Eman,

The direct normal is the amount of beam radiation received perpendicular
(at right angle) to the sun. Thus, sun angles, which are the most 
obvious differences between winter and summer solar radiation, have
no effect on the measured direct normal. However, the amount of time
the sun is in the sky does matter, so all other things being equal,
one would expect more direct normal in the summer than the winter in
northern latitudes.

I've taken a look at the College Station TMY3 weather fileIt does look a 
little anomalous, because the cloud cover amount in June is only 10% 
more than in January. I've also compared the direct normal for all 67
TMY3 and 17 TMY2 weather files for Texas. The variability in monthly
direct normal has gone up noticeably in the TMY3 weather files.

Joe

Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd. Suite 108D
Moraga CA 94556
(o) +925 388 0265
(c) +510 928 2683
yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx
www.whiteboxtechnologies.com



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/