Hi, Murad The crash was caused by a divide by zero error. MaterialProperty:HeatAndMoistureTransfer:Settings, Polyurethane, !- Material Name 0.0001, !- Porosity {m3/m3} 0.2; !- Initial Water Content Ratio {kg/kg} I changed the Porosity from zero to 0.0001, and the program did not crash. There are still some warnings. Timestep should be set to 4. One of the schedule is not complete in the days. Schedule:Compact, LIGHTS, !- Name Fraction, !- Schedule Type Limits Name Through: 12/31, !- Field 1 For: WeekDays SummerDesignDay CustomDay1 CustomDay2, !- Field 2 Until: 8:00, 0.05, !- Field 4 Until: 9:00, 0.9, !- Field 6 Until: 10:00, 0.95, !- Field 8 Until: 11:00, 1.00, !- Field 10 Until: 12:00, 0.95, !- Field 12 Until: 13:00, 0.8, !- Field 14 Until: 14:00, 0.9, !- Field 16 Until: 18:00, 1.00, !- Field 18 Until: 19:00, 0.60, !- Field 20 Until: 21:00, 0.40, !- Field 22 Until: 24:00, 0.05; !- Field 24 You can either complete the other four day types or change it to - For: AllDays. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: zabdulmurad@xxxxxxxxx Date: Fri, 31 Jul 2009 16:14:13 +0000 Subject: [EnergyPlus_Support] Simulation Crashed Using Double Brick Wall with Polyurethane insulation Hello,
I am having a problem with my simulation using HAMT for double brick wall with polyurethane insulation sandwiched between. Simulations using other construction details such as aerated concrete and single red brick wall were found to be normal. Is there something wrong with the properties of the materials, or is there a problem with HAMT in dealing with multi-layered wall?
I have attached the input file in the hope that anyone could assist me.
Thank you for reading.
Murad Send and receive email from all of your webmail accounts - right from your Hotmail inbox! __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |