Hi again I this I managed to find your error. Check the branches you used for the splitter and the mixer of the reheat. Especially check:
SPLITTER,
Reheat Splitter, !- SplitterName
Reheat Inlet Branch, !- Inlet Branch Name
Z1G Reheat Branch, !- Outlet Branch Name 1
Z2G Reheat Branch, !- Outlet Branch Name 2
Z3G Reheat Branch, !- Outlet Branch Name 3
Z4G Reheat Branch, !- Outlet Branch Name 4
Z5G Reheat Branch, !- Outlet Branch Name 5
Z6G Reheat Branch, !- Outlet Branch Name 6
Z7G Reheat Branch, !- Outlet Branch Name 7
Z8G Reheat Branch, !- Outlet Branch Name 8
Z9G Reheat Branch, !- Outlet Branch Name 9
Z10G Reheat Branch, !- Outlet Branch Name 10
Z11G Reheat Branch, !- Outlet Branch Name 11
Z12G Reheat Branch, !- Outlet Branch Name 12
Z15G Reheat Branch, !- Outlet Branch Name 13
Z16G Reheat Branch, !- Outlet Branch Name 14
Z1A Reheat Branch, !- Outlet Branch Name 15
Z2A Reheat Branch, !- Outlet Branch Name 16
Z3A Reheat Branch, !- Outlet Branch Name 17
Z4A Reheat Branch, !- Outlet Branch Name 18
Z5A Reheat Branch, !- Outlet Branch Name 19
Z6A Reheat Branch, !- Outlet Branch Name 20
Z7A Reheat Branch, !- Outlet Branch Name 21
Z8A Reheat Branch, !- Outlet Branch Name 22
Z9A Reheat Branch, !- Outlet Branch Name 23
Z10A Reheat Branch, !- Outlet Branch Name 24
Z11A Reheat Branch, !- Outlet Branch Name 25
Z1B Reheat Branch, !- Outlet Branch Name 26
Z2B Reheat Branch, !- Outlet Branch Name 27
Z3B Reheat Branch, !- Outlet Branch Name 28
Z4B Reheat Branch, !- Outlet Branch Name 29
Z5B Reheat Branch, !- Outlet Branch Name 30
Z6B Reheat Branch, !- Outlet Branch Name 31
Z7B Reheat Branch, !- Outlet Branch Name 32
Z8B Reheat Branch, !- Outlet Branch Name 33
Z9B Reheat Branch, !- Outlet Branch Name 34
Z10B Reheat Branch, !- Outlet Branch Name 35
Z11B Reheat Branch, !- Outlet Branch Name 36
Z1C Reheat Branch, !- Outlet Branch Name 37
Z2C Reheat Branch, !- Outlet Branch Name 38
Z3C Reheat Branch, !- Outlet Branch Name 39
Z4C Reheat Branch, !- Outlet Branch Name 40
Z5C Reheat Branch, !- Outlet Branch Name 41
Z6C Reheat Branch, !- Outlet Branch Name 42
Z7C Reheat Branch, !- Outlet Branch Name 43
Z8C Reheat Branch, !- Outlet Branch Name 44
Z9C Reheat Branch, !- Outlet Branch Name 45
Z10C Reheat Branch, !- Outlet Branch Name 46
Z11C Reheat Branch, !- Outlet Branch Name 47
Reheat Bypass Branch; !- Outlet Branch Name 48
and
MIXER,
Reheat Mixer, !- MixerName
Reheat Outlet Branch, !- Outlet Branch Name
Z1G Reheat Branch, !- Inlet Branch Name 1
Z2G Reheat Branch, !- Inlet Branch Name 2
Z3G Reheat Branch, !- Inlet Branch Name 3
Z4G Reheat Branch, !- Inlet Branch Name 4
Z5G Reheat Branch, !- Inlet Branch Name 5
Z6G Reheat Branch, !- Inlet Branch Name 6
Z7G Reheat Branch, !- Inlet Branch Name 7
Z8G Reheat Branch, !- Inlet Branch Name 8
Z9G Reheat Branch, !- Inlet Branch Name 9
Z10G Reheat Branch, !- Inlet Branch Name 10
Z11G Reheat Branch, !- Inlet Branch Name 11
Z12G Reheat Branch, !- Inlet Branch Name 12
Z15G Reheat Branch, !- Inlet Branch Name 13
Z16G Reheat Branch, !- Inlet Branch Name 14
Z1A Reheat Branch, !- Inlet Branch Name 15
Z2A Reheat Branch, !- Inlet Branch Name 16
Z3A Reheat Branch, !- Inlet Branch Name 17
Z4A Reheat Branch, !- Inlet Branch Name 18
Z5A Reheat Branch, !- Inlet Branch Name 19
Z6A Reheat Branch, !- Inlet Branch Name 20
Z7A Reheat Branch, !- Inlet Branch Name 21
Z8A Reheat Branch, !- Inlet Branch Name 22
Z9A Reheat Branch, !- Inlet Branch Name 23
Z10A Reheat Branch, !- Inlet Branch Name 24
Z11A Reheat Branch, !- Inlet Branch Name 25
Z1B Reheat Branch, !- Inlet Branch Name 26
Z2B Reheat Branch, !- Inlet Branch Name 27
Z3B Reheat Branch, !- Inlet Branch Name 28
Z4B Reheat Branch, !- Inlet Branch Name 29
Z5B Reheat Branch, !- Inlet Branch Name 30
Z6B Reheat Branch, !- Inlet Branch Name 31
Z7B Reheat Branch, !- Inlet Branch Name 32
Z8B Reheat Branch, !- Inlet Branch Name 33
Z9B Reheat Branch, !- Inlet Branch Name 34
Z10B Reheat Branch, !- Inlet Branch Name 35
Z11B Reheat Branch, !- Inlet Branch Name 36
Z1C Reheat Branch, !- Inlet Branch Name 37
Z2C Reheat Branch, !- Inlet Branch Name 38
Z3C Reheat Branch, !- Inlet Branch Name 39
Z4C Reheat Branch, !- Inlet Branch Name 40
Z5C Reheat Branch, !- Inlet Branch Name 41
Z6C Reheat Branch, !- Inlet Branch Name 42
Z7C Reheat Branch, !- Inlet Branch Name 43
Z8C Reheat Branch, !- Inlet Branch Name 44
Z9C Reheat Branch, !- Inlet Branch Name 45
Z10C Reheat Branch, !- Inlet Branch Name 46
Z11C Reheat Branch; !- Inlet Branch Name 47
In the mixer the bypass is missing. If you fix that the simulation should proceed.
Hope the i managed to help you again.
Sotiris Papantoniou
Hello Natassa,
I had the same problem some days ago. Possibly there is no problem with your nodes. The major errors are the following:
************ * Beginning Plant Sizing Calculations
** Severe ** For Connector List=HEATING DEMAND SIDE CONNECTORS
** ~~~ ** ...Item=REHEAT SPLITTER, Type=SPLITTER was not matched.
** ~~~ ** The branch list for this SPLITTER does not match the branch list for its corresponding MIXER.
** Severe ** For Connector List=HEATING DEMAND SIDE CONNECTORS
** ~~~ ** ...Item=REHEAT MIXER, Type=MIXER was not matched.
** ~~~ ** The branch list for this MIXER does not match the branch list for its corresponding SPLITTER.
** Fatal ** GetConnectorListInp ut: Program terminates for preceding conditions
I you fix the above problem I expext the error for the nodes will stop. The reason why you receive these errors is because the simulation stops before checking the nodes "Fatal" and for this reason it has some many mistakes after that.
Hope i managed to help you a bit