Not that this will make any difference in your simulation, but the size 
of the reheat coil only needs to be equal to or slightly greater than 
the cooling coil's SENSIBLE capacity. Sensible capacity is equal to 
Total Cooling Capacity * SHR. So in your case that means 6200 W * 0.64 = 
3968 W. In the HVAC template the heating coil and reheat coil are sized 
with the HVAC Template Heating Coil Capacity input, so as long as you do 
not need more than 3968W for heating, then you can size the reheat coil 
as low as 3968 W. This does not mean you will need a reheat coil of that 
size, it simply means it is a good place to start. You can check the 
reheat coil output after the simulation is complete to see what maximum 
reheating capacity is required.

Richard Raustad wrote:
> The heating.reheat coil does not have enough capacity. You have 
> specified 0.45 W. I changed the heating/reheat coil capacity to be as 
> large as the cooling coil capacity and it worked much better. Keep in 
> mind that when the zone moisture load is greater than the cooling 
> coil's latent capacity, the zone RH.will rise above the humidity set 
> point and a larger coil will be required.
>
> Your file:
> HVACTemplate:System:Unitary,
>    6200,                    !- Cooling Coil Capacity {W}
>    0.45,                    !- Heating Coil Capacity {W}
>
> Corrected file:
> HVACTemplate:System:Unitary,
>    6200,                    !- Cooling Coil Capacity {W}
>    6200,                    !- Heating Coil Capacity {W}
>
>
> Abdul Murad Zainal Abidin wrote:
>>  
>> Hello,
>>  
>> I am in need of a kind assistance from anybody regarding my 
>> simulation. I have tried using HVAC Template for unitary system using 
>> reheat. My intention is to control the zone conditions at 24 deg C 
>> and 55 to 60% relative humidity. The HVAC system is using 100% fresh 
>> air and will be fully extracted. I am still  unable to get the 
>> relative humidity constant and the reheat coil is not functioning. 
>> Attached is my input file. Am I missing something, or lots of things?
>>  
>> Thank you for reading.
>>  
>> Murad
>>
>> 
>

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/