Re: [EnergyPlus_Support] Unitary heat pump: Air to Air



Check the eio file for sizing of the PTHP.
The DX heating coil is probably sized sufficient to meet the load.
If the DX heating coil is not operating, check the Minimum Outdoor 
Dry-Bulb Temperature for Compressor Operation input in the PTHP object 
and see if that is causing the DX heating coil to not operate
If the DX heating coil is operating, check the Total Heating Capacity 
Function of Temperature Curve to make sure it represents the 
manufacturers performance data.

Rashmi Sonal wrote:
>
>
> Hi,
>
>  
>
> I am modelling a building in Boston with packaged terminal heat pumps.
>
> The default option to size the heatpump is based on zone cooling load 
> and there is a supplemental electric heating coil along with heatpump 
> heating coil.
>
>  
>
> The rooms are way below set point if I turn off the supplemental 
> heating coil. Is there a way I can size the heatpump based on zone 
> heating load ?
>
>  
>
> Thanks in advance,
>
> Sonal
>
>  
>
> Rashmi Sonal, LEED AP
>
> Environmental Designer
> Computational and Simulation Analysis (CoSA)
> www.burohappold.com <http://www.burohappold.com>
>
> Tel: (+1) 212 616 0285
>
> This transmission is confidential and intended solely for the person 
> or organization to whom it is correctly addressed. If you are not the 
> intended recipient of this transmission, you should not take any 
> action in reliance on it. Further, this transmission may contain 
> confidential design and other information owned by Buro Happold 
> Consulting Engineers PC. You should not copy, distribute, use, offer 
> for sale or hire such information or in any way infringe the design 
> and intellectual property rights of Buro Happold Consulting Engineers 
> PC. It is intended that communication by email from Buro Happold 
> Consulting Engineers PC or its employees is limited to communications 
> connected to the services provided by Buro Happold Consulting 
> Engineers PC. Buro Happold Consulting Engineers PC accepts no 
> liability for any communications not connected to the services it 
> provides. Computer viruses may be transmitted or downloaded onto your 
> computer system via email communication. It is the recipient's 
> responsibility to take any action necessary to prevent computer 
> viruses being transmitted in this way. Accordingly, Buro Happold 
> Consulting Engineers PC disclaims
>
>
>
> This message has been scanned by MailController 
> <http://www.mailcontroller.altohiway.com/>.
>
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/