Dear Jeannie, Perhaps you should consider reducing the number of zones and
fancoils. Generally, a zone can be as large as you desire (e.g., many
individual rooms in the core of a floor) as long as it has the same occupancy
hours, lighting density, people density, and orientation to the sun.
Small differences for lighting and people density do not influence your results
in any significant way. Similarly, E+ does not care, or produce different results, if
you assign one (very large) fan coil to the zone instead of 20 small fan coils.
For your purposes, one large fan coil and a lesser number of zones makes it
easier for you to create the model and probably reduces your run time a lot. The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of jeannieboef I've just started going through the excersize of adding
additional fancoils to a zone. __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.