When autosizing it is best to autosize all inputs that can be autosized. Yes it OK to autosize select inputs, but these type of errors may occur. Look at the eio file and find the autosized air flow rate for the Coil:Heating:DX:SingleSpeed OFFICE N PTHP HEATING COIL. Then calculate the Rated air volume flow rate per watt of rated total heating capacity based on your entered capacity to see how far out of range you are. Since the PTHP is zone equipment, you should use the actual flow rate for each zone to calculate the capacity for each PTHP unit. Or you could manually enter the air flow rate for each PTHP unit to avoid this error. tobias.leibing wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.