We did few swimming pools here in New Zealand using bog-standard water to water heat pumps without any speciality DX pool units.

You connect chilled water circuit to a coil in exhaust air stream and use condenser water for heating the pool water, underfloor heating and supply air stream heating with gas fired condensing boiler toping-up the difference in heating load.



On 18/03/2010 04:13, James V Dirkes II, PE wrote:
 

Thanks to all who have made suggestions!  I am well along with planning, but still have some issues to work out.  The biggest issue that remains unresolved is how to model the specialty HVAC unit for the pool which uses recovered condenser energy for both reheat and pool water heating.

 

The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653

 

From: EnergyPlus_Support@yahoogroups.com [mailto:EnergyPlus_Support@yahoogroups.com] On Behalf Of Florent
Sent: Wednesday, March 17, 2010 9:17 AM
To: EnergyPlus_Support@yahoogroups.com
Subject: [EnergyPlus_Support] Re: Swimming Pool HVAC

 

 

For the thermal simulation of the actual swiming pool, I use an EMS code with the equation (1) of the ASHRAE Handbook HVAC Application 2007 chapter 4

--- In EnergyPlus_Support@yahoogroups.com, Mário <m_neves32@...> wrote:
>
> Well first of all I think the problem should be devided into two sub-problems:
> 1 - The thermal simulation of the actual swiming pool;
> 2 - The simulation of the HVAC systems neaded to ensure confort inside the actual zone.
>
> In regards to the fist problem my idea is to use a tank heater obejct to simulate the actual pool inside a thermal zone since you can place one of these objects, inside a zone, and adjust the sensible energy loss to those of a real one. Another aspect is that with a tank object you can garantie the integration of the energy neaded to heat the water an account for water loss, that would corresponde to a certan water consumption. That latent loss into the zone would have to be introduced into the zone with another object.
>
> The second aspect of the probelm I don´t have a real idea about but there might be a change to use a HeatPump object...
>
> Best regardes
>
> MN
>
> --- In EnergyPlus_Support@yahoogroups.com, "James V Dirkes II, PE" <jvd2pe@> wrote:
> >
> > It is an indoor swimming pool. I would love to hear your ideas, since I do
> > not have very many ideas about how to model this type of HVAC system.
> >
> >
> >
> > The Building Performance Team
> > James V. Dirkes II, P.E., LEED AP
> > 1631 Acacia Drive NW
> > Grand Rapids, MI 49504
> > 616 450 8653
> >
> >
> >
> > From: EnergyPlus_Support@yahoogroups.com
> > [mailto:EnergyPlus_Support@yahoogroups.com] On Behalf Of Mário
> > Sent: Saturday, March 13, 2010 4:14 PM
> > To: EnergyPlus_Support@yahoogroups.com
> > Subject: [EnergyPlus_Support] Re: Swimming Pool HVAC
> >
> >
> >
> >
> >
> >
> > Hello
> >
> > I´am intressed in this idea are you thinking of an interior swiming pool?
> > I´ve got some ideas about this.
> >
> > MN
> >
> > --- In EnergyPlus_Support@yahoogroups.com
> > <mailto:EnergyPlus_Support%40yahoogroups.com> , "jvd2pe" <jvd2pe@> wrote:
> > >
> > > Dear E+ world,
> > >
> > > Has anyone modeled one of the specialty pool HVAC air handlers which use
> > hot gas from the DX cooling coil for reheat?
> > >
> > > Willing to share your approach? or even better, a working .idf of the HVAC
> > components?
> > >
> >
>




__._,_.___


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___