Re: [EnergyPlus_Support] can t get the ground heat exchanger heat transfer






Hi,but in the table it doesn t show the consumption of the system and the energy that the ground ofeers to the system and these two i definitely need.


From: YuanLu Li <yli006@xxxxxxxxxxx>
To: Linda <energyplus_support@xxxxxxxxxxxxxxx>
Sent: Sun, February 21, 2010 3:01:15 PM
Subject: RE: [EnergyPlus_Support] can t get the ground heat exchanger heat transfer

 


Hi, Natassa
 
Attached .csv is based on the first working IDF.(Feb.2)
 
The last six columns show you the heat transfer of the GHE.  Before that are the GSHP data.
 
The temperatures are not as expected for all zones.  I think you have expanded the IDF from the 3 zone model, but did not include all the controls for all zones.  One air loop for 100 over zones is not practical.  Try shutting off the reheat coils heating source during the summer days, and make sure that the air loop is using the same distrubution unit with thermostat control for each zone.
 
Heating and cooling seems to be on at the same time in the attached result.  The warning on the partitions will only affect the result of those zones listed in the error file, and not all the other zones..
 
Because I did not run the annual simulation, the table report would not show all the results, but do have the sizing information.

 Dr. Li  



 

To: EnergyPlus_Support@ yahoogroups. com
From: natamats@yahoo. com
Date: Sun, 21 Feb 2010 10:19:13 +0000
Subject: [EnergyPlus_ Support] can t get the ground heat exchanger heat transfer

 
Hello,
I have filled in the report to get me the ground heat exchanger heat transfer but it gives me in the results that it equals with 0.Can somebody tell me why is this happening and what I should do to get the heat transfer please?
Thank you,
Natassa




Live connected with Hotmail on your phone. Learn more.



__._,_.___


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___
Attachment not found:
d:\eudora\attach\withReheat coilsTable1.htm