I took your 3.0 input file and converted it to 4.0. Â After running it, I looked at the diagram of the HVAC loops, and there are a couple things that look odd to me, but the chilled water loop itself seems to be setup OK.
I debugged a bit, and may have come across a bug in the chiller simulation. Â You see, the pump is trying to run, even though it seems the loop doesn't have demand. Â This shouldn't be happening because the pump is set to Intermittent, but regardless it is. Â When this occurs, the chiller doesn't have any demand, and so the flow from the pump should just pass through the chiller and out the outlet of the loop. Â However, the chiller is cutting off the flow. Â Thus the pump is pushing flow, but the chiller is turning it off. Â
I am concerned that some of the air loop/coil configurations could be causing this odd behavior of flow request and components turned off, as the coils interact with the demand side of the loop. Two recommendations for now:
1: Add a bypass to the plant loop supply side to allow this excess flow to go down that path.
2: Investigate the coil/air loops setup a bit more to make sure the configurations are allowed. Â I'll look into this as well, but I am not as familiar over there as I am with the plant simulation.
In the meantime, I'll file this is a bug in the chiller and investigate a little further how to catch and provide error support for this situation.
Thanks,
Edwin Lee
On Sat, Dec 19, 2009 at 14:17, Edwin Lee
<leeed2001@xxxxxxxxx> wrote:
YunPeng:
Would you be able to post the input file causing this error? Â Or post the file to a
Helpdesk ticket maybe? Â I'd like to have a look and see if I could find the problem for you.
Thanks,
Edwin Lee
EnergyPlus Development Team
On Sat, Dec 19, 2009 at 04:07,
Y.P.Hu <hyp@xxxxxxxxxxxxxxxxx> wrote:
Â
thank you dashamir, I'll try it!
dashamir marini å??é??:
>
>
> Hello
>
> From first view of Warning message seems that mass flow rate among out
> and in node at PlantSupplySide exceed tolerance value which you have
> input in your idf file. That means some leakage may have occured in
> demand side (distribution system or zone equipments) of your system.
> Usually this happen for air system flow, and I'm not sure if it can
> happen for water flow too.
> One my suggestion would be: try to increase tolerance value just to
> understand if this warning will occure more of course without
> exceeding limit values. If happen again try to check control objects
> in idf file.
>
> that is my opinion
>
> good luck
>
> Dashamir
>
>
--
ã??Give my best wishes to you!
Respectfully yours, YunPeng Hu
Huazhong University of Science and Technology
Wuhan, Hubei, China
hyp@xxxxxxxxxxxxxxxxx
hyp6789@xxxxxxx
__._,_.___
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
__,_._,___