[EnergyPlus_Support] Re: Cross Mixing Ventilation



I confirm it's a limitation of Cross Mixing. One zone couldn't have two Cross Mixing objects. 

I think you could use ZoneMissing objects (with equal design flow rate) to remplace them.

Camille T. 

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "marziasedino" <marziasedino@...> wrote:
>
> 
> Dear all,
> 
> I am modeling natural ventilation within an atrium (three storeys high) by defining three thermal zones one on top of the other and connecting them with the Cross Mixing module.
> I defined the Cross Mixing for each zone (I tried to define it both once and twice, as my delta T is 0) but I get the following error message:
> 
> "GetSimpleAirModelInputs: Overlapping Cross Mixings found
> Cross Mixing with receiving zone 15191, source zone 11832
> overlaps with Cross Mixing with receiving zone 15191, source zone 16416"
> 
> It seems that E+ doesn't like the fact that a zone is named twice in the Cross Mixing Module. But this is the only way I can define the fact that each zone is connected, i.e.
> zone 1 mixes with zone 2 and vice versa
> zone 2 mixes with zone 3 and vice versa
> 
> Is it a limit of the Cross Mixing feature or am I messing wth something?
> 
> thanks a lot
> 
> Marzia
>




------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/