Re: [EnergyPlus_Support] Simulation using HVAC Template with Reheat and Humidity Control
The heating.reheat coil does not have enough capacity. You have
specified 0.45 W. I changed the heating/reheat coil capacity to be as
large as the cooling coil capacity and it worked much better. Keep in
mind that when the zone moisture load is greater than the cooling coil's
latent capacity, the zone RH.will rise above the humidity set point and
a larger coil will be required.
Your file:
HVACTemplate:System:Unitary,
6200, !- Cooling Coil Capacity {W}
0.45, !- Heating Coil Capacity {W}
Corrected file:
HVACTemplate:System:Unitary,
6200, !- Cooling Coil Capacity {W}
6200, !- Heating Coil Capacity {W}
Abdul Murad Zainal Abidin wrote:
>
> Hello,
>
> I am in need of a kind assistance from anybody regarding my
> simulation. I have tried using HVAC Template for unitary system using
> reheat. My intention is to control the zone conditions at 24 deg C and
> 55 to 60% relative humidity. The HVAC system is using 100% fresh air
> and will be fully extracted. I am still unable to get the relative
> humidity constant and the reheat coil is not functioning. Attached is
> my input file. Am I missing something, or lots of things?
>
> Thank you for reading.
>
> Murad
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/