[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

RE: [EnergyPlus_Support] Question about enthalpy opening control.



Enthalpy control condition:

All of the zone's openable windows and doors are opened if Hzone > Hout and
Tzone > Tset and Venting Availability Schedule allows venting.

The Input Output Reference provides detailed information on p. 858. 

Low and high delta H are used to modulate the openness. Figure 82 on p. 861
in the same reference show how modulation works.

Lixing 

-----Original Message-----
From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of vesthetics
Sent: Tuesday, April 27, 2010 3:59 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Question about enthalpy opening control.


I wonder one thing more about Airflow Network enthalpy control.

In the AirflowNetwork:Multizone:zone

When I control the openings by enthalpy control, I can't understand delta H
= 0

Where can I set the setpoint enthalpy?

There's setpoint regarding "temperature" only. 

Is this also refers to  "Ventilation Control Zone Temperature Setpoint
Schedule" ? 

But I think this is only defining temperature, there's no humidity included.



When control the openings by delta T. it's clear. 

At first this refers to "Ventilation Control Zone Temperature Setpoint
Schedule"

If the outdoor air is lower than set point (I set 26'C), ventilation is
available. 

and then multiplier on venting open factor is multiflied based on the delta
T(indoor air temp - Outdoor air temp)

right? 



When it comes to enthalpy. 

all the process is the same, except setpoint H.

I don't know where can I set this. 

Please give me your help. 

 









------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a
high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
Documentation link and press the "search" button.
Yahoo! Groups Links







------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/