[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Pump on Demand Side = True ?





Thank You One very mutch for the help.
 


From: Edwin Lee <leeed2001@xxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Fri, December 4, 2009 4:39:34 PM
Subject: Re: [EnergyPlus_Support] Pump on Demand Side = True ?

 

MN:


There can only be a demand side pump if there is a common pipe simulation in place, in which case there will be both demand and supply pumps.  The pump cannot be passive, because it will always want to be the component setting the flow.  

You may be able to approximate the energy consumption if you know the required flow rates throughout the simulation and can approximate the pump head.

Edwin Lee
EnergyPlus Development Team

On Fri, Dec 4, 2009 at 10:35, M�¡rio <m_neves32@yahoo. com> wrote:
 

Good Afternoon Fellow Energyplus Users

Does anyone know if it´s possible to place a pump in the demand side of a plant network? The pump will be passive placed in series with an active component like a ZoneHVAC:BassBoard. I just want the energy consumpion of the Pump.

Thank You Once Again
MN





__._,_.___


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___