[EnergyPlus_Support] Surface heat flux interpretation



Hello,

Looking to a surface heat transfer I can't understand how heat flux is computed.

In Winter Design Day calc (T out = -3.1°C, T int = 22°C).
The U value surface-to-surface is 1 (one layer with a R=1 material only). My wall is 82.07 m2.

Convection algorithms are Simple for interior and exterior. I set no wind so that U convection int and out are those expected (Uc int = 3.076, Uc out = 8.23). At surface level output show me these values.

Now if I try to manually calculated heat transfer using convection given by outputs I can't get the Heat loss calculated by E+.
E+ give me 1194 W when I find 1434 W.

Where am I wrong?
May be this formula is not complete, does E+ uses another equation?
Heat = U-value-with-film x Surface x (T int - T out)

Thanks for any tip




------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/