In plant loops, temperature- based controls can be modeled using ComponentSetpoint plant equipment operation. With this you could model as a boiler in series with a temperature setpoint on its outlet.
You also might be able to simplify the problem by using the heater inside the storage tank as a way to model the separate back up heater.
From: EnergyPlus_Support@ yahoogroups. com [mailto: EnergyPlus_Support@ yahoogroups. com ] On Behalf Of Leticia Neves
Sent: Thursday, October 15, 2009 11:33 AM
To: EnergyPlus_Support@ yahoogroups. com
Subject: [EnergyPlus_ Support] Water heater - solar collector and instantaneous water heater
Hi,
I have some issues in a water heater model.
My project consists in a storage tank that is heated both by a solar collector and a instantaneous water heater (that complements the solar collector when it is necessary).
I have two sources to heat the storage tank, but the object 'Water heater: mixed' only allows one inlet and outlet source side.
I can try to create one loop that contains: the solar collector, the pump, the instantaneous water heater and then the storage tank, so I have just one source in the storage tank. The problem is that I have to have the possibility to bypass the instantaneous water heater when it is not necessary. In the 'branch' object I have the option to bypass, but it is controlled only by flow rate, and not by temperature.
How can I do that?
Thanks,
Leticia Neves