I have had a look at your file posted to
Helpserve. There are so many problems with this file I am surprised it runs at
all, but not surprised it runs differently in V2.2. First, the geometry is inside out.
You have chosen UpperLeftCorner, and CounterClockWise, but then entered the
surface vertex data in clockwise order. Your zone loads are going to be
totally wrong. One problem is that the supply side
"Riscaldamento supply ingresso" branch has too much equipment on
it. The first branch on the supply side of a plant loop should have only
a pump. Yours has pump, waterheater, and a pipe. You need to
rearrange this loop to have just the pump on the supply side inlet, then the
water heater with a bypass around it, and then boiler on a single flow branch
after the water heater. The problem with the node temperature
results after the CHP are likely because your bypass branch has control type
"passive" when it should be "Bypass." The branch "Motore demand WH"
for the water heater's source side needs to have "ACTIVE" branch
control so it can make flow requests. From:
thank you for your answer, __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |