Fernando, You have not connected the DX heating coil to any equipment
or AirLoop. The only heating coil you are using is the Coil:Heating:Water
object. If you want to use the DX coil and a Heat Pump, you’ll have
to use a AirLoopHVAC:UnitaryHeatPump:WaterTo Air object. This object assumes that you also use a DX coil for cooling,
so you may have some difficulty. I think that a chiller and a HeatPump
don’t normally get used at the same time. There is good and there is
evil. Love goodness. There is beauty and there is
ugliness. Love beauty. There is life and there is
death. Love life. There is love and there is
evil. Love love and hate hate. There is honesty and there is
dishonesty. Love honesty. __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.