If the PTAC fan is moving air, the Packaged Terminal Air Conditioner
Sensible Zone Heating Rate should not be 0. Check the fan operating mode
(constant fan or auto fan) and also check to see what the zone
temperature is with respect to the zone temperature set point.--
Hu Jia wrote:
>
>
> Hello, everyone:
>
> I want to simulate the heating and cooling loads of an office to see
> how the window blinds affect the heating or cooling loads. I choose a
> PTAC (Packaged Terminal Air Conditioner) in the HVAC
> Templates:Zone:PTAC object. For Thermostatsetpoint:Dual point is 24
> and 20, respectively.
>
> In the ouput file, I select some variables related to heating and
> cooling loads, for example, Zone/Sys Sensible Heating Rate [W],
> :Zone/Sys Sensible Load Predicted [W], Packaged Terminal Air
> Conditioner Sensible Zone Heating Rate[W]. From the manual document,
> because only PTAC is used in the zone, I initially think that the
> three should be equal.
>
> But for some days, Zone/Sys Sensible Load Predicted [W] is 0, and
> Packaged Terminal Air Conditioner Sensible Zone Heating Rate[W] is
> 9.525853, which is not equal to Zone/Sys Sensible Heating Rate [W].
>
> Can anyone explain the relationship of the three variables for me?
>
> Thank you.
>
>
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
__._,_.___
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
![]()
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe
__,_._,___