Dear Hanan, Yes DesignBuilder calculates thermal mass data but in the
current release it is not easy to get the output. In the next version, thermal
mass will be displayed on the constructions dialog on the Calculated tab as a
Km value in KJ/m2/K. Also, thermal mass will be included in the CSV report as
Km x area for each surface so you can sum the values for the whole zone/building.
Km is defined in prEN 13790 as a standard measure of thermal mass as measured from
the inside. Km
Definition (from BRE SBEM manual): Calculate the contribution of each layer of construction by
calculating: density (kg/m3) x thickness (m) x specific heat capacity
(kJ/(kgK)). Starting from the layer of the construction closest to the space
(i.e., from the interior), add these values together until any one of the
following conditions is satisfied: the total thickness of layers exceeds 0.1
metres you have reached the mid-point of the
construction you have reached an insulating layer (defined
as having a conductivity of 0.08W/mK) This new
version should be available in beta test form next week. Look out for
v2.1.0.052 or later. Regards, Andy From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Dr Architect
Dear Everyone, I hope this email finds you
all well, Question please: I was asked to provide some
information about the "external walls thermal inertia" before
and after applying some modifications like changing the type of
insulation.
if not, which software can
calculate it? Thanks! Hanan
__._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.