[EnergyPlus_Support] No cooling setpoint -- still warnings and unmet hours



I have zones that are heating only zones with convective baseboard heating only. i am using control type 1 with a single heating setpoint but I am getting unmet hours and warnings about there being zero cooling load.

What am i missing here? are these warning normal because of the zone sizing runs? How can I eliminate un-met hours? see idf clip below.

ZoneControl:Thermostat,
    GF_stair Thermostat,!- Name
    Gf_Stair,!- Zone Name
    HVACTemplate-Always 1,!- Control Type Schedule Name
    ThermostatSetpoint:SingleHeating,!- Control 1 Object Type
    Unnoccupied Heating Only Thermostat Control;!- Control 1 Name


ThermostatSetpoint:SingleHeating,
    Unnoccupied Heating Only Thermostat Control,
    Unoccupied Heating Only Heating SP Sch;

Sizing:Zone,
    Gf_Stair,!- Zone Name
    14,!- Zone Cooling Design Supply Air Temperature {C}
    33,!- Zone Heating Design Supply Air Temperature {C}
    0.008,!- Zone Cooling Design Supply Air Humidity Ratio 
    0.008,!- Zone Heating Design Supply Air Humidity Ratio 
    Flow/Person,!- Outdoor Air Method
    0.007,!- Outdoor Air Flow per Person {m3/s}
    0.0,!- Outdoor Air Flow per Zone Floor Area {m3/s-m2}
    0.0,!- Outdoor Air Flow per Zone {m3/s}
    ,!- Zone Sizing Factor
    DesignDay,!- Cooling Design Air Flow Method
    0,!- Cooling Design Air Flow Rate {m3/s}
    ,!- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2}
    ,!- Cooling Minimum Air Flow {m3/s}
    0,!- Cooling Minimum Air Flow Fraction
    DesignDay,!- Heating Design Air Flow Method
    0,!- Heating Design Air Flow Rate {m3/s}
    ,!- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}
    ,!- Heating Maximum Air Flow {m3/s}
    0;!- Heating Maximum Air Flow Fraction





------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/