[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] heating and cooling load



The error means you are writing two set points to the same node. The 
second SP manager will overwrite the data posted by the first SP 
manager. What are you controlling with these set point managers? I don't 
even see a zone inlet node named one or two?? You should delete these if 
you don't need them.

  SetpointManager:SingleZone:Heating,
    heat,                    !- Name
    Temperature,             !- Control Variable
    -99,                     !- Minimum Supply Air Temperature {C}
    99,                      !- Maximum Supply Air Temperature {C}
    Rinker building office,  !- Control Zone Name
    one,                     !- Zone Node Name
    two,                     !- Zone Inlet Node Name
    zone node;               !- Setpoint Node or NodeList Name
 
  SetpointManager:SingleZone:Cooling,
    cooling,                 !- Name
    Temperature,             !- Control Variable
    -99,                     !- Minimum Supply Air Temperature {C}
    99,                      !- Maximum Supply Air Temperature {C}
    Rinker building office,  !- Control Zone Name
    one,                     !- Zone Node Name
    two,                     !- Zone Inlet Node Name
    zone node;               !- Setpoint Node or NodeList Name


Hu Jia wrote:
>  
>
> Hi, everyone,
>
> I posted my heating and loading problem in my last message. For your
> convenience, I have uploaded the input file to Yahoo Group: File :
> /_Problem_Submittals/heating and cooling loads.zip.
> You can access this file at the URL:
> http://groups.yahoo.com/group/EnergyPlus_Support/files/_Problem_Submittals/heating%20and%20cooling%20loads.zip 
> <http://groups.yahoo.com/group/EnergyPlus_Support/files/_Problem_Submittals/heating%20and%20cooling%20loads.zip>
>
> Besides, when I run it, there are several warnings for this input
> file. Could anyone help me how to deal with this warning as follows?
>
> ** Warning ** SetpointManager:SingleZone:Heating "HEAT"
> ** ~~~ ** ...set point node conflicts with another set point manager.
> ** ~~~ ** ...conflicting set point manager =
> SetpointManager:SingleZone:Cooling "COOLING"
> ** ~~~ ** ...conflicting node name = ONE
> ** ~~~ ** ...control type variable = Temperature
> ** Warning ** SetpointManager:SingleZone:Heating "HEAT"
> ** ~~~ ** ...set point node conflicts with another set point manager.
> ** ~~~ ** ...conflicting set point manager =
> SetpointManager:SingleZone:Cooling "COOLING"
> ** ~~~ ** ...conflicting node name = TWO
> ** ~~~ ** ...control type variable = Temperature
>
> Thank you all.
>
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/