Hi, Natassa I had a look at your IDF. You are now trying to use GSHE and one plant loop. The IDF had 23 warnings and 20 sever warning. Those Summer On, Winter On problems were in the very old IDF we looked at. But we never reached that point because the plant loop cannot be split into four sections to connect to the heat 4 pumps. The Zone partition warnings were there before. The node connection warnings are also very similar. Practically, the re-heat coil and the heating coil are the same. By changing the names, you may have some nodes mixed up again. I used the zone1, zone2, etc for the plant branches, so that it would be easier to separate the two groups of names. You are still using version 2.2. I think you should up grade to version 4.0. ================ In the old IDF, the schedule for both Summer On and Winter On was ON. The type 4 thermostat resulves the heating/cooling requirement. You have DaySchedule, ON, defined in your current IDF, but only for the Summer and WinderDesignDay. You may need to re-define the schedules or add. Schedule:Compact, Summer ON, !- Name On/Off, !- Schedule Type Limits Name Through: 12/31, !- Field 1 For: Alldays, !- Field 2 Until: 24:00, !- Field 3 1; !- Field 4 There are more errors. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: natamats@xxxxxxxxx Date: Sun, 31 Jan 2010 09:15:33 -0800 Subject: Re: [EnergyPlus_Support] Need help with this idf Thank you very much for your help, you were right. I did the change and some mistakes were corrected. But it still has a few mistakes which i don t know how to correct. I am attaching the idf file and the mistakes.Please take a look.
Thank you very much, Natassa To: EnergyPlus_Support@ Sent: Sun, January 31, 2010 1:12:31 PM Subject: Re: [EnergyPlus_ Hi again I this I managed to find your error. Check the branches you used for the splitter and the mixer of the reheat. Especially check: Óôéò 31 Éáíïõáñßïõ 2010 12:55 ì.ì., ï ÷ñÞóôçò ÓùôÞñçò Ðáðáíôùíßïõ <sotos.enveng@ gmail.com> Ýãñáøå: Hello Natassa, Windows Live Messenger makes it easier to stay in touch - learn how! __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |