|
I can only comment on the first warning. You have specified a
value in the “Return Air Fraction” field but you have no return air system
(PTAC) so the gains are being placed back into the space. Read through the I/O
Internal Gains section for more information on the adjustment of these
fractions. Alan
Jackson, LEED AP From:
EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On
Behalf Of Hu,Jia Hello, I used EnergyPlus to
simulate a small office which a window. Two lights and a PTAC
template is used. Two ref. points is set in the office to measure the
illuminance and glare level. I use the version 3.1 to
run the simulation. There are five warnings in my input file . I have uploaded
my input file, ERR text and my weatherfile to "Files > _Problem_Submittals " And the zip file name
is "some warnings". Could anyone explain why there are the following two
warnings or help me to fix these warnings? Thank you in advance. ** Warning ** For zone=RINKER BUILDING OFFICE
return air heat gain from lights will be applied to the zone air. ** Warning ** World Coordinate System
selected. Any non-zero Building/Zone North Axes or non-zero Zone Origins
are ignored. Thank you. JH __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |