hey,

have you checked the units?
it looks like you've specified the flow rate in kg/s in the idf-file, however reported the variables in m3/s.

Best,
Tobias



--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Fabio Augusto Carezia <fabioacfoz@...> wrote:
>
> 
> Hello
> 	
> 	
> 	
> 	
> 
> 
> 	
> 
> 
> 	
> 	
> I´m evaluating a system with a self-conteined dx cooling coil and a constant flow fan without any terminal control, very simple. The total flow is 1,9 m3/s, with is set on the fan, on the coil, on the air loop and on the branch. There are 8 zones, the sum of all Airterminal: singleduct: uncontrolled is 1,9 either. However, after the simulation, the output is showing an airflow of 2,26 m3/s, and the airflow in each zone exceeds the specified in the program. Does anyone know why this could be happening? 		 	   		  
> _________________________________________________________________
> Acesse o Portal MSN do seu celular e se mantenha sempre atualizado. Clique aqui.
> http://www.windowslive.com.br/celular/home.asp?utm_source=MSN_Hotmail&utm_medium=Tagline&utm_campaign=MobileServices200908
>




------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/