Hi, Natassa I had a look at your IDF. You are now trying to use GSHE and one plant loop. The IDF had 23 warnings and 20 sever warning. Those Summer On, Winter On problems were in the very old IDF we looked at. But we never reached that point because the plant loop cannot be split into four sections to connect to the heat 4 pumps. The Zone partition warnings were there before. The node connection warnings are also very similar. Practically, the re-heat coil and the heating coil are the same. By changing the names, you may have some nodes mixed up again. I used the zone1, zone2, etc for the plant branches, so that it would be easier to separate the two groups of names. You are still using version 2.2. I think you should up grade to version 4.0. ================ In the old IDF, the schedule for both Summer On and Winter On was ON. The type 4 thermostat resulves the heating/cooling requirement. You have DaySchedule, ON, defined in your current IDF, but only for the Summer and WinderDesignDay. You may need to re-define the schedules or add. Schedule:Compact, Summer ON, !- Name On/Off, !- Schedule Type Limits Name Through: 12/31, !- Field 1 For: Alldays, !- Field 2 Until: 24:00, !- Field 3 1; !- Field 4 There are more errors. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: natamats@xxxxxxxxx Date: Sun, 31 Jan 2010 09:15:33 -0800 Subject: Re: [EnergyPlus_Support] Need help with this idf Thank you very much for your help, you were right. I did the change and some mistakes were corrected. But it still has a few mistakes which i don t know how to correct. I am attaching the idf file and the mistakes.Please take a look.
Thank you very much, Natassa To: EnergyPlus_Support@ Sent: Sun, January 31, 2010 1:12:31 PM Subject: Re: [EnergyPlus_
Hi again I this I managed to find your error. Check the branches you used for the splitter and the mixer of the reheat. Especially check: SPLITTER, Reheat Splitter, !- SplitterName Reheat Inlet Branch, !- Inlet Branch Name Z1G Reheat Branch, !- Outlet Branch Name 1 Z2G Reheat Branch, !- Outlet Branch Name 2 Z3G Reheat Branch, !- Outlet Branch Name 3 Z4G Reheat Branch, !- Outlet Branch Name 4 Z5G Reheat Branch, !- Outlet Branch Name 5 Z6G Reheat Branch, !- Outlet Branch Name 6 Z7G Reheat Branch, !- Outlet Branch Name 7 Z8G Reheat Branch, !- Outlet Branch Name 8 Z9G Reheat Branch, !- Outlet Branch Name 9 Z10G Reheat Branch, !- Outlet Branch Name 10 Z11G Reheat Branch, !- Outlet Branch Name 11 Z12G Reheat Branch, !- Outlet Branch Name 12 Z15G Reheat Branch, !- Outlet Branch Name 13 Z16G Reheat Branch, !- Outlet Branch Name 14 Z1A Reheat Branch, !- Outlet Branch Name 15 Z2A Reheat Branch, !- Outlet Branch Name 16 Z3A Reheat Branch, !- Outlet Branch Name 17 Z4A Reheat Branch, !- Outlet Branch Name 18 Z5A Reheat Branch, !- Outlet Branch Name 19 Z6A Reheat Branch, !- Outlet Branch Name 20 Z7A Reheat Branch, !- Outlet Branch Name 21 Z8A Reheat Branch, !- Outlet Branch Name 22 Z9A Reheat Branch, !- Outlet Branch Name 23 Z10A Reheat Branch, !- Outlet Branch Name 24 Z11A Reheat Branch, !- Outlet Branch Name 25 Z1B Reheat Branch, !- Outlet Branch Name 26 Z2B Reheat Branch, !- Outlet Branch Name 27 Z3B Reheat Branch, !- Outlet Branch Name 28 Z4B Reheat Branch, !- Outlet Branch Name 29 Z5B Reheat Branch, !- Outlet Branch Name 30 Z6B Reheat Branch, !- Outlet Branch Name 31 Z7B Reheat Branch, !- Outlet Branch Name 32 Z8B Reheat Branch, !- Outlet Branch Name 33 Z9B Reheat Branch, !- Outlet Branch Name 34 Z10B Reheat Branch, !- Outlet Branch Name 35 Z11B Reheat Branch, !- Outlet Branch Name 36 Z1C Reheat Branch, !- Outlet Branch Name 37 Z2C Reheat Branch, !- Outlet Branch Name 38 Z3C Reheat Branch, !- Outlet Branch Name 39 Z4C Reheat Branch, !- Outlet Branch Name 40 Z5C Reheat Branch, !- Outlet Branch Name 41 Z6C Reheat Branch, !- Outlet Branch Name 42 Z7C Reheat Branch, !- Outlet Branch Name 43 Z8C Reheat Branch, !- Outlet Branch Name 44 Z9C Reheat Branch, !- Outlet Branch Name 45 Z10C Reheat Branch, !- Outlet Branch Name 46 Z11C Reheat Branch, !- Outlet Branch Name 47 Reheat Bypass Branch; !- Outlet Branch Name 48 and MIXER, Reheat Mixer, !- MixerName Reheat Outlet Branch, !- Outlet Branch Name Z1G Reheat Branch, !- Inlet Branch Name 1 Z2G Reheat Branch, !- Inlet Branch Name 2 Z3G Reheat Branch, !- Inlet Branch Name 3 Z4G Reheat Branch, !- Inlet Branch Name 4 Z5G Reheat Branch, !- Inlet Branch Name 5 Z6G Reheat Branch, !- Inlet Branch Name 6 Z7G Reheat Branch, !- Inlet Branch Name 7 Z8G Reheat Branch, !- Inlet Branch Name 8 Z9G Reheat Branch, !- Inlet Branch Name 9 Z10G Reheat Branch, !- Inlet Branch Name 10 Z11G Reheat Branch, !- Inlet Branch Name 11 Z12G Reheat Branch, !- Inlet Branch Name 12 Z15G Reheat Branch, !- Inlet Branch Name 13 Z16G Reheat Branch, !- Inlet Branch Name 14 Z1A Reheat Branch, !- Inlet Branch Name 15 Z2A Reheat Branch, !- Inlet Branch Name 16 Z3A Reheat Branch, !- Inlet Branch Name 17 Z4A Reheat Branch, !- Inlet Branch Name 18 Z5A Reheat Branch, !- Inlet Branch Name 19 Z6A Reheat Branch, !- Inlet Branch Name 20 Z7A Reheat Branch, !- Inlet Branch Name 21 Z8A Reheat Branch, !- Inlet Branch Name 22 Z9A Reheat Branch, !- Inlet Branch Name 23 Z10A Reheat Branch, !- Inlet Branch Name 24 Z11A Reheat Branch, !- Inlet Branch Name 25 Z1B Reheat Branch, !- Inlet Branch Name 26 Z2B Reheat Branch, !- Inlet Branch Name 27 Z3B Reheat Branch, !- Inlet Branch Name 28 Z4B Reheat Branch, !- Inlet Branch Name 29 Z5B Reheat Branch, !- Inlet Branch Name 30 Z6B Reheat Branch, !- Inlet Branch Name 31 Z7B Reheat Branch, !- Inlet Branch Name 32 Z8B Reheat Branch, !- Inlet Branch Name 33 Z9B Reheat Branch, !- Inlet Branch Name 34 Z10B Reheat Branch, !- Inlet Branch Name 35 Z11B Reheat Branch, !- Inlet Branch Name 36 Z1C Reheat Branch, !- Inlet Branch Name 37 Z2C Reheat Branch, !- Inlet Branch Name 38 Z3C Reheat Branch, !- Inlet Branch Name 39 Z4C Reheat Branch, !- Inlet Branch Name 40 Z5C Reheat Branch, !- Inlet Branch Name 41 Z6C Reheat Branch, !- Inlet Branch Name 42 Z7C Reheat Branch, !- Inlet Branch Name 43 Z8C Reheat Branch, !- Inlet Branch Name 44 Z9C Reheat Branch, !- Inlet Branch Name 45 Z10C Reheat Branch, !- Inlet Branch Name 46 Z11C Reheat Branch; !- Inlet Branch Name 47 In the mixer the bypass is missing. If you fix that the simulation should proceed. Hope the i managed to help you again. Sotiris Papantoniou Óôéò 31 Éáíïõáñßïõ 2010 12:55 ì.ì., ï ÷ñÞóôçò ÓùôÞñçò Ðáðáíôùíßïõ <sotos.enveng@ gmail.com> Ýãñáøå: Hello Natassa, Say Happy New Year with Messenger for Mobile. See more. __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |