RE: [EnergyPlus_Support] Modeling a part of building?
Jinhyok Heo,
In the DesignBuilder user interface to EnergyPlus there is an option you can use to control which zones are to be included in the model. Where there is an included zone adjacent to an excluded zone, the boundary in the included zone is modelled as adiabatic (the assumption being that the excluded zone is probably at the same temperature).
To do this in idf data you can change the surface definition so that the reference of the adjacent zone is the same as the current zone and set the corresponding other side surface name to be the same name as the actual surface name. Alternatively, I think that the latest versions of EnergyPlus provide a specific surface type for modelling adiabatic boundaries.
Regards,
Andy
-----Original Message-----
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Jinhyok Heo
Sent: quinta-feira, 28 de Janeiro de 2010 22:35
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Modeling a part of building?
Dear all,
May I ask what are the best practices to model just a part of building?
If I am just interested in simulating some zones of a building, is there
a way not to model the whole building? I guess I need to figure out how
to assume the boundary conditions of the zones and describe them in idf.
Regards,
--
Jinhyok Heo
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/