Re: [EnergyPlus_Support] creating 'real' weather files - Wind/solar data
Arslan,
> Please take a look at page three of the attached document and under
> the section "Solar and Shading Calculations" you'll find that E+
> calculates all the radiation values needed from your location and
> geometry input.
I beg to differ. E+ calculates the "plane-of-array" irradiance using the
Perez model. But its inputs are the direct and diffuse horizontal
irradiances, which need to be known beforehand.
Paul,
< I have found some wind/solar data for local weather stations, but there are problems, like the solar data was only recorded until the start of 2007, and the diffuse horizontal radiation has been recorded at zero for the whole year, and i cannot seem to find out if this is a real measurement, or that it has not been measured.
Diffuse must be strictly positive any day, so these are missing values...
There was a recent thread on how to obtain "real" radiation/weather
data, which you should check.
Chris
--
Chris A. Gueymard, PhD
Solar Consulting Services
P.O. Box 392
Colebrook, NH 03576, USA
Tel. (603) 237-8550
Fax (603) 237-5314
http://www.SolarConsultingServices.com
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/