Re: [EnergyPlus_Support] Re: how to do weather file simulation



The input for Do the design day simulation determines if the DesignDay 
objects are simulated.
The input for Do the weather file simulation determines if the RunPeriod 
objects are simulation.

The other 3 inputs for Do the ??? sizing calculations... are used to 
autosize equipment for zone, system, or plant. Zone is used for zone 
equipment (window AC, baseboards), System is used primarily for air 
loops, and plant is used to size chilled, hot water, and condenser loops.

If an input in an object (e.g. Pump) has "autosize", this means that the 
simulation will automatically size this equipment based on the sizing 
object inputs (Zone Sizing and System Sizing objects).
If an input in an object has a value (e.g., 0.5), this means the 
simulation will use this value during the simulation and sizing will not 
be performed on this object.

If you want to autosize equipment, find an example file which specifies 
"autosize" as an objects input and see which other objects are used to 
size the equipment.
Also read the documentation for the Zone Sizing and System Sizing objects.

This help forum (Yahoo group) is more for user-to-user help where the 
general public that uses EnergyPlus will try to answer your questions 
and help you with your simulation
A more useful help system has been set up to answer your questions by 
the core developers of EnergyPlus. Questions should be sent to this help 
system when other users of EnergyPlus can not answer your questions on 
the Yahoo group. The email address is: energyplus-support@xxxxxxxx


yangchen19851226 wrote:
>
>
> You mean the four options should be set to yes except design day 
> simulaton.But the examples incorporated in the example file which do 
> the weather file simulation have characters ,that is,air flow rates 
> and for the program to use these results to automatically size the 
> HVAC components a number of input objects must be present and certain 
> object input fields must be entered.
> Can you explain to me.
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx 
> <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad 
> <RRaustad@...> wrote:
> >
> > Set the last of the "other two options" in the Run Control object to 
> YES.
> >
> > RUN CONTROL,
> > Yes, Do the zone sizing calculation
> > Yes, Do the system sizing calculation
> > Yes, Do the plant sizing calculation
> > No, Do the design day simulations
> > Yes; Do the weather file simulation
> >
> >
> > yangchen19851226 wrote:
> > >
> > >
> > > Hi,
> > > I have some questions to ask.In the run control object,the first 
> three
> > > options are for sizing simulation.In my case,these sizing options 
> were
> > > set to yes,the other two options were set to no,the simulation 
> results
> > > made me puzzled because I can only get zone sizing and system sizing
> > > datas.
> > > If I have got the plant sizing results and zone sizing results.How 
> can
> > > I run the weather file simulation?
> > > Looking for your help.
> > >
> > > Regards
> > >
> > >
> >
> > --
> > Richard A. Raustad
> > Senior Research Engineer
> > Florida Solar Energy Center
> > University of Central Florida
> > 1679 Clearlake Road
> > Cocoa, FL 32922-5703
> > Phone: (321) 638-1454
> > Fax: (321) 638-1439 or 1010
> > Visit our web site at: http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> >
> > UCF - From Promise to Prominence: Celebrating 40 Years
> >
>
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/