, but it can simulate the performance of one. E+ ground loop simulation is based on "g-function" model and thus requires user to provide the g-function (basically the step thermal response of the borehole) and other soil, fluid properties. E+ provides a library of g-functions of common borefield types, but if you have a complicated or a huge borefield you might consider developing custom g-functions using a commercial software. There are publications (theses and articles) from Oklahoma State University that discusses the model in detail.
Good luck.
Sankar
Pregas Srinivasan wrote:Hi,
I am designing and analyzing a geothermal closed loop vertical pipes system. My company uses Trace, but it doesnt have the capacity to calculate the geothermal pipe length and simulate the conditions based on the soil characteristics. I was wondering if energy plus can do such analysis? Any inputs/help is appreciated.
Thanks
Pregas Srinivasan
Thompson Consulting engineers,
Newport News, VA
--
Sankar Padhmanabhan
Graduate Research Assistant
Ph.D Student Mechanical & Aerospace Engg
Oklahoma State University,
Stillwater, OK-74078
Ph:405-744-2410 (O)
__._,_.___
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
![]()
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe
__,_._,___