Re: [EnergyPlus_Support] Radiant Cooling





Check the eso file (in xESOview) to see where the shutoff is occurring and what the corresponding humidity is, temperature of the radiant surface, etc.  You should be able to adjust the temperature and/or flow rate settings in the low-temp radiant system object to avoid getting too cold.
David


On Fri, Apr 24, 2009 at 12:59 PM, L Herrmann <l.herrmann@xxxxxxxxxxxxxx> wrote:


Hello; I am trying to run a model that uses radiant heating and cooling.  During the cooling months, the radiant system incounters a reoccuring error.  The radiant surface temperature drops below the due-point temperature and condensation occurs.  I believe the radiant system is automatically shutting itself off.  Here is the warning statement:
 
Warning ** Surface temperature below dew-point temperature--potential for condensation exists
   **   ~~~   ** Flow to the following radiant system will be shut-off to avoid condensation
   **   ~~~   ** Hydronic Radiant System Name = RESISTIVE ZONE RADIANT FLOOR
   **   ~~~   ** Predicted radiant system surface temperature = 18.30
   **   ~~~   ** Zone dew-point temperature= 17.48
   **   ~~~   **  Occurrence info=CHICAGO IL USA TMY2-94846 WMO#=725300, 04/03 14:40 - 14:50
   **   ~~~   ** Note that there is a 1.00 C safety built-in to the shut-off criteria
   **   ~~~   ** Note also that this affects all surfaces that are part of this radiant system
 
Radiant systems are complicated and envolve a lot of engineering skill... can anyone offer advice into this condensation proplem??
 
 
Here is another warning that I am getting for days in May and June:
 
 ** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at CHICAGO IL USA TMY2-94846 WMO#=725300, 05/05 15:00 - 15:10
   **   ~~~   ** ...use Output:Diagnostics,DisplayExtraWarnings;   to show more details on each max iteration exceeded.
   ** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at CHICAGO IL USA TMY2-94846 WMO#=725300, 05/05 15:00 - 15:02
 
What does this mean?
 
Thanks!
Lesley




__._,_.___


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___