|
Hi, I have an earthtube “exhaust”
type model. The design flow rate is 0.055556 m3/s (equivalent to 200 m3/h), the
“constant term flow coefficient” is 1 and the other 3 coefficients
are 0. The air flow schedule is 100% every day from 9.00am to 17.00pm. I look the results and I see
that the volume output is not always 200m3 for every working hour of the
simulation (i.e. from 9am to 5pm). There are cases where the volume is, for
example, 150 m3, 166.7 m3, etc. Do you know why I do not get
always 200m3 at my output? Best regards, Georgios This email has been scanned by the Altman Email Security System. For more information please visit www.altman.co.uk/emailsystems __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |