Re: [EnergyPlus_Support] heating and cooling load



If the PTAC fan is moving air, the Packaged Terminal Air Conditioner 
Sensible Zone Heating Rate should not be 0. Check the fan operating mode 
(constant fan or auto fan) and also check to see what the zone 
temperature is with respect to the zone temperature set point.

Hu Jia wrote:
>  
>
> Hello, everyone:
>
> I want to simulate the heating and cooling loads of an office to see
> how the window blinds affect the heating or cooling loads. I choose a
> PTAC (Packaged Terminal Air Conditioner) in the HVAC
> Templates:Zone:PTAC object. For Thermostatsetpoint:Dual point is 24
> and 20, respectively.
>
> In the ouput file, I select some variables related to heating and
> cooling loads, for example, Zone/Sys Sensible Heating Rate [W],
> :Zone/Sys Sensible Load Predicted [W], Packaged Terminal Air
> Conditioner Sensible Zone Heating Rate[W]. From the manual document,
> because only PTAC is used in the zone, I initially think that the
> three should be equal.
>
> But for some days, Zone/Sys Sensible Load Predicted [W] is 0, and
> Packaged Terminal Air Conditioner Sensible Zone Heating Rate[W] is
> 9.525853, which is not equal to Zone/Sys Sensible Heating Rate [W].
>
> Can anyone explain the relationship of the three variables for me?
>
> Thank you.
>
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/