Hi Lawrie,
i've transition the file in 4.0 and posted it.
But there is a error.
thanks
L Lawrie å??é??:
>
> One immediate problem is that you are still using V3.0. We're at V4.0
> now -- there may be changes that have helped or better diagnosed this
> problem.
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> < mailto:EnergyPlus_Support%40yahoogroups.com>, "Y.P.Hu" <hyp@...> wrote:
> >
> > thank you Edwin, i post it.
> > I want to simulate an air and radiant system.
> > Edwin Lee å??é�":
:
>
>
--
ã??Give my best wishes to you!
Respectfully yours, YunPeng Hu
Huazhong University of Science and Technology
Wuhan, Hubei, China
hyp@xxxxxxxxxxxxxxxxx
hyp6789@xxxxxxx
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/
!-Generator IDFEditor 1.33c
!-Option SortedOrder
!-NOTE: All comments with '!-' are ignored by the IDFEditor and are generated automatically.
!- Use '!' comments if they need to be retained when using the IDFEditor.
!- =========== ALL OBJECTS IN CLASS: VERSION ===========
Version,4.0;
!- =========== ALL OBJECTS IN CLASS: SIMULATIONCONTROL ===========
SimulationControl,
Yes, !- Do Zone Sizing Calculation
Yes, !- Do System Sizing Calculation
Yes, !- Do Plant Sizing Calculation
Yes, !- Run Simulation for Sizing Periods
Yes; !- Run Simulation for Weather File Run Periods
!- =========== ALL OBJECTS IN CLASS: BUILDING ===========
Building,
Building, !- Name
0.0, !- North Axis {deg}
City, !- Terrain
0.04, !- Loads Convergence Tolerance Value
0.5, !- Temperature Convergence Tolerance Value {deltaC}
FullInteriorAndExterior, !- Solar Distribution
25; !- Maximum Number of Warmup Days
!- =========== ALL OBJECTS IN CLASS: SURFACECONVECTIONALGORITHM:INSIDE ===========
SurfaceConvectionAlgorithm:Inside,Detailed;
!- =========== ALL OBJECTS IN CLASS: SURFACECONVECTIONALGORITHM:OUTSIDE ===========
SurfaceConvectionAlgorithm:Outside,Detailed;
!- =========== ALL OBJECTS IN CLASS: HEATBALANCEALGORITHM ===========
HeatBalanceAlgorithm,ConductionTransferFunction,200;
!- =========== ALL OBJECTS IN CLASS: ZONECAPACITANCEMULTIPLIER ===========
ZoneCapacitanceMultiplier,1;
!- =========== ALL OBJECTS IN CLASS: TIMESTEP ===========
Timestep,6;
!- =========== ALL OBJECTS IN CLASS: SITE:LOCATION ===========
Site:Location,
Wuhan_Hubei_CHN, !- Name
30.62, !- Latitude {deg}
114.13, !- Longitude {deg}
8, !- Time Zone {hr}
23; !- Elevation {m}
!- =========== ALL OBJECTS IN CLASS: SIZINGPERIOD:DESIGNDAY ===========
SizingPeriod:DesignDay,
Wuhan Ann Clg .4% Condns DB=>MWB, !- Name
35.4, !- Maximum Dry-Bulb Temperature {C}
6, !- Daily Temperature Range {deltaC}
27.4, !- Humidity Indicating Conditions at Maximum Dry-Bulb
101049, !- Barometric Pressure {Pa}
3, !- Wind Speed {m/s}
0, !- Wind Direction {deg}
1, !- Sky Clearness
0, !- Rain Indicator
0, !- Snow Indicator
21, !- Day of Month
7, !- Month
SummerDesignDay, !- Day Type
, !- Daylight Saving Time Indicator
WetBulb, !- Humidity Indicating Type
, !- Relative Humidity Day Schedule Name
DefaultMultipliers, !- Dry-Bulb Temperature Range Modifier Type
, !- Dry-Bulb Temperature Range Modifier Schedule Name
ASHRAEClearSky; !- Solar Model Indicator
!- =========== ALL OBJECTS IN CLASS: RUNPERIODCONTROL:SPECIALDAYS ===========
RunPeriodControl:SpecialDays,
SummerDDay, !- Name
7/21, !- Start Date
1, !- Duration {days}
SummerDesignDay; !- Special Day Type
!- =========== ALL OBJECTS IN CLASS: SITE:GROUNDTEMPERATURE:BUILDINGSURFACE ===========
Site:GroundTemperature:BuildingSurface,6.9,5.9,7.7,10.5,17.9,23.6,27.4,28.6,26.6,22.2,16.3,10.8;
!- =========== ALL OBJECTS IN CLASS: SCHEDULETYPELIMITS ===========
ScheduleTypeLimits,
Any Number; !- Name
ScheduleTypeLimits,
Fraction, !- Name
0.0, !- Lower Limit Value
1.0, !- Upper Limit Value
CONTINUOUS; !- Numeric Type
ScheduleTypeLimits,
Temperature, !- Name
-60, !- Lower Limit Value
200, !- Upper Limit Value
CONTINUOUS; !- Numeric Type
ScheduleTypeLimits,
Control Type, !- Name
0, !- Lower Limit Value
4, !- Upper Limit Value
DISCRETE; !- Numeric Type
ScheduleTypeLimits,
On/Off, !- Name
0, !- Lower Limit Value
1, !- Upper Limit Value
DISCRETE; !- Numeric Type
!- =========== ALL OBJECTS IN CLASS: SCHEDULE:COMPACT ===========
Schedule:Compact,
Activity Sch, !- Name
Any Number, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Alldays, !- Field 2
Until: 24:00,131.80; !- Field 3
Schedule:Compact,
Work Eff Sch, !- Name
Any Number, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Alldays, !- Field 2
Until: 24:00,0.00; !- Field 3
Schedule:Compact,
Clothing Sch, !- Name
Any Number, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Alldays, !- Field 2
Until: 24:00,1.00; !- Field 3
Schedule:Compact,
Air Velo Sch, !- Name
Any Number, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Alldays, !- Field 2
Until: 24:00,0.137; !- Field 3
Schedule:Compact,
Office Occupancy, !- Name
ANY NUMBER, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Weekdays, !- Field 2
Until: 6:00,0.00, !- Field 3
Until: 7:00,0.10, !- Field 5
Until: 8:00,0.50, !- Field 7
Until: 12:00,1.00, !- Field 9
Until: 13:00,0.50, !- Field 11
Until: 16:00,1.00, !- Field 13
Until: 17:00,0.50, !- Field 15
Until: 18:00,0.10, !- Field 17
Until: 24:00,0.00, !- Field 19
For: Weekends Holidays, !- Field 21
Until: 24:00,0.00, !- Field 22
For: SummerDesignDay, !- Field 24
Until: 6:00,0.00, !- Field 25
Until: 7:00,0.10, !- Field 27
Until: 8:00,0.50, !- Field 29
Until: 12:00,1.00, !- Field 31
Until: 13:00,0.50, !- Field 33
Until: 16:00,1.00, !- Field 35
Until: 17:00,0.50, !- Field 37
Until: 18:00,0.10, !- Field 39
Until: 24:00,0.00, !- Field 41
For: WinterDesignDay, !- Field 43
Until: 24:00,0.00, !- Field 44
For: CustomDay1, !- Field 46
Until: 24:00,0.00, !- Field 47
For: CustomDay2, !- Field 49
Until: 24:00,0.00; !- Field 50
Schedule:Compact,
Intermittent, !- Name
ANY NUMBER, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Weekdays, !- Field 2
Until: 8:00,0.00, !- Field 3
Until: 18:00,1.00, !- Field 5
Until: 24:00,0.00, !- Field 7
For: Weekends Holidays, !- Field 9
Until: 24:00,0.00, !- Field 10
For: SummerDesignDay, !- Field 12
Until: 8:00,0.00, !- Field 13
Until: 18:00,1.00, !- Field 15
Until: 24:00,0.00, !- Field 17
For: WinterDesignDay, !- Field 19
Until: 24:00,0.00, !- Field 20
For: CustomDay1, !- Field 22
Until: 24:00,0.00, !- Field 23
For: CustomDay2, !- Field 25
Until: 24:00,0.00; !- Field 26
Schedule:Compact,
Office Lighting, !- Name
ANY NUMBER, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Weekdays, !- Field 2
Until: 6:00,5.00E-002, !- Field 3
Until: 7:00,0.20, !- Field 5
Until: 17:00,1.00, !- Field 7
Until: 18:00,0.50, !- Field 9
Until: 24:00,5.00E-002, !- Field 11
For: Weekends Holidays, !- Field 13
Until: 24:00,5.00E-002, !- Field 14
For: SummerDesignDay, !- Field 16
Until: 6:00,5.00E-002, !- Field 17
Until: 7:00,0.20, !- Field 19
Until: 17:00,1.00, !- Field 21
Until: 18:00,0.50, !- Field 23
Until: 24:00,5.00E-002, !- Field 25
For: WinterDesignDay, !- Field 27
Until: 24:00,5.00E-002, !- Field 28
For: CustomDay1, !- Field 30
Until: 24:00,5.00E-002, !- Field 31
For: CustomDay2, !- Field 33
Until: 24:00,5.00E-002; !- Field 34
Schedule:Compact,
On Peak, !- Name
Fraction, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Alldays, !- Field 2
Until: 9:00,0.00, !- Field 3
Until: 18:00,1.00, !- Field 5
Until: 24:00,0.00; !- Field 7
Schedule:Compact,
Off Peak, !- Name
Fraction, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Alldays, !- Field 2
Until: 9:00,1.00, !- Field 3
Until: 18:00,0.00, !- Field 5
Until: 24:00,1.00; !- Field 7
Schedule:Compact,
ON, !- Name
Fraction, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Alldays, !- Field 2
Until: 24:00,1.00; !- Field 3
Schedule:Compact,
SEASONAL RESET SUPPLY AIR TEMP SCH, !- Name
TEMPERATURE, !- Schedule Type Limits Name
Through: 3/31, !- Field 1
For: Alldays, !- Field 2
Until: 24:00,16.00, !- Field 3
Through: 9/30, !- Field 5
For: Alldays, !- Field 6
Until: 24:00,13.00, !- Field 7
Through: 12/31, !- Field 9
For: Alldays, !- Field 10
Until: 24:00,16.00; !- Field 11
Schedule:Compact,
CW LOOP TEMP SCHEDULE, !- Name
TEMPERATURE, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Alldays, !- Field 2
Until: 24:00,5.22; !- Field 3
Schedule:Compact,
CW Radiant LOOP TEMP SCHEDULE, !- Name
TEMPERATURE, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Alldays, !- Field 2
Until: 24:00,17; !- Field 3
Schedule:Compact,
HW LOOP TEMP SCHEDULE, !- Name
TEMPERATURE, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Alldays, !- Field 2
Until: 24:00,82.00; !- Field 3
Schedule:Compact,
FANANDCOILAVAILSCHED, !- Name
FRACTION, !- Schedule Type Limits Name
Through: 3/31, !- Field 1
For: Alldays, !- Field 2
Until: 24:00,1.00, !- Field 3
Through: 9/30, !- Field 5
For: Weekdays, !- Field 6
Until: 7:00,0.00, !- Field 7
Until: 17:00,1.00, !- Field 9
Until: 24:00,0.00, !- Field 11
For: Weekends Holidays CustomDay1 CustomDay2, !- Field 13
Until: 24:00,0.00, !- Field 14
For: SummerDesignDay, !- Field 16
Until: 24:00,1.00, !- Field 17
For: WinterDesignDay, !- Field 19
Until: 24:00,1.00, !- Field 20
Through: 12/31, !- Field 22
For: Alldays, !- Field 23
Until: 24:00,1.00; !- Field 24
Schedule:Compact,
COOLINGCOILAVAILSCHED, !- Name
FRACTION, !- Schedule Type Limits Name
Through: 3/31, !- Field 1
For: Alldays, !- Field 2
Until: 24:00,0.00, !- Field 3
Through: 9/30, !- Field 5
For: Weekdays, !- Field 6
Until: 7:00,0.00, !- Field 7
Until: 17:00,1.00, !- Field 9
Until: 24:00,0.00, !- Field 11
For: Weekends Holidays CustomDay1 CustomDay2, !- Field 13
Until: 24:00,0.00, !- Field 14
For: SummerDesignDay, !- Field 16
Until: 24:00,1.00, !- Field 17
For: WinterDesignDay, !- Field 19
Until: 24:00,1.00, !- Field 20
Through: 12/31, !- Field 22
For: Alldays, !- Field 23
Until: 24:00,0.00; !- Field 24
Schedule:Compact,
HEATING SETPOINTS, !- Name
TEMPERATURE, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Weekdays Weekends Holidays CustomDay1 CustomDay2, !- Field 2
Until: 7:00,15.00, !- Field 3
Until: 17:00,20.00, !- Field 5
Until: 24:00,15.00, !- Field 7
For: SummerDesignDay, !- Field 9
Until: 24:00,15.00, !- Field 10
For: WinterDesignDay, !- Field 12
Until: 24:00,20.00; !- Field 13
Schedule:Compact,
COOLING SETPOINTS, !- Name
TEMPERATURE, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Weekdays Weekends Holidays CustomDay1 CustomDay2, !- Field 2
Until: 7:00,30.00, !- Field 3
Until: 17:00,24.00, !- Field 5
Until: 24:00,30.00, !- Field 7
For: SummerDesignDay, !- Field 9
Until: 24:00,24.00, !- Field 10
For: WinterDesignDay, !- Field 12
Until: 24:00,50.00; !- Field 13
Schedule:Compact,
ZONE CONTROL TYPE SCHED, !- Name
CONTROL TYPE, !- Schedule Type Limits Name
Through: 3/31, !- Field 1
For: Alldays, !- Field 2
Until: 24:00,1, !- Field 3
Through: 9/30, !- Field 5
For: Alldays, !- Field 6
Until: 24:00,2, !- Field 7
Through: 12/31, !- Field 9
For: Alldays, !- Field 10
Until: 24:00,1; !- Field 11
Schedule:Compact,
Condenser LOOP TEMP SCHEDULE, !- Name
TEMPERATURE, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Alldays, !- Field 2
Until: 24:00,29.4; !- Field 3
Schedule:Compact,
RADIANTSYSAVAILSCHED, !- Name
FRACTION, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Alldays, !- Field 2
Until: 24:00,1.00; !- Field 3
Schedule:Compact,
RADIANT HEATING SETPOINTS, !- Name
TEMPERATURE, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Alldays, !- Field 2
Until: 7:00,12.00, !- Field 3
Until: 17:00,17.00, !- Field 5
Until: 24:00,12.00; !- Field 7
Schedule:Compact,
RADIANT COOLING SETPOINTS, !- Name
TEMPERATURE, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Alldays, !- Field 2
Until: 24:00,26; !- Field 3
Schedule:Compact,
Office Occupancy For OA, !- Name
Fraction, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Alldays, !- Field 2
Until 6:00,1, !- Field 3
until 18:00,1, !- Field 5
until 24:00,1; !- Field 7
Schedule:Compact,
DOAS Precool Air Summer Temp, !- Name
TEMPERATURE, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Alldays, !- Field 2
Until: 24:00,7; !- Field 3
Schedule:Compact,
DOAS Preheat Air Winter Temp, !- Name
TEMPERATURE, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Alldays, !- Field 2
Until: 24:00,50; !- Field 3
Schedule:Compact,
DOAS CoolingCoil Air Summer Temp, !- Name
TEMPERATURE, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Alldays, !- Field 2
Until: 24:00,16; !- Field 3
Schedule:Compact,
DOAS HeatingCoil Air Winter Temp, !- Name
TEMPERATURE, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Alldays, !- Field 2
Until: 24:00,40; !- Field 3
Schedule:Compact,
OFF, !- Name
On/Off, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Alldays, !- Field 2
Until: 24:00,0; !- Field 3
Schedule:Compact,
DOAS Precool Air Summer RaH, !- Name
TEMPERATURE, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: Alldays, !- Field 2
Until: 24:00,0.00590; !- Field 3
!- =========== ALL OBJECTS IN CLASS: MATERIAL ===========
Material,
F08 Metal surface, !- Name
Smooth, !- Roughness
0.0008, !- Thickness {m}
45.28, !- Conductivity {W/m-K}
7824, !- Density {kg/m3}
500; !- Specific Heat {J/kg-K}
Material,
I02 50mm insulation board, !- Name
MediumRough, !- Roughness
0.0508, !- Thickness {m}
0.03, !- Conductivity {W/m-K}
43, !- Density {kg/m3}
1210; !- Specific Heat {J/kg-K}
Material,
G01a 19mm gypsum board, !- Name
MediumSmooth, !- Roughness
0.019, !- Thickness {m}
0.16, !- Conductivity {W/m-K}
800, !- Density {kg/m3}
1090; !- Specific Heat {J/kg-K}
Material,
M11 100mm lightweight concrete, !- Name
MediumRough, !- Roughness
0.1016, !- Thickness {m}
0.53, !- Conductivity {W/m-K}
1280, !- Density {kg/m3}
840; !- Specific Heat {J/kg-K}
Material,
F16 Acoustic tile, !- Name
MediumSmooth, !- Roughness
0.0191, !- Thickness {m}
0.06, !- Conductivity {W/m-K}
368, !- Density {kg/m3}
590; !- Specific Heat {J/kg-K}
Material,
M01 100mm brick, !- Name
MediumRough, !- Roughness
0.1016, !- Thickness {m}
0.89, !- Conductivity {W/m-K}
1920, !- Density {kg/m3}
790; !- Specific Heat {J/kg-K}
Material,
M15 200mm heavyweight concrete, !- Name
MediumRough, !- Roughness
0.2032, !- Thickness {m}
1.95, !- Conductivity {W/m-K}
2240, !- Density {kg/m3}
900; !- Specific Heat {J/kg-K}
Material,
M05 200mm concrete block,!- Name
MediumRough, !- Roughness
0.2032, !- Thickness {m}
1.11, !- Conductivity {W/m-K}
800, !- Density {kg/m3}
920; !- Specific Heat {J/kg-K}
!- =========== ALL OBJECTS IN CLASS: MATERIAL:AIRGAP ===========
Material:AirGap,
F04 Wall air space resistance, !- Name
0.15; !- Thermal Resistance {m2-K/W}
Material:AirGap,
F05 Ceiling air space resistance, !- Name
0.18; !- Thermal Resistance {m2-K/W}
!- =========== ALL OBJECTS IN CLASS: WINDOWMATERIAL:GLAZING ===========
WindowMaterial:Glazing,
CLEAR 3MM, !- Name
SpectralAverage, !- Optical Data Type
, !- Window Glass Spectral Data Set Name
0.003, !- Thickness {m}
0.837, !- Solar Transmittance at Normal Incidence
0.075, !- Front Side Solar Reflectance at Normal Incidence
0.075, !- Back Side Solar Reflectance at Normal Incidence
0.898, !- Visible Transmittance at Normal Incidence
0.081, !- Front Side Visible Reflectance at Normal Incidence
0.081, !- Back Side Visible Reflectance at Normal Incidence
0, !- Infrared Transmittance at Normal Incidence
0.84, !- Front Side Infrared Hemispherical Emissivity
0.84, !- Back Side Infrared Hemispherical Emissivity
0.9; !- Conductivity {W/m-K}
!- =========== ALL OBJECTS IN CLASS: WINDOWMATERIAL:GAS ===========
WindowMaterial:Gas,
AIR 6MM, !- Name
Air, !- Gas Type
0.0063; !- Thickness {m}
!- =========== ALL OBJECTS IN CLASS: CONSTRUCTION ===========
Construction,
Window Single Pane, !- Name
CLEAR 3MM; !- Outside Layer
Construction,
Window Double Pane, !- Name
CLEAR 3MM, !- Outside Layer
AIR 6MM, !- Layer 2
CLEAR 3MM; !- Layer 3
Construction,
Light Exterior Wall, !- Name
F08 Metal surface, !- Outside Layer
I02 50mm insulation board, !- Layer 2
F04 Wall air space resistance, !- Layer 3
G01a 19mm gypsum board; !- Layer 4
Construction,
Light Roof/Ceiling, !- Name
M11 100mm lightweight concrete, !- Outside Layer
F05 Ceiling air space resistance, !- Layer 2
F16 Acoustic tile; !- Layer 3
Construction,
Light Partition, !- Name
G01a 19mm gypsum board, !- Outside Layer
F04 Wall air space resistance, !- Layer 2
G01a 19mm gypsum board; !- Layer 3
Construction,
Light Floor, !- Name
F16 Acoustic tile, !- Outside Layer
F05 Ceiling air space resistance, !- Layer 2
M11 100mm lightweight concrete; !- Layer 3
Construction,
Heavy Exterior Wall, !- Name
M01 100mm brick, !- Outside Layer
M15 200mm heavyweight concrete, !- Layer 2
I02 50mm insulation board, !- Layer 3
F04 Wall air space resistance, !- Layer 4
G01a 19mm gypsum board; !- Layer 5
Construction,
Heavy Roof/Ceiling, !- Name
M15 200mm heavyweight concrete, !- Outside Layer
F05 Ceiling air space resistance, !- Layer 2
F16 Acoustic tile; !- Layer 3
Construction,
Heavy Partition, !- Name
G01a 19mm gypsum board, !- Outside Layer
M05 200mm concrete block,!- Layer 2
G01a 19mm gypsum board; !- Layer 3
Construction,
Heavy Floor, !- Name
F16 Acoustic tile, !- Outside Layer
F05 Ceiling air space resistance, !- Layer 2
M15 200mm heavyweight concrete; !- Layer 3
!- =========== ALL OBJECTS IN CLASS: CONSTRUCTION:INTERNALSOURCE ===========
Construction:InternalSource,
Roof with Radiant, !- Name
2, !- Source Present After Layer Number
2, !- Temperature Calculation Requested After Layer Number
1, !- Dimensions for the CTF Calculation
0.15, !- Tube Spacing {m}
M15 200mm heavyweight concrete, !- Outside Layer
F05 Ceiling air space resistance, !- Layer 2
F16 Acoustic tile; !- Layer 3
!- =========== ALL OBJECTS IN CLASS: GLOBALGEOMETRYRULES ===========
GlobalGeometryRules,
UpperLeftCorner, !- Starting Vertex Position
Counterclockwise, !- Vertex Entry Direction
World; !- Coordinate System
!- =========== ALL OBJECTS IN CLASS: ZONE ===========
Zone,
ZONE1, !- Name
0.0, !- Direction of Relative North {deg}
-1.4758, !- X Origin {m}
-2.5913, !- Y Origin {m}
0.0, !- Z Origin {m}
, !- Type
1; !- Multiplier
!- =========== ALL OBJECTS IN CLASS: BUILDINGSURFACE:DETAILED ===========
BuildingSurface:Detailed,
5EDA03, !- Name
Floor, !- Surface Type
Light Floor, !- Construction Name
ZONE1, !- Zone Name
Ground, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
NoSun, !- Sun Exposure
NoWind, !- Wind Exposure
autocalculate, !- View Factor to Ground
4, !- Number of Vertices
0.000000,0.000000,0.000000, !- X,Y,Z ==> Vertex 1 {m}
0.000000,4,0.000000, !- X,Y,Z ==> Vertex 2 {m}
3,4,0.000000, !- X,Y,Z ==> Vertex 3 {m}
3,0.000000,0.000000; !- X,Y,Z ==> Vertex 4 {m}
BuildingSurface:Detailed,
5B2EAB, !- Name
Wall, !- Surface Type
Light Exterior Wall, !- Construction Name
ZONE1, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
autocalculate, !- View Factor to Ground
4, !- Number of Vertices
3,4,2.800000, !- X,Y,Z ==> Vertex 1 {m}
3,4,0.000000, !- X,Y,Z ==> Vertex 2 {m}
0.000000,4,0.000000, !- X,Y,Z ==> Vertex 3 {m}
0.000000,4,2.800000; !- X,Y,Z ==> Vertex 4 {m}
BuildingSurface:Detailed,
7D3A34, !- Name
Roof, !- Surface Type
Roof with Radiant, !- Construction Name
ZONE1, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
autocalculate, !- View Factor to Ground
4, !- Number of Vertices
0.000000,0.000000,2.800000, !- X,Y,Z ==> Vertex 1 {m}
3,0.000000,2.800000, !- X,Y,Z ==> Vertex 2 {m}
3,4,2.800000, !- X,Y,Z ==> Vertex 3 {m}
0.000000,4,2.800000; !- X,Y,Z ==> Vertex 4 {m}
BuildingSurface:Detailed,
D6F186, !- Name
Wall, !- Surface Type
Light Exterior Wall, !- Construction Name
ZONE1, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
autocalculate, !- View Factor to Ground
4, !- Number of Vertices
0.000000,4,2.800000, !- X,Y,Z ==> Vertex 1 {m}
0.000000,4,0.000000, !- X,Y,Z ==> Vertex 2 {m}
0.000000,0.000000,0.000000, !- X,Y,Z ==> Vertex 3 {m}
0.000000,0.000000,2.800000; !- X,Y,Z ==> Vertex 4 {m}
BuildingSurface:Detailed,
9583E2, !- Name
Wall, !- Surface Type
Light Exterior Wall, !- Construction Name
ZONE1, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
autocalculate, !- View Factor to Ground
4, !- Number of Vertices
0.000000,0.000000,2.800000, !- X,Y,Z ==> Vertex 1 {m}
0.000000,0.000000,0.000000, !- X,Y,Z ==> Vertex 2 {m}
3,0.000000,0.000000, !- X,Y,Z ==> Vertex 3 {m}
3,0.000000,2.800000; !- X,Y,Z ==> Vertex 4 {m}
BuildingSurface:Detailed,
181D38, !- Name
Wall, !- Surface Type
Light Exterior Wall, !- Construction Name
ZONE1, !- Zone Name
Outdoors, !- Outside Boundary Condition
, !- Outside Boundary Condition Object
SunExposed, !- Sun Exposure
WindExposed, !- Wind Exposure
autocalculate, !- View Factor to Ground
4, !- Number of Vertices
3,0.000000,2.800000, !- X,Y,Z ==> Vertex 1 {m}
3,0.000000,0.000000, !- X,Y,Z ==> Vertex 2 {m}
3,4,0.000000, !- X,Y,Z ==> Vertex 3 {m}
3,4,2.800000; !- X,Y,Z ==> Vertex 4 {m}
!- =========== ALL OBJECTS IN CLASS: FENESTRATIONSURFACE:DETAILED ===========
FenestrationSurface:Detailed,
65B8F9, !- Name
Door, !- Surface Type
Light Exterior Wall, !- Construction Name
9583E2, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- View Factor to Ground
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
1.000000,0.000000,1.800000, !- X,Y,Z ==> Vertex 1 {m}
1.000000,0.000000,0.000000, !- X,Y,Z ==> Vertex 2 {m}
2.000000,0.000000,0.000000, !- X,Y,Z ==> Vertex 3 {m}
2.000000,0.000000,1.800000; !- X,Y,Z ==> Vertex 4 {m}
FenestrationSurface:Detailed,
7BDCB2, !- Name
Window, !- Surface Type
Window Single Pane, !- Construction Name
181D38, !- Building Surface Name
, !- Outside Boundary Condition Object
, !- View Factor to Ground
, !- Shading Control Name
, !- Frame and Divider Name
, !- Multiplier
4, !- Number of Vertices
3.000000,1.500000,2.400000, !- X,Y,Z ==> Vertex 1 {m}
3.000000,1.500000,1.200000, !- X,Y,Z ==> Vertex 2 {m}
3.000000,2.500000,1.200000, !- X,Y,Z ==> Vertex 3 {m}
3.000000,2.500000,2.400000; !- X,Y,Z ==> Vertex 4 {m}
!- =========== ALL OBJECTS IN CLASS: PEOPLE ===========
People,
Zone1 People, !- Name
ZONE1, !- Zone Name
Office Occupancy For OA, !- Number of People Schedule Name
people, !- Number of People Calculation Method
10, !- Number of People
, !- People per Zone Floor Area {person/m2}
, !- Zone Floor Area per Person {m2/person}
0.3, !- Fraction Radiant
0.52, !- Sensible Heat Fraction
Activity Sch; !- Activity Level Schedule Name
!- =========== ALL OBJECTS IN CLASS: OTHEREQUIPMENT ===========
OtherEquipment,
OtherEquipent:OA, !- Name
ZONE1, !- Zone Name
ON, !- Schedule Name
EquipmentLevel, !- Design Level Calculation Method
2000, !- Design Level {W}
, !- Watts per Zone Floor Area {W/m2}
, !- Watts per Person {W/Person}
0, !- Fraction Latent
0, !- Fraction Radiant
0; !- Fraction Lost
!- =========== ALL OBJECTS IN CLASS: SIZING:ZONE ===========
Sizing:Zone,
ZONE1, !- Zone Name
14, !- Zone Cooling Design Supply Air Temperature {C}
50, !- Zone Heating Design Supply Air Temperature {C}
0.009, !- Zone Cooling Design Supply Air Humidity Ratio {kg-H2O/kg-air}
0.0004, !- Zone Heating Design Supply Air Humidity Ratio {kg-H2O/kg-air}
Flow/Person, !- Outdoor Air Method
0.0083, !- Outdoor Air Flow per Person {m3/s}
, !- Outdoor Air Flow per Zone Floor Area {m3/s-m2}
, !- Outdoor Air Flow per Zone {m3/s}
0, !- Zone Sizing Factor
DesignDay, !- Cooling Design Air Flow Method
, !- Cooling Design Air Flow Rate {m3/s}
, !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2}
, !- Cooling Minimum Air Flow {m3/s}
, !- Cooling Minimum Air Flow Fraction
DesignDay, !- Heating Design Air Flow Method
, !- Heating Design Air Flow Rate {m3/s}
, !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}
, !- Heating Maximum Air Flow {m3/s}
; !- Heating Maximum Air Flow Fraction
!- =========== ALL OBJECTS IN CLASS: SIZING:SYSTEM ===========
Sizing:System,
DOAS AirLoop, !- AirLoop Name
Sensible, !- Type of Load to Size On
autosize, !- Design Outdoor Air Flow Rate {m3/s}
0, !- Minimum System Air Flow Ratio
4.5, !- Preheat Design Temperature {C}
0.008, !- Preheat Design Humidity Ratio {kg-H2O/kg-Air}
11.5, !- Precool Design Temperature {C}
0.008, !- Precool Design Humidity Ratio {kg-H2O/kg-Air}
12.8, !- Central Cooling Design Supply Air Temperature {C}
16.7, !- Central Heating Design Supply Air Temperature {C}
NonCoincident, !- Sizing Option
No, !- 100% Outdoor Air in Cooling
No, !- 100% Outdoor Air in Heating
0.008, !- Central Cooling Design Supply Air Humidity Ratio {kg-H2O/kg-Air}
0.008, !- Central Heating Design Supply Air Humidity Ratio {kg-H2O/kg-Air}
DesignDay, !- Cooling Design Air Flow Method
, !- Cooling Design Air Flow Rate {m3/s}
DesignDay, !- Heating Design Air Flow Method
; !- Heating Design Air Flow Rate {m3/s}
!- =========== ALL OBJECTS IN CLASS: SIZING:PLANT ===========
Sizing:Plant,
PlantLpSplSide CHW Chilled Water Loop, !- Plant or Condenser Loop Name
Cooling, !- Loop Type
7, !- Design Loop Exit Temperature {C}
5; !- Loop Design Temperature Difference {deltaC}
Sizing:Plant,
PlantLpSplSide Radiant CHW Chilled Water Loop, !- Plant or Condenser Loop Name
Cooling, !- Loop Type
17, !- Design Loop Exit Temperature {C}
5; !- Loop Design Temperature Difference {deltaC}
Sizing:Plant,
PlantLpSplSide HW Heated Water Loop, !- Plant or Condenser Loop Name
Heating, !- Loop Type
82, !- Design Loop Exit Temperature {C}
11; !- Loop Design Temperature Difference {deltaC}
!- =========== ALL OBJECTS IN CLASS: ZONECONTROL:THERMOSTAT ===========
ZoneControl:Thermostat,
Zone1Thermostat, !- Name
ZONE1, !- Zone Name
Zone Control Type Sched, !- Control Type Schedule Name
ThermostatSetpoint:SingleCooling, !- Control 1 Object Type
Cooling Setpoint with SB,!- Control 1 Name
ThermostatSetpoint:SingleHeating, !- Control 2 Object Type
Heating Setpoint with SB;!- Control 2 Name
!- =========== ALL OBJECTS IN CLASS: THERMOSTATSETPOINT:SINGLEHEATING ===========
ThermostatSetpoint:SingleHeating,
Heating Setpoint with SB,!- Name
Heating Setpoints; !- Setpoint Temperature Schedule Name
!- =========== ALL OBJECTS IN CLASS: THERMOSTATSETPOINT:SINGLECOOLING ===========
ThermostatSetpoint:SingleCooling,
Cooling Setpoint with SB,!- Name
Cooling Setpoints; !- Setpoint Temperature Schedule Name
!- =========== ALL OBJECTS IN CLASS: ZONEHVAC:LOWTEMPERATURERADIANT:VARIABLEFLOW ===========
ZoneHVAC:LowTemperatureRadiant:VariableFlow,
CRCP1, !- Name
Office Occupancy For OA, !- Availability Schedule Name
ZONE1, !- Zone Name
7D3A34, !- Surface Name or Radiant Surface Group Name
0.013, !- Hydronic Tubing Inside Diameter {m}
autosize, !- Hydronic Tubing Length {m}
MeanAirTemperature, !- Temperature Control Type
autosize, !- Maximum Hot Water Flow {m3/s}
CRCP1 HW Inlet Node, !- Heating Water Inlet Node Name
CRCP1 HW Outlet Node, !- Heating Water Outlet Node Name
2, !- Heating Control Throttling Range {deltaC}
RADIANT HEATING SETPOINTS, !- Heating Control Temperature Schedule Name
autosize, !- Maximum Cold Water Flow {m3/s}
CRCP1 CHW Inlet Node, !- Cooling Water Inlet Node Name
CRCP1 CHW Outlet Node, !- Cooling Water Outlet Node Name
2, !- Cooling Control Throttling Range {deltaC}
RADIANT COOLING SETPOINTS; !- Cooling Control Temperature Schedule Name
!- =========== ALL OBJECTS IN CLASS: AIRTERMINAL:SINGLEDUCT:UNCONTROLLED ===========
AirTerminal:SingleDuct:Uncontrolled,
Zone1 DOAS AirTerminal, !- Name
Office Occupancy For OA, !- Availability Schedule Name
DOAS ZONE1 INLET NODE, !- Zone Supply Air Node Name
autosize; !- Maximum Air Flow Rate {m3/s}
!- =========== ALL OBJECTS IN CLASS: ZONEHVAC:EQUIPMENTLIST ===========
ZoneHVAC:EquipmentList,
Zone1 Equipment List, !- Name
AirTerminal:SingleDuct:Uncontrolled, !- Zone Equipment 1 Object Type
Zone1 DOAS AirTerminal, !- Zone Equipment 1 Name
1, !- Zone Equipment 1 Cooling Priority
1, !- Zone Equipment 1 Heating Priority
ZoneHVAC:LowTemperatureRadiant:VariableFlow, !- Zone Equipment 2 Object Type
CRCP1, !- Zone Equipment 2 Name
2, !- Zone Equipment 2 Cooling Priority
2; !- Zone Equipment 2 Heating Priority
!- =========== ALL OBJECTS IN CLASS: ZONEHVAC:EQUIPMENTCONNECTIONS ===========
ZoneHVAC:EquipmentConnections,
ZONE1, !- Zone Name
Zone1 Equipment List, !- Zone Conditioning Equipment List Name
DOAS Zone1 Inlet Node, !- Zone Air Inlet Node or NodeList Name
, !- Zone Air Exhaust Node or NodeList Name
Zone1 Air Node, !- Zone Air Node Name
Zone1 Outlet Node; !- Zone Return Air Node Name
!- =========== ALL OBJECTS IN CLASS: FAN:VARIABLEVOLUME ===========
Fan:VariableVolume,
DOAS Fan, !- Name
Office Occupancy For OA, !- Availability Schedule Name
0.5, !- Fan Efficiency
75, !- Pressure Rise {Pa}
autosize, !- Maximum Flow Rate {m3/s}
0, !- Minimum Flow Rate {m3/s}
0.9, !- Motor Efficiency
, !- Motor In Airstream Fraction
0.35, !- Fan Coefficient 1
0.3, !- Fan Coefficient 2
-.54, !- Fan Coefficient 3
0.87, !- Fan Coefficient 4
0, !- Fan Coefficient 5
DOAS OA Mixer Outlet Node, !- Air Inlet Node Name
DOAS Fan Outlet Node, !- Air Outlet Node Name
General; !- End-Use Subcategory
!- =========== ALL OBJECTS IN CLASS: COIL:COOLING:WATER ===========
Coil:Cooling:Water,
DOAS CoolingCoil, !- Name
OFF, !- Availability Schedule Name
autosize, !- Design Water Flow Rate {m3/s}
autosize, !- Design Air Flow Rate {m3/s}
autosize, !- Design Inlet Water Temperature {C}
autosize, !- Design Inlet Air Temperature {C}
autosize, !- Design Outlet Air Temperature {C}
autosize, !- Design Inlet Air Humidity Ratio {kg-H2O/kg-air}
autosize, !- Design Outlet Air Humidity Ratio {kg-H2O/kg-air}
DOAS CoolingCoil CHW Inlet Node, !- Water Inlet Node Name
DOAS CoolingCoil CHW Outlet Node, !- Water Outlet Node Name
DOAS Fan Outlet Node, !- Air Inlet Node Name
DOAS CoolingCoil Air Outlet Node, !- Air Outlet Node Name
SimpleAnalysis, !- Type of Analysis
CrossFlow; !- Heat Exchanger Configuration
Coil:Cooling:Water,
DOAS Precool CoolingCoil,!- Name
Office Occupancy For OA, !- Availability Schedule Name
autosize, !- Design Water Flow Rate {m3/s}
autosize, !- Design Air Flow Rate {m3/s}
autosize, !- Design Inlet Water Temperature {C}
autosize, !- Design Inlet Air Temperature {C}
autosize, !- Design Outlet Air Temperature {C}
autosize, !- Design Inlet Air Humidity Ratio {kg-H2O/kg-air}
autosize, !- Design Outlet Air Humidity Ratio {kg-H2O/kg-air}
DOAS Precool CoolingCoil CHW Inlet Node, !- Water Inlet Node Name
DOAS Precool CoolingCoil CHW Outlet Node, !- Water Outlet Node Name
DOAS OA Inlet Node, !- Air Inlet Node Name
DOAS Precool CoolingCoil Air Outlet Node, !- Air Outlet Node Name
SimpleAnalysis, !- Type of Analysis
CrossFlow; !- Heat Exchanger Configuration
!- =========== ALL OBJECTS IN CLASS: COIL:HEATING:WATER ===========
Coil:Heating:Water,
DOAS HeatingCoil, !- Name
OFF, !- Availability Schedule Name
, !- U-Factor Times Area Value {W/K}
, !- Maximum Water Flow Rate {m3/s}
DOAS HeatingCoil HW Inlet Node, !- Water Inlet Node Name
DOAS HeatingCoil HW Outlet Node, !- Water Outlet Node Name
DOAS CoolingCoil Air Outlet Node, !- Air Inlet Node Name
DOAS AirLpSplSide Outlet Node, !- Air Outlet Node Name
NominalCapacity, !- Performance Input Method
100, !- Rated Capacity {W}
82.2, !- Rated Inlet Water Temperature {C}
16.6, !- Rated Inlet Air Temperature {C}
71.1, !- Rated Outlet Water Temperature {C}
32.2; !- Rated Outlet Air Temperature {C}
Coil:Heating:Water,
DOAS Preheat HeatingCoil,!- Name
OFF, !- Availability Schedule Name
, !- U-Factor Times Area Value {W/K}
, !- Maximum Water Flow Rate {m3/s}
DOAS Preheat HeatingCoil HW Inlet Node, !- Water Inlet Node Name
DOAS Preheat HeatingCoil HW Outlet Node, !- Water Outlet Node Name
DOAS Precool CoolingCoil Air Outlet Node, !- Air Inlet Node Name
DOAS Preheat HeatingCoil Air Outlet Node, !- Air Outlet Node Name
NominalCapacity, !- Performance Input Method
100, !- Rated Capacity {W}
82.2, !- Rated Inlet Water Temperature {C}
16.6, !- Rated Inlet Air Temperature {C}
71.1, !- Rated Outlet Water Temperature {C}
32.2; !- Rated Outlet Air Temperature {C}
!- =========== ALL OBJECTS IN CLASS: CONTROLLER:WATERCOIL ===========
Controller:WaterCoil,
DOAS CoolingCoil Controller, !- Name
Temperature, !- Control Variable
Reverse, !- Action
Flow, !- Actuator Variable
DOAS CoolingCoil Air Outlet Node, !- Sensor Node Name
DOAS CoolingCoil CHW Inlet Node, !- Actuator Node Name
autosize, !- Controller Convergence Tolerance {deltaC}
autosize, !- Maximum Actuated Flow {m3/s}
0; !- Minimum Actuated Flow {m3/s}
Controller:WaterCoil,
DOAS Precool CoolingCoil Controller, !- Name
Temperature, !- Control Variable
Reverse, !- Action
Flow, !- Actuator Variable
DOAS Precool CoolingCoil Air Outlet Node, !- Sensor Node Name
DOAS Precool CoolingCoil CHW Inlet Node, !- Actuator Node Name
autosize, !- Controller Convergence Tolerance {deltaC}
autosize, !- Maximum Actuated Flow {m3/s}
0; !- Minimum Actuated Flow {m3/s}
Controller:WaterCoil,
DOAS HeatingCoil Controller, !- Name
Temperature, !- Control Variable
Normal, !- Action
Flow, !- Actuator Variable
DOAS AirLpSplSide Outlet Node, !- Sensor Node Name
DOAS HeatingCoil HW Inlet Node, !- Actuator Node Name
autosize, !- Controller Convergence Tolerance {deltaC}
autosize, !- Maximum Actuated Flow {m3/s}
0; !- Minimum Actuated Flow {m3/s}
Controller:WaterCoil,
DOAS Preheat HeatingCoil Controller, !- Name
Temperature, !- Control Variable
Normal, !- Action
Flow, !- Actuator Variable
DOAS Preheat HeatingCoil Air Outlet Node, !- Sensor Node Name
DOAS Preheat HeatingCoil HW Inlet Node, !- Actuator Node Name
autosize, !- Controller Convergence Tolerance {deltaC}
autosize, !- Maximum Actuated Flow {m3/s}
0; !- Minimum Actuated Flow {m3/s}
!- =========== ALL OBJECTS IN CLASS: CONTROLLER:OUTDOORAIR ===========
Controller:OutdoorAir,
DOAS OA Controller, !- Name
DOAS OA Mixer ExhaustNd, !- Relief Air Outlet Node Name
DOAS AirLpSplSide Inlet Node, !- Return Air Node Name
DOAS OA Mixer Outlet Node, !- Mixed Air Node Name
DOAS OA Inlet Node, !- Actuator Node Name
0.083, !- Minimum Outdoor Air Flow Rate {m3/s}
0.083, !- Maximum Outdoor Air Flow Rate {m3/s}
NoEconomizer, !- Economizer Control Type
, !- Economizer Control Action Type
, !- Economizer Maximum Limit Dry-Bulb Temperature {C}
, !- Economizer Maximum Limit Enthalpy {J/kg}
, !- Economizer Maximum Limit Dewpoint Temperature {C}
, !- Electronic Enthalpy Limit Curve Name
, !- Economizer Minimum Limit Dry-Bulb Temperature {C}
NoLockout, !- Lockout Type
FixedMinimum, !- Minimum Limit Type
Office Occupancy For OA, !- Minimum Outdoor Air Schedule Name
Office Occupancy For OA, !- Minimum Fraction of Outdoor Air Schedule Name
, !- Maximum Fraction of Outdoor Air Schedule Name
Controller MV, !- Mechanical Ventilation Controller Name
, !- Time of Day Economizer Control Schedule Name
No, !- High Humidity Control
, !- Humidistat Control Zone Name
1, !- High Humidity Outdoor Air Flow Ratio
Yes; !- Control High Indoor Humidity Based on Outdoor Humidity Ratio
!- =========== ALL OBJECTS IN CLASS: CONTROLLER:MECHANICALVENTILATION ===========
Controller:MechanicalVentilation,
Controller MV, !- Name
Office Occupancy For OA, !- Availability Schedule Name
Sum, !- Zone Outdoor Air Method
ZoneSum, !- System Outdoor Air Method
ZONE1, !- Zone 1 Name
0, !- Ventilation Rate per Unit Floor Area 1 {m3/s-m2}
0.0083, !- Ventilation Rate per Occupant 1 {m3/s-person}
1, !- Zone Air Distribution Effectiveness in Cooling Mode 1 {dimensionless}
1, !- Zone Air Distribution Effectiveness in Heating Mode 1 {dimensionless}
; !- Zone Air Distribution Effectiveness Schedule Name 1
!- =========== ALL OBJECTS IN CLASS: AIRLOOPHVAC:CONTROLLERLIST ===========
AirLoopHVAC:ControllerList,
DOAS OA CHW HW Coil Controller List, !- Name
Controller:WaterCoil, !- Controller 1 Object Type
DOAS CoolingCoil Controller, !- Controller 1 Name
Controller:WaterCoil, !- Controller 2 Object Type
DOAS HeatingCoil Controller; !- Controller 2 Name
AirLoopHVAC:ControllerList,
DOAS OA System Controller List, !- Name
Controller:OutdoorAir, !- Controller 1 Object Type
DOAS OA Controller, !- Controller 1 Name
Controller:WaterCoil, !- Controller 2 Object Type
DOAS Precool CoolingCoil Controller, !- Controller 2 Name
Controller:WaterCoil, !- Controller 3 Object Type
DOAS Preheat HeatingCoil Controller; !- Controller 3 Name
!- =========== ALL OBJECTS IN CLASS: AIRLOOPHVAC ===========
AirLoopHVAC,
DOAS AirLoop, !- Name
DOAS OA CHW HW Coil Controller List, !- Controller List Name
DOAS System Availability Managers List, !- Availability Manager List Name
autosize, !- Design Supply Air Flow Rate {m3/s}
DOAS AirLpSplSide Branch List, !- Branch List Name
, !- Connector List Name
DOAS AirLpSplSide Inlet Node, !- Supply Side Inlet Node Name
DOAS AirLpDmdSide Outlet Node, !- Demand Side Outlet Node Name
DOAS AirLpDmdSide Inlet Node, !- Demand Side Inlet Node Names
DOAS AirLpSplSide Outlet Node; !- Supply Side Outlet Node Names
!- =========== ALL OBJECTS IN CLASS: AIRLOOPHVAC:OUTDOORAIRSYSTEM:EQUIPMENTLIST ===========
AirLoopHVAC:OutdoorAirSystem:EquipmentList,
DOAS OA System Equipment List, !- Name
Coil:Cooling:Water, !- Component 1 Object Type
DOAS Precool CoolingCoil,!- Component 1 Name
Coil:Heating:Water, !- Component 2 Object Type
DOAS Preheat HeatingCoil,!- Component 2 Name
OutdoorAir:Mixer, !- Component 3 Object Type
DOAS OA Mixer; !- Component 3 Name
!- =========== ALL OBJECTS IN CLASS: AIRLOOPHVAC:OUTDOORAIRSYSTEM ===========
AirLoopHVAC:OutdoorAirSystem,
DOAS OA System Equipment,!- Name
DOAS OA System Controller List, !- Controller List Name
DOAS OA System Equipment List, !- Outdoor Air Equipment List Name
DOAS System Availability Managers List; !- Availability Manager List Name
!- =========== ALL OBJECTS IN CLASS: OUTDOORAIR:MIXER ===========
OutdoorAir:Mixer,
DOAS OA Mixer, !- Name
DOAS OA Mixer Outlet Node, !- Mixed Air Node Name
DOAS Preheat HeatingCoil Air Outlet Node, !- Outdoor Air Stream Node Name
DOAS OA Mixer ExhaustNd, !- Relief Air Stream Node Name
DOAS AirLpSplSide Inlet Node; !- Return Air Stream Node Name
!- =========== ALL OBJECTS IN CLASS: AIRLOOPHVAC:ZONESPLITTER ===========
AirLoopHVAC:ZoneSplitter,
DOAS Splitter, !- Name
DOAS AirLpDmdSide Inlet Node, !- Inlet Node Name
DOAS Zone1 Inlet Node; !- Outlet 1 Node Name
!- =========== ALL OBJECTS IN CLASS: AIRLOOPHVAC:SUPPLYPATH ===========
AirLoopHVAC:SupplyPath,
DOAS AirSplPath, !- Name
DOAS AirLpDmdSide Inlet Node, !- Supply Air Path Inlet Node Name
AirLoopHVAC:ZoneSplitter,!- Component 1 Object Type
DOAS Splitter; !- Component 1 Name
!- =========== ALL OBJECTS IN CLASS: AIRLOOPHVAC:ZONEMIXER ===========
AirLoopHVAC:ZoneMixer,
AirLpDmdSide Return Mixer, !- Name
DOAS AirLpDmdSide Outlet Node, !- Outlet Node Name
Zone1 Outlet Node; !- Inlet 1 Node Name
!- =========== ALL OBJECTS IN CLASS: AIRLOOPHVAC:RETURNPATH ===========
AirLoopHVAC:ReturnPath,
RtnPath, !- Name
DOAS AirLpDmdSide Outlet Node, !- Return Air Path Outlet Node Name
AirLoopHVAC:ZoneMixer, !- Component 1 Object Type
AirLpDmdSide Return Mixer; !- Component 1 Name
!- =========== ALL OBJECTS IN CLASS: BRANCH ===========
!*******For a DOAS CoolingCoil and HeatingCoil, them Water Pipe branch, Starting
Branch,
DOAS CoolingCoil CHW Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Coil:Cooling:Water, !- Component 1 Object Type
DOAS CoolingCoil, !- Component 1 Name
DOAS CoolingCoil CHW Inlet Node, !- Component 1 Inlet Node Name
DOAS CoolingCoil CHW Outlet Node, !- Component 1 Outlet Node Name
Active; !- Component 1 Branch Control Type
Branch,
DOAS HeatingCoil HW Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Coil:Heating:Water, !- Component 1 Object Type
DOAS HeatingCoil, !- Component 1 Name
DOAS HeatingCoil HW Inlet Node, !- Component 1 Inlet Node Name
DOAS HeatingCoil HW Outlet Node, !- Component 1 Outlet Node Name
Active; !- Component 1 Branch Control Type
!*******For a DOAS Precool CoolingCoil and Preheat HeatingCoil, them Water Pipe branch, Starting
Branch,
DOAS Precool CoolingCoil CHW Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Coil:Cooling:Water, !- Component 1 Object Type
DOAS Precool CoolingCoil,!- Component 1 Name
DOAS Precool CoolingCoil CHW Inlet Node, !- Component 1 Inlet Node Name
DOAS Precool CoolingCoil CHW Outlet Node, !- Component 1 Outlet Node Name
Active; !- Component 1 Branch Control Type
Branch,
DOAS Preheat HeatingCoil HW Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Coil:Heating:Water, !- Component 1 Object Type
DOAS Preheat HeatingCoil,!- Component 1 Name
DOAS Preheat HeatingCoil HW Inlet Node, !- Component 1 Inlet Node Name
DOAS Preheat HeatingCoil HW Outlet Node, !- Component 1 Outlet Node Name
Active; !- Component 1 Branch Control Type
!*******For PlantLpDmdSide CHW (Inlet, Outlet & Bypass) Branch without the Zone equipment Branch, Starting
Branch,
PlantLpDmdSide CHW Inlet Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
PlantLpDmdSide CHW Inlet Pipe, !- Component 1 Name
PlantLpDmdSide CHW Inlet Node, !- Component 1 Inlet Node Name
PlantLpDmdSide CHW Inlet Pipe Outlet Node, !- Component 1 Outlet Node Name
Passive; !- Component 1 Branch Control Type
Branch,
PlantLpDmdSide CHW Outlet Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
PlantLpDmdSide CHW Outlet Pipe, !- Component 1 Name
PlantLpDmdSide CHW Outlet Pipe Inlet Node, !- Component 1 Inlet Node Name
PlantLpDmdSide CHW Outlet Node, !- Component 1 Outlet Node Name
Passive; !- Component 1 Branch Control Type
Branch,
PlantLpDmdSide CHW Bypass Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
PlantLpDmdSide CHW Bypass Pipe, !- Component 1 Name
PlantLpDmdSide CHW Bypass Pipe Inlet Node, !- Component 1 Inlet Node Name
PlantLpDmdSide CHW Bypass Pipe Outlet Node, !- Component 1 Outlet Node Name
Passive; !- Component 1 Branch Control Type
!*******For PlantLpDmdSide Radiant CHW (Inlet, Outlet & Bypass) Branch without the Zone equipment Branch, Starting
Branch,
PlantLpDmdSide Radiant CHW Inlet Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
PlantLpDmdSide Radiant CHW Inlet Pipe, !- Component 1 Name
PlantLpDmdSide Radiant CHW Inlet Node, !- Component 1 Inlet Node Name
PlantLpDmdSide Radiant CHW Inlet Pipe Outlet Node, !- Component 1 Outlet Node Name
Passive; !- Component 1 Branch Control Type
Branch,
PlantLpDmdSide Radiant CHW Outlet Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
PlantLpDmdSide Radiant CHW Outlet Pipe, !- Component 1 Name
PlantLpDmdSide Radiant CHW Outlet Pipe Inlet Node, !- Component 1 Inlet Node Name
PlantLpDmdSide Radiant CHW Outlet Node, !- Component 1 Outlet Node Name
Passive; !- Component 1 Branch Control Type
Branch,
PlantLpDmdSide Radiant CHW Bypass Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
PlantLpDmdSide Radiant CHW Bypass Pipe, !- Component 1 Name
PlantLpDmdSide Radiant CHW Bypass Pipe Inlet Node, !- Component 1 Inlet Node Name
PlantLpDmdSide Radiant CHW Bypass Pipe Outlet Node, !- Component 1 Outlet Node Name
Passive; !- Component 1 Branch Control Type
!*******For PlantLpDmdSide HW (Inlet, Outlet & Bypass) Branch without the Zone equipment Branch, Starting
Branch,
PlantLpDmdSide HW Inlet Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
PlantLpDmdSide HW Inlet Pipe, !- Component 1 Name
PlantLpDmdSide HW Inlet Node, !- Component 1 Inlet Node Name
PlantLpDmdSide HW Inlet Pipe Outlet Node, !- Component 1 Outlet Node Name
Passive; !- Component 1 Branch Control Type
Branch,
PlantLpDmdSide HW Outlet Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
PlantLpDmdSide HW Outlet Pipe, !- Component 1 Name
PlantLpDmdSide HW Outlet Pipe Inlet Node, !- Component 1 Inlet Node Name
PlantLpDmdSide HW Outlet Node, !- Component 1 Outlet Node Name
Passive; !- Component 1 Branch Control Type
Branch,
PlantLpDmdSide HW Bypass Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
PlantLpDmdSide HW Bypass Pipe, !- Component 1 Name
PlantLpDmdSide HW Bypass Pipe Inlet Node, !- Component 1 Inlet Node Name
PlantLpDmdSide HW Bypass Pipe Outlet Node, !- Component 1 Outlet Node Name
Passive; !- Component 1 Branch Control Type
!*******For PlantLpSplSide CHW (Inlet with HeaderedPump, Outlet, Bypass & Chiller1 Evaporator) Branch with the Plant equipment Branch, Starting
Branch,
PlantLpSplSide CHW Inlet Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pump:VariableSpeed, !- Component 1 Object Type
CHW Pump1, !- Component 1 Name
PlantLpSplSide CHW Inlet Node, !- Component 1 Inlet Node Name
CHW Pump1 Outlet Node, !- Component 1 Outlet Node Name
Active; !- Component 1 Branch Control Type
Branch,
PlantLpSplSide CHW Outlet Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
PlantLpSplSide CHW Outlet Pipe, !- Component 1 Name
PlantLpSplSide CHW Outlet Pipe Inlet Node, !- Component 1 Inlet Node Name
PlantLpSplSide CHW Outlet Node, !- Component 1 Outlet Node Name
Passive; !- Component 1 Branch Control Type
Branch,
PlantLpSplSide CHW Chiller1 Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Chiller:Electric, !- Component 1 Object Type
PlantLpSplSide CHW Chiller1, !- Component 1 Name
PlantLpSplSide CHW Chiller1 Inlet Node, !- Component 1 Inlet Node Name
PlantLpSplSide CHW Chiller1 Outlet Node, !- Component 1 Outlet Node Name
Active; !- Component 1 Branch Control Type
!*******For PlantLpSplSide Radiant CHW (Inlet with HeaderedPump, Outlet, Bypass & Chiller1 Evaporator) Branch with the Plant equipment Branch, Starting
Branch,
PlantLpSplSide Radiant CHW Inlet Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pump:VariableSpeed, !- Component 1 Object Type
Radiant CHW Pump1, !- Component 1 Name
PlantLpSplSide Radiant CHW Inlet Node, !- Component 1 Inlet Node Name
Radiant CHW Pump1 Outlet Node, !- Component 1 Outlet Node Name
Active; !- Component 1 Branch Control Type
Branch,
PlantLpSplSide Radiant CHW Outlet Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
PlantLpSplSide Radiant CHW Outlet Pipe, !- Component 1 Name
PlantLpSplSide Radiant CHW Outlet Pipe Inlet Node, !- Component 1 Inlet Node Name
PlantLpSplSide Radiant CHW Outlet Node, !- Component 1 Outlet Node Name
Passive; !- Component 1 Branch Control Type
Branch,
PlantLpSplSide Radiant CHW Chiller1 Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Chiller:Electric, !- Component 1 Object Type
PlantLpSplSide Radiant CHW Chiller1, !- Component 1 Name
PlantLpSplSide Radiant CHW Chiller1 Inlet Node, !- Component 1 Inlet Node Name
PlantLpSplSide Radiant CHW Chiller1 Outlet Node, !- Component 1 Outlet Node Name
Active; !- Component 1 Branch Control Type
!Branch,
! PlantLpSplSide CHW Bypass Branch, !- Name
! autosize, !- Maximum Flow Rate {m3/s}
! Pipe:Adiabatic, !- Component 1 Object Type
! PlantLpSplSide CHW Bypass Pipe, !- Component 1 Name
! PlantLpSplSide CHW Bypass Pipe Inlet Node, !- Component 1 Inlet Node Name
! PlantLpSplSide CHW Bypass Pipe Outlet Node, !- Component 1 Outlet Node Name
! Passive; !- Component 1 Branch Control Type
!*******For PlantLpSplSide HW (Inlet with HeaderedPump, Outlet, Bypass & Boiler1) Branch with the plant equipment Branch, Starting
Branch,
PlantLpSplSide HW Inlet Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pump:VariableSpeed, !- Component 1 Object Type
HW Pump1, !- Component 1 Name
PlantLpSplSide HW Inlet Node, !- Component 1 Inlet Node Name
HW Pump1 Outlet Node, !- Component 1 Outlet Node Name
Active; !- Component 1 Branch Control Type
Branch,
PlantLpSplSide HW Outlet Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
PlantLpSplSide HW Outlet Pipe, !- Component 1 Name
PlantLpSplSide HW Outlet Pipe Inlet Node, !- Component 1 Inlet Node Name
PlantLpSplSide HW Outlet Node, !- Component 1 Outlet Node Name
Passive; !- Component 1 Branch Control Type
Branch,
PlantLpSplSide HW Boiler1 Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Boiler:HotWater, !- Component 1 Object Type
PlantLpSplSide HW Boiler1, !- Component 1 Name
PlantLpSplSide HW Boiler1 Inlet Node, !- Component 1 Inlet Node Name
PlantLpSplSide HW Boiler1 Outlet Node, !- Component 1 Outlet Node Name
Active; !- Component 1 Branch Control Type
Branch,
PlantLpSplSide HW Bypass Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Pipe:Adiabatic, !- Component 1 Object Type
PlantLpSplSide HW Bypass Pipe, !- Component 1 Name
PlantLpSplSide HW Bypass Pipe Inlet Node, !- Component 1 Inlet Node Name
PlantLpSplSide HW Bypass Pipe Outlet Node, !- Component 1 Outlet Node Name
Passive; !- Component 1 Branch Control Type
!*******For DOAS System the outdoor Stream, Starting
Branch,
DOAS AirLpSplSide Branch,!- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
AirLoopHVAC:OutdoorAirSystem, !- Component 1 Object Type
DOAS OA System Equipment,!- Component 1 Name
DOAS AirLpSplSide Inlet Node, !- Component 1 Inlet Node Name
DOAS OA Mixer Outlet Node, !- Component 1 Outlet Node Name
Active, !- Component 1 Branch Control Type
Fan:VariableVolume, !- Component 2 Object Type
DOAS Fan, !- Component 2 Name
DOAS OA Mixer Outlet Node, !- Component 2 Inlet Node Name
DOAS Fan Outlet Node, !- Component 2 Outlet Node Name
Active, !- Component 2 Branch Control Type
Coil:Cooling:Water, !- Component 3 Object Type
DOAS CoolingCoil, !- Component 3 Name
DOAS Fan Outlet Node, !- Component 3 Inlet Node Name
DOAS CoolingCoil Air Outlet Node, !- Component 3 Outlet Node Name
SeriesActive, !- Component 3 Branch Control Type
Coil:Heating:Water, !- Component 4 Object Type
DOAS HeatingCoil, !- Component 4 Name
DOAS CoolingCoil Air Outlet Node, !- Component 4 Inlet Node Name
DOAS AirLpSplSide Outlet Node, !- Component 4 Outlet Node Name
SeriesActive; !- Component 4 Branch Control Type
Branch,
CRCP1 CHW Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
ZoneHVAC:LowTemperatureRadiant:VariableFlow, !- Component 1 Object Type
CRCP1, !- Component 1 Name
CRCP1 CHW Inlet Node, !- Component 1 Inlet Node Name
CRCP1 CHW Outlet Node, !- Component 1 Outlet Node Name
Active; !- Component 1 Branch Control Type
Branch,
CRCP1 HW Branch, !- Name
autosize, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
ZoneHVAC:LowTemperatureRadiant:VariableFlow, !- Component 1 Object Type
CRCP1, !- Component 1 Name
CRCP1 HW Inlet Node, !- Component 1 Inlet Node Name
CRCP1 HW Outlet Node, !- Component 1 Outlet Node Name
Active; !- Component 1 Branch Control Type
!- =========== ALL OBJECTS IN CLASS: BRANCHLIST ===========
BranchList,
PlantLpDmdSide CHW Branch List, !- Name
PlantLpDmdSide CHW Inlet Branch, !- Branch 1 Name
DOAS CoolingCoil CHW Branch, !- Branch 2 Name
DOAS Precool CoolingCoil CHW Branch, !- Branch 3 Name
PlantLpDmdSide CHW Bypass Branch, !- Branch 4 Name
PlantLpDmdSide CHW Outlet Branch; !- Branch 5 Name
BranchList,
PlantLpDmdSide Radiant CHW Branch List, !- Name
PlantLpDmdSide Radiant CHW Inlet Branch, !- Branch 1 Name
CRCP1 CHW Branch, !- Branch 2 Name
PlantLpDmdSide Radiant CHW Bypass Branch, !- Branch 3 Name
PlantLpDmdSide Radiant CHW Outlet Branch; !- Branch 4 Name
BranchList,
PlantLpDmdSide HW Branch List, !- Name
PlantLpDmdSide HW Inlet Branch, !- Branch 1 Name
DOAS HeatingCoil HW Branch, !- Branch 2 Name
DOAS Preheat HeatingCoil HW Branch, !- Branch 3 Name
CRCP1 HW Branch, !- Branch 4 Name
PlantLpDmdSide HW Bypass Branch, !- Branch 5 Name
PlantLpDmdSide HW Outlet Branch; !- Branch 6 Name
BranchList,
PlantLpSplSide CHW Branch List, !- Name
PlantLpSplSide CHW Inlet Branch, !- Branch 1 Name
PlantLpSplSide CHW Chiller1 Branch, !- Branch 2 Name
PlantLpSplSide CHW Outlet Branch; !- Branch 3 Name
BranchList,
PlantLpSplSide Radiant CHW Branch List, !- Name
PlantLpSplSide Radiant CHW Inlet Branch, !- Branch 1 Name
PlantLpSplSide Radiant CHW Chiller1 Branch, !- Branch 2 Name
PlantLpSplSide Radiant CHW Outlet Branch; !- Branch 3 Name
BranchList,
PlantLpSplSide HW Branch List, !- Name
PlantLpSplSide HW Inlet Branch, !- Branch 1 Name
PlantLpSplSide HW Boiler1 Branch, !- Branch 2 Name
PlantLpSplSide HW Bypass Branch, !- Branch 3 Name
PlantLpSplSide HW Outlet Branch; !- Branch 4 Name
BranchList,
DOAS AirLpSplSide Branch List, !- Name
DOAS AirLpSplSide Branch;!- Branch 1 Name
!- =========== ALL OBJECTS IN CLASS: CONNECTOR:SPLITTER ===========
!*******PlantLpDmdSide CHW & HW Splitter, Starting
Connector:Splitter,
PlantLpDmdSide CHW Splitter, !- Name
PlantLpDmdSide CHW Inlet Branch, !- Inlet Branch Name
DOAS CoolingCoil CHW Branch, !- Outlet Branch 1 Name
DOAS Precool CoolingCoil CHW Branch, !- Outlet Branch 2 Name
PlantLpDmdSide CHW Bypass Branch; !- Outlet Branch 3 Name
Connector:Splitter,
PlantLpDmdSide Radiant CHW Splitter, !- Name
PlantLpDmdSide Radiant CHW Inlet Branch, !- Inlet Branch Name
CRCP1 CHW Branch, !- Outlet Branch 1 Name
PlantLpDmdSide Radiant CHW Bypass Branch; !- Outlet Branch 2 Name
Connector:Splitter,
PlantLpDmdSide HW Splitter, !- Name
PlantLpDmdSide HW Inlet Branch, !- Inlet Branch Name
DOAS HeatingCoil HW Branch, !- Outlet Branch 1 Name
DOAS Preheat HeatingCoil HW Branch, !- Outlet Branch 2 Name
CRCP1 HW Branch, !- Outlet Branch 3 Name
PlantLpDmdSide HW Bypass Branch; !- Outlet Branch 4 Name
!*******PlantLpSplSide CHW & HW Splitter, Starting
Connector:Splitter,
PlantLpSplSide CHW Splitter, !- Name
PlantLpSplSide CHW Inlet Branch, !- Inlet Branch Name
PlantLpSplSide CHW Chiller1 Branch; !- Outlet Branch 1 Name
Connector:Splitter,
PlantLpSplSide Radiant CHW Splitter, !- Name
PlantLpSplSide Radiant CHW Inlet Branch, !- Inlet Branch Name
PlantLpSplSide Radiant CHW Chiller1 Branch; !- Outlet Branch 1 Name
! PlantLpSplSide CHW Bypass Branch; !- Outlet Branch 2 Name
Connector:Splitter,
PlantLpSplSide HW Splitter, !- Name
PlantLpSplSide HW Inlet Branch, !- Inlet Branch Name
PlantLpSplSide HW Boiler1 Branch, !- Outlet Branch 1 Name
PlantLpSplSide HW Bypass Branch; !- Outlet Branch 2 Name
!- =========== ALL OBJECTS IN CLASS: CONNECTOR:MIXER ===========
!*******PlantLpDmdSide CHW & HW Mixer, Starting
Connector:Mixer,
PlantLpDmdSide CHW Mixer,!- Name
PlantLpDmdSide CHW Outlet Branch, !- Outlet Branch Name
DOAS CoolingCoil CHW Branch, !- Inlet Branch 1 Name
DOAS Precool CoolingCoil CHW Branch, !- Inlet Branch 2 Name
PlantLpDmdSide CHW Bypass Branch; !- Inlet Branch 3 Name
Connector:Mixer,
PlantLpDmdSide Radiant CHW Mixer, !- Name
PlantLpDmdSide Radiant CHW Outlet Branch, !- Outlet Branch Name
CRCP1 CHW Branch, !- Inlet Branch 1 Name
PlantLpDmdSide Radiant CHW Bypass Branch; !- Inlet Branch 2 Name
Connector:Mixer,
PlantLpDmdSide HW Mixer, !- Name
PlantLpDmdSide HW Outlet Branch, !- Outlet Branch Name
DOAS HeatingCoil HW Branch, !- Inlet Branch 1 Name
DOAS Preheat HeatingCoil HW Branch, !- Inlet Branch 2 Name
CRCP1 HW Branch, !- Inlet Branch 3 Name
PlantLpDmdSide HW Bypass Branch; !- Inlet Branch 4 Name
!*******PlantLpSplSide CHW & HW Mixer, Starting
Connector:Mixer,
PlantLpSplSide CHW Mixer,!- Name
PlantLpSplSide CHW Outlet Branch, !- Outlet Branch Name
PlantLpSplSide CHW Chiller1 Branch; !- Inlet Branch 1 Name
Connector:Mixer,
PlantLpSplSide Radiant CHW Mixer, !- Name
PlantLpSplSide Radiant CHW Outlet Branch, !- Outlet Branch Name
PlantLpSplSide Radiant CHW Chiller1 Branch; !- Inlet Branch 1 Name
! PlantLpSplSide CHW Bypass Branch; !- Outlet Branch 2 Name
Connector:Mixer,
PlantLpSplSide HW Mixer, !- Name
PlantLpSplSide HW Outlet Branch, !- Outlet Branch Name
PlantLpSplSide HW Boiler1 Branch, !- Inlet Branch 1 Name
PlantLpSplSide HW Bypass Branch; !- Inlet Branch 2 Name
!- =========== ALL OBJECTS IN CLASS: CONNECTORLIST ===========
!*******PlantLpDmdSide CHW & HW Connector, Starting
ConnectorList,
PlantLpDmdSide CHW Connector List, !- Name
Connector:Splitter, !- Connector 1 Object Type
PlantLpDmdSide CHW Splitter, !- Connector 1 Name
Connector:Mixer, !- Connector 2 Object Type
PlantLpDmdSide CHW Mixer;!- Connector 2 Name
ConnectorList,
PlantLpDmdSide Radiant CHW Connector List, !- Name
Connector:Splitter, !- Connector 1 Object Type
PlantLpDmdSide Radiant CHW Splitter, !- Connector 1 Name
Connector:Mixer, !- Connector 2 Object Type
PlantLpDmdSide Radiant CHW Mixer; !- Connector 2 Name
ConnectorList,
PlantLpDmdSide HW Connector List, !- Name
Connector:Splitter, !- Connector 1 Object Type
PlantLpDmdSide HW Splitter, !- Connector 1 Name
Connector:Mixer, !- Connector 2 Object Type
PlantLpDmdSide HW Mixer; !- Connector 2 Name
!*******PlantLpDmdSide CHW & HW Connector, Starting
ConnectorList,
PlantLpSplSide CHW Connector List, !- Name
Connector:Splitter, !- Connector 1 Object Type
PlantLpSplSide CHW Splitter, !- Connector 1 Name
Connector:Mixer, !- Connector 2 Object Type
PlantLpSplSide CHW Mixer;!- Connector 2 Name
ConnectorList,
PlantLpSplSide Radiant CHW Connector List, !- Name
Connector:Splitter, !- Connector 1 Object Type
PlantLpSplSide Radiant CHW Splitter, !- Connector 1 Name
Connector:Mixer, !- Connector 2 Object Type
PlantLpSplSide Radiant CHW Mixer; !- Connector 2 Name
ConnectorList,
PlantLpSplSide HW Connector List, !- Name
Connector:Splitter, !- Connector 1 Object Type
PlantLpSplSide HW Splitter, !- Connector 1 Name
Connector:Mixer, !- Connector 2 Object Type
PlantLpSplSide HW Mixer; !- Connector 2 Name
!- =========== ALL OBJECTS IN CLASS: NODELIST ===========
NodeList,
Outdoor Air Inlet Node List, !- Name
DOAS OA Inlet Node; !- Node 1 Name
NodeList,
Zone1 Air Inlet Node List, !- Name
DOAS Zone1 Inlet Node; !- Node 1 Name
!- =========== ALL OBJECTS IN CLASS: OUTDOORAIR:NODE ===========
OutdoorAir:Node,
PlantLpSplSide CHW Chiller1 Condenser Inlet Node, !- Name
4; !- Height Above Ground {m}
OutdoorAir:Node,
PlantLpSplSide Radiant CHW Chiller1 Condenser Inlet Node, !- Name
4; !- Height Above Ground {m}
!- =========== ALL OBJECTS IN CLASS: OUTDOORAIR:NODELIST ===========
OutdoorAir:NodeList,
Outdoor Air Inlet Node List; !- Node or NodeList Name 1
!- =========== ALL OBJECTS IN CLASS: PUMP:VARIABLESPEED ===========
!Pump:VariableSpeed,
! Condenser Pump1, !- Name
! CondenserLpSplSide Inlet Node, !- Inlet Node Name
! Condenser Pump1 Outlet Node, !- Outlet Node Name
! autosize, !- Rated Flow Rate {m3/s}
! 179352, !- Rated Pump Head {Pa}
! autosize, !- Rated Power Consumption {W}
! 0.9, !- Motor Efficiency
! 0.0, !- Fraction of Motor Inefficiencies to Fluid Stream
! 0, !- Coefficient 1 of the Part Load Performance Curve
! 1, !- Coefficient 2 of the Part Load Performance Curve
! 0, !- Coefficient 3 of the Part Load Performance Curve
! 0, !- Coefficient 4 of the Part Load Performance Curve
! 0, !- Minimum Flow Rate {m3/s}
! INTERMITTENT, !- Pump Control Type
! ON; !- Pump Flow Rate Schedule Name
!HeaderedPumps:ConstantSpeed,
! CHW Pump1, !- Name
! PlantLpSplSide CHW Inlet Node, !- Inlet Node Name
! CHW Pump1 Outlet Node, !- Outlet Node Name
! autosize, !- Total Rated Flow Rate {m3/s}
! 1, !- Number of Pumps in Bank
! Sequential, !- Flow Sequencing Control Scheme
! 179352, !- Rated Pump Head {Pa}
! autosize, !- Rated Power Consumption {W}
! 0.9, !- Motor Efficiency
! , !- Fraction of Motor Inefficiencies to Fluid Stream
! Continuous; !- Pump Control Type
!HeaderedPumps:ConstantSpeed,
! HW Pump1, !- Name
! PlantLpSplSide HW Inlet Node, !- Inlet Node Name
! HW Pump1 Outlet Node, !- Outlet Node Name
! autosize, !- Total Rated Flow Rate {m3/s}
! 1, !- Number of Pumps in Bank
! Sequential, !- Flow Sequencing Control Scheme
! 179352, !- Rated Pump Head {Pa}
! autosize, !- Rated Power Consumption {W}
! 0.9, !- Motor Efficiency
! , !- Fraction of Motor Inefficiencies to Fluid Stream
! Continuous; !- Pump Control Type
Pump:VariableSpeed,
CHW Pump1, !- Name
PlantLpSplSide CHW Inlet Node, !- Inlet Node Name
CHW Pump1 Outlet Node, !- Outlet Node Name
autosize, !- Rated Flow Rate {m3/s}
179352, !- Rated Pump Head {Pa}
autosize, !- Rated Power Consumption {W}
0.9, !- Motor Efficiency
0.0, !- Fraction of Motor Inefficiencies to Fluid Stream
0, !- Coefficient 1 of the Part Load Performance Curve
1, !- Coefficient 2 of the Part Load Performance Curve
0, !- Coefficient 3 of the Part Load Performance Curve
0, !- Coefficient 4 of the Part Load Performance Curve
0, !- Minimum Flow Rate {m3/s}
INTERMITTENT; !- Pump Control Type
Pump:VariableSpeed,
HW Pump1, !- Name
PlantLpSplSide HW Inlet Node, !- Inlet Node Name
HW Pump1 Outlet Node, !- Outlet Node Name
autosize, !- Rated Flow Rate {m3/s}
179352, !- Rated Pump Head {Pa}
autosize, !- Rated Power Consumption {W}
0.9, !- Motor Efficiency
0.0, !- Fraction of Motor Inefficiencies to Fluid Stream
0, !- Coefficient 1 of the Part Load Performance Curve
1, !- Coefficient 2 of the Part Load Performance Curve
0, !- Coefficient 3 of the Part Load Performance Curve
0, !- Coefficient 4 of the Part Load Performance Curve
0, !- Minimum Flow Rate {m3/s}
INTERMITTENT; !- Pump Control Type
Pump:VariableSpeed,
Radiant CHW Pump1, !- Name
PlantLpSplSide Radiant CHW Inlet Node, !- Inlet Node Name
Radiant CHW Pump1 Outlet Node, !- Outlet Node Name
autosize, !- Rated Flow Rate {m3/s}
179352, !- Rated Pump Head {Pa}
autosize, !- Rated Power Consumption {W}
0.9, !- Motor Efficiency
0.0, !- Fraction of Motor Inefficiencies to Fluid Stream
0, !- Coefficient 1 of the Part Load Performance Curve
1, !- Coefficient 2 of the Part Load Performance Curve
0, !- Coefficient 3 of the Part Load Performance Curve
0, !- Coefficient 4 of the Part Load Performance Curve
0, !- Minimum Flow Rate {m3/s}
INTERMITTENT; !- Pump Control Type
!- =========== ALL OBJECTS IN CLASS: BOILER:HOTWATER ===========
Boiler:HotWater,
PlantLpSplSide HW Boiler1, !- Name
Electricity, !- Fuel Type
autosize, !- Nominal Capacity {W}
0.8, !- Nominal Thermal Efficiency
BoilerEfficiency, !- Normalized Boiler Efficiency Curve Name
60, !- Design Water Outlet Temperature {C}
autosize, !- Design Water Flow Rate {m3/s}
0.0, !- Minimum Part Load Ratio
1.2, !- Maximum Part Load Ratio
1.0, !- Optimum Part Load Ratio
PlantLpSplSide HW Boiler1 Inlet Node, !- Boiler Water Inlet Node Name
PlantLpSplSide HW Boiler1 Outlet Node, !- Boiler Water Outlet Node Name
100., !- Water Outlet Upper Temperature Limit {C}
VariableFlow; !- Boiler Flow Mode
!- =========== ALL OBJECTS IN CLASS: CHILLER:ELECTRIC ===========
! Chiller for DOAS Precoll
Chiller:Electric,
PlantLpSplSide CHW Chiller1, !- Name
AirCooled, !- Condenser Type
autosize, !- Nominal Capacity {W}
3.2, !- Nominal COP
PlantLpSplSide CHW Chiller1 Inlet Node, !- Chilled Water Inlet Node Name
PlantLpSplSide CHW Chiller1 Outlet Node, !- Chilled Water Outlet Node Name
PlantLpSplSide CHW Chiller1 Condenser Inlet Node, !- Condenser Inlet Node Name
PlantLpSplSide CHW Chiller1 Condenser Outlet Node, !- Condenser Outlet Node Name
0.0, !- Minimum Part Load Ratio
1.0, !- Maximum Part Load Ratio
0.65, !- Optimum Part Load Ratio
35.0, !- Design Condenser Inlet Temperature {C}
2.778, !- Temperature Rise Coefficient
5.22, !- Design Chilled Water Outlet Temperature {C}
autosize, !- Design Chilled Water Flow Rate {m3/s}
autosize, !- Design Condenser Water Flow Rate {m3/s}
0.9949, !- Coefficient 1 of Capacity Ratio Curve
-0.045954, !- Coefficient 2 of Capacity Ratio Curve
-0.0013543, !- Coefficient 3 of Capacity Ratio Curve
2.333, !- Coefficient 1 of Power Ratio Curve
-1.975, !- Coefficient 2 of Power Ratio Curve
0.6121, !- Coefficient 3 of Power Ratio Curve
0.03303, !- Coefficient 1 of Full Load Ratio Curve
0.6852, !- Coefficient 2 of Full Load Ratio Curve
0.2818, !- Coefficient 3 of Full Load Ratio Curve
5, !- Chilled Water Outlet Temperature Lower Limit {C}
VariableFlow; !- Chiller Flow Mode
! Chiller for Radiant Coil
Chiller:Electric,
PlantLpSplSide Radiant CHW Chiller1, !- Name
AirCooled, !- Condenser Type
autosize, !- Nominal Capacity {W}
3.2, !- Nominal COP
PlantLpSplSide Radiant CHW Chiller1 Inlet Node, !- Chilled Water Inlet Node Name
PlantLpSplSide Radiant CHW Chiller1 Outlet Node, !- Chilled Water Outlet Node Name
PlantLpSplSide Radiant CHW Chiller1 Condenser Inlet Node, !- Condenser Inlet Node Name
PlantLpSplSide Radiant CHW Chiller1 Condenser Outlet Node, !- Condenser Outlet Node Name
0.0, !- Minimum Part Load Ratio
1.0, !- Maximum Part Load Ratio
0.65, !- Optimum Part Load Ratio
35.0, !- Design Condenser Inlet Temperature {C}
2.778, !- Temperature Rise Coefficient
16, !- Design Chilled Water Outlet Temperature {C}
autosize, !- Design Chilled Water Flow Rate {m3/s}
autosize, !- Design Condenser Water Flow Rate {m3/s}
0.9949, !- Coefficient 1 of Capacity Ratio Curve
-0.045954, !- Coefficient 2 of Capacity Ratio Curve
-0.0013543, !- Coefficient 3 of Capacity Ratio Curve
2.333, !- Coefficient 1 of Power Ratio Curve
-1.975, !- Coefficient 2 of Power Ratio Curve
0.6121, !- Coefficient 3 of Power Ratio Curve
0.03303, !- Coefficient 1 of Full Load Ratio Curve
0.6852, !- Coefficient 2 of Full Load Ratio Curve
0.2818, !- Coefficient 3 of Full Load Ratio Curve
5, !- Chilled Water Outlet Temperature Lower Limit {C}
VariableFlow; !- Chiller Flow Mode
!- =========== ALL OBJECTS IN CLASS: PLANTLOOP ===========
!DistrictCooling,
! PlantLpSplSide CHW Chiller1, !- Name
! PlantLpSplSide CHW Chiller1 Inlet Node, !- Chilled Water Inlet Node Name
! PlantLpSplSide CHW Chiller1 Outlet Node, !- Chilled Water Outlet Node Name
! 10000; !- Nominal Capacity {W}
! DOAS Cooling Loop
PlantLoop,
PlantLpSplSide CHW Chilled Water Loop, !- Name
Water, !- Fluid Type
PlantLpSplSide CHW Cooling Loop Operation, !- Plant Equipment Operation Scheme Name
PlantLpSplSide CHW Outlet Node, !- Loop Temperature Setpoint Node Name
98, !- Maximum Loop Temperature {C}
1, !- Minimum Loop Temperature {C}
autosize, !- Maximum Loop Flow Rate {m3/s}
0.0, !- Minimum Loop Flow Rate {m3/s}
autocalculate, !- Plant Loop Volume {m3}
PlantLpSplSide CHW Inlet Node, !- Plant Side Inlet Node Name
PlantLpSplSide CHW Outlet Node, !- Plant Side Outlet Node Name
PlantLpSplSide CHW Branch List, !- Plant Side Branch List Name
PlantLpSplSide CHW Connector List, !- Plant Side Connector List Name
PlantLpDmdSide CHW Inlet Node, !- Demand Side Inlet Node Name
PlantLpDmdSide CHW Outlet Node, !- Demand Side Outlet Node Name
PlantLpDmdSide CHW Branch List, !- Demand Side Branch List Name
PlantLpDmdSide CHW Connector List, !- Demand Side Connector List Name
Sequential, !- Load Distribution Scheme
Chilled Water Loop System Availability Managers List; !- Availability Manager List Name
! Radiant Cooling Loop
PlantLoop,
PlantLpSplSide Radiant CHW Chilled Water Loop, !- Name
Water, !- Fluid Type
PlantLpSplSide Radiant CHW Cooling Loop Operation, !- Plant Equipment Operation Scheme Name
PlantLpSplSide Radiant CHW Outlet Node, !- Loop Temperature Setpoint Node Name
98, !- Maximum Loop Temperature {C}
1, !- Minimum Loop Temperature {C}
autosize, !- Maximum Loop Flow Rate {m3/s}
0.0, !- Minimum Loop Flow Rate {m3/s}
autocalculate, !- Plant Loop Volume {m3}
PlantLpSplSide Radiant CHW Inlet Node, !- Plant Side Inlet Node Name
PlantLpSplSide Radiant CHW Outlet Node, !- Plant Side Outlet Node Name
PlantLpSplSide Radiant CHW Branch List, !- Plant Side Branch List Name
PlantLpSplSide Radiant CHW Connector List, !- Plant Side Connector List Name
PlantLpDmdSide Radiant CHW Inlet Node, !- Demand Side Inlet Node Name
PlantLpDmdSide Radiant CHW Outlet Node, !- Demand Side Outlet Node Name
PlantLpDmdSide Radiant CHW Branch List, !- Demand Side Branch List Name
PlantLpDmdSide Radiant CHW Connector List, !- Demand Side Connector List Name
Sequential, !- Load Distribution Scheme
Chilled Water Loop System Availability Managers List; !- Availability Manager List Name
! Heating Loop
PlantLoop,
PlantLpSplSide HW Heated Water Loop, !- Name
Water, !- Fluid Type
PlantLpSplSide HW Heating Loop Operation, !- Plant Equipment Operation Scheme Name
PlantLpSplSide HW Outlet Node, !- Loop Temperature Setpoint Node Name
100, !- Maximum Loop Temperature {C}
10, !- Minimum Loop Temperature {C}
autosize, !- Maximum Loop Flow Rate {m3/s}
0.0, !- Minimum Loop Flow Rate {m3/s}
autocalculate, !- Plant Loop Volume {m3}
PlantLpSplSide HW Inlet Node, !- Plant Side Inlet Node Name
PlantLpSplSide HW Outlet Node, !- Plant Side Outlet Node Name
PlantLpSplSide HW Branch List, !- Plant Side Branch List Name
PlantLpSplSide HW Connector List, !- Plant Side Connector List Name
PlantLpDmdSide HW Inlet Node, !- Demand Side Inlet Node Name
PlantLpDmdSide HW Outlet Node, !- Demand Side Outlet Node Name
PlantLpDmdSide HW Branch List, !- Demand Side Branch List Name
PlantLpDmdSide HW Connector List, !- Demand Side Connector List Name
Sequential, !- Load Distribution Scheme
Heated Water Loop System Availability Managers List; !- Availability Manager List Name
!- =========== ALL OBJECTS IN CLASS: PIPE:ADIABATIC ===========
!*******For PlantLpDmdSide CHW Pipe (Inlet, Outlet & Bypass), Starting
Pipe:Adiabatic,
PlantLpDmdSide CHW Inlet Pipe, !- Name
PlantLpDmdSide CHW Inlet Node, !- Inlet Node Name
PlantLpDmdSide CHW Inlet Pipe Outlet Node; !- Outlet Node Name
Pipe:Adiabatic,
PlantLpDmdSide CHW Outlet Pipe, !- Name
PlantLpDmdSide CHW Outlet Pipe Inlet Node, !- Inlet Node Name
PlantLpDmdSide CHW Outlet Node; !- Outlet Node Name
Pipe:Adiabatic,
PlantLpDmdSide CHW Bypass Pipe, !- Name
PlantLpDmdSide CHW Bypass Pipe Inlet Node, !- Inlet Node Name
PlantLpDmdSide CHW Bypass Pipe Outlet Node; !- Outlet Node Name
!*******For PlantLpDmdSide Radiant CHW Pipe (Inlet, Outlet & Bypass), Starting
Pipe:Adiabatic,
PlantLpDmdSide Radiant CHW Inlet Pipe, !- Name
PlantLpDmdSide Radiant CHW Inlet Node, !- Inlet Node Name
PlantLpDmdSide Radiant CHW Inlet Pipe Outlet Node; !- Outlet Node Name
Pipe:Adiabatic,
PlantLpDmdSide Radiant CHW Outlet Pipe, !- Name
PlantLpDmdSide Radiant CHW Outlet Pipe Inlet Node, !- Inlet Node Name
PlantLpDmdSide Radiant CHW Outlet Node; !- Outlet Node Name
Pipe:Adiabatic,
PlantLpDmdSide Radiant CHW Bypass Pipe, !- Name
PlantLpDmdSide Radiant CHW Bypass Pipe Inlet Node, !- Inlet Node Name
PlantLpDmdSide Radiant CHW Bypass Pipe Outlet Node; !- Outlet Node Name
!*******For PlantLpDmdSide HW Pipe (Inlet, Outlet & Bypass), Starting
Pipe:Adiabatic,
PlantLpDmdSide HW Inlet Pipe, !- Name
PlantLpDmdSide HW Inlet Node, !- Inlet Node Name
PlantLpDmdSide HW Inlet Pipe Outlet Node; !- Outlet Node Name
Pipe:Adiabatic,
PlantLpDmdSide HW Outlet Pipe, !- Name
PlantLpDmdSide HW Outlet Pipe Inlet Node, !- Inlet Node Name
PlantLpDmdSide HW Outlet Node; !- Outlet Node Name
Pipe:Adiabatic,
PlantLpDmdSide HW Bypass Pipe, !- Name
PlantLpDmdSide HW Bypass Pipe Inlet Node, !- Inlet Node Name
PlantLpDmdSide HW Bypass Pipe Outlet Node; !- Outlet Node Name
!*******For PlantLpSplSide CHW Pipe (Outlet & Bypass), Starting
!*******Without Inlet Pipe, because the first component should be the Pump,
!*******If HeaderedPump isn't used and chiller has a bypass pipe, the Inlet Pipe should be used before the PlantLpSplSide spliter
!*******If Chiller's water flow type is the variavleflow, the bypass pipe doesn't work
Pipe:Adiabatic,
PlantLpSplSide CHW Outlet Pipe, !- Name
PlantLpSplSide CHW Outlet Pipe Inlet Node, !- Inlet Node Name
PlantLpSplSide CHW Outlet Node; !- Outlet Node Name
!Pipe:Adiabatic,
! PlantLpSplSide CHW Bypass Pipe, !- Name
! PlantLpSplSide CHW Bypass Pipe Inlet Node, !- Inlet Node Name
! PlantLpSplSide CHW Bypass Pipe Outlet Node; !- Outlet Node Name
!*******For PlantLpSplSide CHW Pipe (Outlet & Bypass), Starting
Pipe:Adiabatic,
PlantLpSplSide Radiant CHW Outlet Pipe, !- Name
PlantLpSplSide Radiant CHW Outlet Pipe Inlet Node, !- Inlet Node Name
PlantLpSplSide Radiant CHW Outlet Node; !- Outlet Node Name
!*******For PlantLpSplSide HW Pipe (Outlet & Bypass), Starting
!*******Without Inlet Pipe, because the first component should be the Pump,
!*******If HeaderedPump is'nt used and chiller has a bypass pipe, the Inlet Pipe should be used before the PlantLpSplSide spliter
Pipe:Adiabatic,
PlantLpSplSide HW Outlet Pipe, !- Name
PlantLpSplSide HW Outlet Pipe Inlet Node, !- Inlet Node Name
PlantLpSplSide HW Outlet Node; !- Outlet Node Name
Pipe:Adiabatic,
PlantLpSplSide HW Bypass Pipe, !- Name
PlantLpSplSide HW Bypass Pipe Inlet Node, !- Inlet Node Name
PlantLpSplSide HW Bypass Pipe Outlet Node; !- Outlet Node Name
!- =========== ALL OBJECTS IN CLASS: PLANTEQUIPMENTLIST ===========
PlantEquipmentList,
Plant Loop Cooling Equipment List, !- Name
Chiller:Electric, !- Equipment 1 Object Type
PlantLpSplSide CHW Chiller1; !- Equipment 1 Name
PlantEquipmentList,
Plant Loop Radiant Cooling Equipment List, !- Name
Chiller:Electric, !- Equipment 1 Object Type
PlantLpSplSide Radiant CHW Chiller1; !- Equipment 1 Name
PlantEquipmentList,
Plant Loop Heating Equipment List, !- Name
Boiler:HotWater, !- Equipment 1 Object Type
PlantLpSplSide HW Boiler1; !- Equipment 1 Name
!- =========== ALL OBJECTS IN CLASS: PLANTEQUIPMENTOPERATION:COOLINGLOAD ===========
PlantEquipmentOperation:CoolingLoad,
Chiller Control Operration, !- Name
0, !- Load Range 1 Lower Limit {W}
100000, !- Load Range 1 Upper Limit {W}
Plant Loop Cooling Equipment List; !- Priority Control 1 Equipment List Name
PlantEquipmentOperation:CoolingLoad,
Radiant Chiller Control Operration, !- Name
0, !- Load Range 1 Lower Limit {W}
100000, !- Load Range 1 Upper Limit {W}
Plant Loop Radiant Cooling Equipment List; !- Priority Control 1 Equipment List Name
!- =========== ALL OBJECTS IN CLASS: PLANTEQUIPMENTOPERATION:HEATINGLOAD ===========
PlantEquipmentOperation:HeatingLoad,
Boiler Control Operration, !- Name
0, !- Load Range 1 Lower Limit {W}
100000, !- Load Range 1 Upper Limit {W}
Plant Loop Heating Equipment List; !- Priority Control 1 Equipment List Name
!- =========== ALL OBJECTS IN CLASS: PLANTEQUIPMENTOPERATIONSCHEMES ===========
PlantEquipmentOperationSchemes,
PlantLpSplSide CHW Cooling Loop Operation, !- Name
PlantEquipmentOperation:CoolingLoad, !- Control Scheme 1 Object Type
Radiant Chiller Control Operration, !- Control Scheme 1 Name
Office Occupancy For OA; !- Control Scheme 1 Schedule Name
PlantEquipmentOperationSchemes,
PlantLpSplSide Radiant CHW Cooling Loop Operation, !- Name
PlantEquipmentOperation:CoolingLoad, !- Control Scheme 1 Object Type
Chiller Control Operration, !- Control Scheme 1 Name
Office Occupancy For OA; !- Control Scheme 1 Schedule Name
PlantEquipmentOperationSchemes,
PlantLpSplSide HW Heating Loop Operation, !- Name
PlantEquipmentOperation:HeatingLoad, !- Control Scheme 1 Object Type
Boiler Control Operration, !- Control Scheme 1 Name
Office Occupancy For OA; !- Control Scheme 1 Schedule Name
!- =========== ALL OBJECTS IN CLASS: AVAILABILITYMANAGER:SCHEDULED ===========
AvailabilityManager:Scheduled,
DOAS System Availability Managers, !- Name
Office Occupancy For OA; !- Schedule Name
AvailabilityManager:Scheduled,
Chilled Water Loop Availability Managers, !- Name
Office Occupancy For OA; !- Schedule Name
AvailabilityManager:Scheduled,
Heated Water Loop Availability Managers, !- Name
Office Occupancy For OA; !- Schedule Name
!- =========== ALL OBJECTS IN CLASS: AVAILABILITYMANAGERASSIGNMENTLIST ===========
AvailabilityManagerAssignmentList,
DOAS System Availability Managers List, !- Name
AvailabilityManager:Scheduled, !- Availability Manager 1 Object Type
DOAS System Availability Managers; !- Availability Manager 1 Name
AvailabilityManagerAssignmentList,
Chilled Water Loop System Availability Managers List, !- Name
AvailabilityManager:Scheduled, !- Availability Manager 1 Object Type
Chilled Water Loop Availability Managers; !- Availability Manager 1 Name
AvailabilityManagerAssignmentList,
Heated Water Loop System Availability Managers List, !- Name
AvailabilityManager:Scheduled, !- Availability Manager 1 Object Type
Heated Water Loop Availability Managers; !- Availability Manager 1 Name
!- =========== ALL OBJECTS IN CLASS: SETPOINTMANAGER:SCHEDULED ===========
SetpointManager:Scheduled,
Plant Loop Cooling Setpoint Manager, !- Name
Temperature, !- Control Variable
CW LOOP TEMP SCHEDULE, !- Schedule Name
PlantLpSplSide CHW Outlet Node; !- Setpoint Node or NodeList Name
SetpointManager:Scheduled,
Plant Loop Radiant Cooling Setpoint Manager, !- Name
Temperature, !- Control Variable
CW Radiant LOOP TEMP SCHEDULE, !- Schedule Name
PlantLpSplSide Radiant CHW Outlet Node; !- Setpoint Node or NodeList Name
SetpointManager:Scheduled,
Plant Loop Heating Setpoint Manager, !- Name
Temperature, !- Control Variable
HW LOOP TEMP SCHEDULE, !- Schedule Name
PlantLpSplSide HW Outlet Node; !- Setpoint Node or NodeList Name
SetpointManager:Scheduled,
DOAS Precool Air Summer Setpoint Manager, !- Name
Temperature, !- Control Variable
DOAS Precool Air Summer Temp, !- Schedule Name
DOAS Precool CoolingCoil Air Outlet Node; !- Setpoint Node or NodeList Name
SetpointManager:Scheduled,
DOAS Preheat Air Winter Setpoint Manager, !- Name
Temperature, !- Control Variable
DOAS Preheat Air Winter Temp, !- Schedule Name
DOAS Preheat HeatingCoil Air Outlet Node; !- Setpoint Node or NodeList Name
SetpointManager:Scheduled,
DOAS CoolingCoil Air Summer Setpoint Manager, !- Name
Temperature, !- Control Variable
DOAS Precool Air Summer Temp, !- Schedule Name
DOAS CoolingCoil Air Outlet Node; !- Setpoint Node or NodeList Name
SetpointManager:Scheduled,
DOAS HeatingCoil Air Winter Setpoint Manager, !- Name
Temperature, !- Control Variable
DOAS Preheat Air Winter Temp, !- Schedule Name
DOAS AirLpSplSide Outlet Node; !- Setpoint Node or NodeList Name
!- =========== ALL OBJECTS IN CLASS: CURVE:QUADRATIC ===========
Curve:Quadratic,
BoilerEfficiency, !- Name
1.0, !- Coefficient1 Constant
0.0, !- Coefficient2 x
0.0, !- Coefficient3 x**2
0, !- Minimum Value of x
1; !- Maximum Value of x
!- =========== ALL OBJECTS IN CLASS: OUTPUT:REPORTS ===========
Output:VariableDictionary,Regular;
!- =========== ALL OBJECTS IN CLASS: OUTPUT:VARIABLE ===========
Output:Variable,*,Zone/Sys Air Temperature,Timestep;
Output:Variable,*,Outdoor Dry Bulb,Timestep;
Output:Variable,*,Zone Mean Air Temperature,Timestep;
Output:Variable,*,Zone Mean Radiant Temperature,Timestep;
Output:Variable,*,AirLoopHVAC Actual Outdoor Air Fraction,Timestep;
Output:Variable,*,People Number Of Occupants,Timestep;
Output:Variable,DOAS OA Mixer ExhaustNd,System Node Volume Flow Rate Standard Density,Timestep;
Output:Variable,DOAS OA Mixer ExhaustNd,System Node Temp,Timestep;
Output:Variable,DOAS AirLpDmdSide Inlet Node,System Node Temp,Timestep;
Output:Variable,DOAS AirLpSplSide Inlet Node,System Node Volume Flow Rate Standard Density,Timestep;
Output:Variable,DOAS Preheat HeatingCoil Air Outlet Node,System Node Temp,Timestep;
Output:Variable,DOAS Preheat HeatingCoil Air Outlet Node,System Node Volume Flow Rate Standard Density,Timestep;
Output:Variable,DOAS Precool CoolingCoil Air Outlet Node,System Node Temp,Timestep;
Output:Variable,DOAS Precool CoolingCoil Air Outlet Node,System Node Volume Flow Rate Standard Density,Timestep;
Output:Variable,DOAS OA Inlet Node,System Node Temp,Timestep;
Output:Variable,DOAS OA Inlet Node,System Node Volume Flow Rate Standard Density,Timestep;
Output:Variable,DOAS OA Mixer Outlet Node,System Node Temp,Timestep;
Output:Variable,DOAS OA Mixer Outlet Node,System Node Volume Flow Rate Standard Density,Timestep;
Output:Variable,DOAS Fan Outlet Node,System Node Temp,Timestep;
Output:Variable,DOAS Fan Outlet Node,System Node Volume Flow Rate Standard Density,Timestep;
Output:Variable,DOAS CoolingCoil Air Outlet Node,System Node Temp,Timestep;
Output:Variable,DOAS CoolingCoil Air Outlet Node,System Node Volume Flow Rate Standard Density,Timestep;
Output:Variable,*,Hydronic Low Temp Radiant Water Inlet Temp,Timestep;
Output:Variable,*,Hydronic Low Temp Radiant Water Outlet Temp,Timestep;
Output:Variable,*,Hydronic Low Temp Radiant Water Mass Flow,Timestep;
Output:Variable,*,Zone/Sys Sensible Load to Cooling Setpoint Predicted,Timestep;
Output:Variable,*,Zone/Sys Sensible Load Predicted,Timestep;
Output:Variable,*,Zone/Sys Moisture Load Rate Predicted,Timestep;
Output:Variable,*,Zone/Sys Sensible Load Predicted,Timestep;
Output:Variable,*,Zone Air Relative Humidity;
Output:Variable,*,Zone Air Relative Humidity;
Output:Variable,*,Zone Air Humidity Ratio;
Output:Variable,*,Zone/Sys Moisture Load Rate Predicted;
Output:Variable,*,Zone/Sys Sensible Load to Cooling Setpoint Predicted;