Re: [EnergyPlus_Support] Specificaton of PTHP Units





When autosizing it is best to autosize all inputs that can be autosized. Yes it OK to autosize select inputs, but these type of errors may occur. Look at the eio file and find the autosized air flow rate for the Coil:Heating:DX:SingleSpeed OFFICE N PTHP HEATING COIL. Then calculate the Rated air volume flow rate per watt of rated total heating capacity based on your entered capacity to see how far out of range you are. Since the PTHP is zone equipment, you should use the actual flow rate for each zone to calculate the capacity for each PTHP unit. Or you could manually enter the air flow rate for each PTHP unit to avoid this error.

tobias.leibing wrote:
 

Hi there,

I've got a question about the PTHP-Units.
So far, I did several simulation runs, I've simulated the model completely on autosizing and wanted to implement step by step the given design values afterwards.
However, encountered problems when I specify the COPs and capacities of the units but leave the flow rates on autosize.

The error-message in this case is as follows:

** Severe ** Coil:Heating:DX:SingleSpeed OFFICE N PTHP HEATING COIL: Rated air volume flow rate per watt of rated total heating capacity is out of range. See Input-Output Reference Manual for valid range.

If I check the Input-Output Reference Manual it says in the section for the DX Cooling Coil, that "the rated air volume flow rate should be between 0.00004027 m3/s and 0.00006041 m3/s per watt of rated total cooling capacity" (s.p. 1216).
Now, what I'v did, was using the upper value for two zones, multiplied by the design capacity, and I still have the same error message for those two zones.

What else could be the problem for this?

What are the necessary specs for a PTHP unit and which values can I leave on autosize?

Your help is greatly appreciated!

Tobias


-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


__._,_.___


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___