[EnergyPlus_Support] Re: Warnings
Thank you Jeannieboef for your response.
I have taken most of them are autosizing. Are you referring to the following to autoze, then this waht my configuration if Chiller:Electric:EIR looks like
Chiller:Electric:EIR,
Chiller2, !- Name
2110200, !- Reference Capacity {W}
5.0, !- Reference COP {W/W}
5, !- Reference Leaving Chilled Water Temperature {C}
32, !- Reference Entering Condenser Fluid Temperature {C}
autosize, !- Reference Chilled Water Flow Rate {m3/s}
autosize, !- Reference Condenser Water Flow Rate {m3/s}
Chiller2 CentCapFT, !- Cooling Capacity Function of Temperature Curve Name
Chiller2 CentEIRFT, !- Electric Input to Cooling Output Ratio Function of Temperature Curve Name
Chiller2 CentEIRFPLR, !- Electric Input to Cooling Output Ratio Function of Part Load Ratio Curve Name
0, !- Minimum Part Load Ratio
1, !- Maximum Part Load Ratio
1, !- Optimum Part Load Ratio
0.25, !- Minimum Unloading Ratio
Chiller2 ChW Inlet, !- Chilled Water Inlet Node Name
Chiller2 ChW Outlet, !- Chilled Water Outlet Node Name
Chiller2 Cnd Inlet, !- Condenser Inlet Node Name
Chiller2 Cnd Outlet, !- Condenser Outlet Node Name
WaterCooled, !- Condenser Type
0, !- Condenser Fan Power Ratio {W/W}
1, !- Compressor Motor Efficiency
5, !- Leaving Chilled Water Lower Temperature Limit {C}
ConstantFlow, !- Chiller Flow Mode
0, !- Design Heat Recovery Water Flow Rate {m3/s}
, !- Heat Recovery Inlet Node Name
, !- Heat Recovery Outlet Node Name
1; !- Sizing Factor
Thanks
-Ven
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "jeannieboef" <jeannieboef@...> wrote:
>
> looks like the equipment is trying to work outside of appropriate opperating conditions for the size and type selected. could you select a different size or type or is your sizing auto?
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "eplusven" <eplusven@> wrote:
> >
> > Hi All,
> >
> > I am getting the following warnigns and they are happening repeatedly. Please help, how can I fix these
> >
> > Thanks
> > -ven
> >
> > Program Version,EnergyPlus 4.0.0.024, 5/5/2010 6:24 PM,IDD_Version 4.0.0.024
> > ************* Beginning Zone Sizing Calculations
> > ** Warning ** Energy input ratio as a function of temperature curve output is not equal to 1.0
> > ** ~~~ ** (+ or - 10%) at reference conditions for Chiller:Electric:EIR= CHILLER2
> > ** ~~~ ** Curve output at reference conditions = 1.136
> > ** Warning ** Energy input ratio as a function of temperature curve output is not equal to 1.0
> > ** ~~~ ** (+ or - 10%) at reference conditions for Chiller:Electric:EIR= CHILLER3
> > ** ~~~ ** Curve output at reference conditions = 1.136
> > ** Warning ** Energy input ratio as a function of temperature curve output is not equal to 1.0
> > ** ~~~ ** (+ or - 10%) at reference conditions for Chiller:Electric:EIR= CHILLER1
> > ** ~~~ ** Curve output at reference conditions = 1.136
> > ************* Beginning System Sizing Calculations
> > ************* Beginning Plant Sizing Calculations
> > ** Warning ** In calculating the design coil UA for Coil:Cooling:Water AHU COOLING COIL
> > ** ~~~ ** no apparatus dew-point can be found for the initial entering and leaving conditions;
> > ** ~~~ ** the coil bypass factor is unrealistically large;
> > ** ~~~ ** the coil outlet design conditions will be changed to correct the problem.
> > ** ~~~ ** The initial design conditions are: Tair,in = 25.94
> > ** ~~~ ** Wair,in = 8.7981E-003
> > ** ~~~ ** Twater,in = 5.00
> > ** ~~~ ** Tair,out = 24.00
> > ** ~~~ ** Wair,out = 8.0000E-003
> > ** ~~~ ** The revised design conditions are: Tair,out = 22.26
> > ** ~~~ ** Wair,out = 8.6981E-003
> > ************* Testing Individual Branch Integrity
> > ************* All Branches passed integrity testing
> > ************* Testing Individual Supply Air Path Integrity
> > ************* All Supply Air Paths passed integrity testing
> > ************* Testing Individual Return Air Path Integrity
> > ************* All Return Air Paths passed integrity testing
> > ************* No node connection errors were found.
> > ** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at NEXTDAYSIM, 04/01 18:00 - 18:15
> > ** ~~~ ** SimFlags=[TFFFFFFF] AirLoops[T],ZoneEq[F],NonZoneEq[F],PlantLoops[F],CondLoops[F],ElecCircuits[F],PlantDemandLoops[F],CondDemandLoops[F]..F=ok,T=fail
> > ** ~~~ ** HVAC Tolerance Flags=[1000011] Enthalpy[1],MassFlow[0],HumRat[0],Pressure[0],FlowQual[0],Energy[1],Temp[1]..0=ok,1=fail
> > ** ~~~ ** HVAC Tolerance Values, Most Recent listed first
> > ** ~~~ ** HVAC EnthalpyTol=1677.584, MassFlowTol=0.000, HumRatTol=8.5924E-008, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=805987.293, TempTol=1.67
> > ** ~~~ ** HVAC side outlet node=[425 - ZONE EQUIPMENT OUTLET NODE]
> > ** ~~~ ** HVAC EnthalpyTol=1677.584, MassFlowTol=0.000, HumRatTol=8.5924E-008, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=805987.293, TempTol=1.67
> > ** ~~~ ** HVAC side outlet node=[1 - AHU SYS 1 OUTLET NODE]
> > ** ~~~ ** HVAC EnthalpyTol=1681.996, MassFlowTol=0.000, HumRatTol=8.6150E-008, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=808106.990, TempTol=1.67
> > ** ~~~ ** HVAC side outlet node=[425 - ZONE EQUIPMENT OUTLET NODE]
> > ** ~~~ ** HVAC EnthalpyTol=1681.996, MassFlowTol=0.000, HumRatTol=8.6150E-008, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=808106.990, TempTol=1.67
> > ** ~~~ ** HVAC side outlet node=[1 - AHU SYS 1 OUTLET NODE]
> > ** ~~~ ** HVAC EnthalpyTol=1686.419, MassFlowTol=0.000, HumRatTol=8.6376E-008, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=810232.262, TempTol=1.67
> > ** ~~~ ** HVAC side outlet node=[425 - ZONE EQUIPMENT OUTLET NODE]
> > ** ~~~ ** Plant Tolerance Flags=[00000000] Enthalpy[0],MassFlow[0],HumRat[0],Pressure[0],FlowQual[0],Energy[0],Temp[0],PlantFlowMassFlow[0]..0=ok,1=fail
> > ** ~~~ ** Plant Tolerance Values, Most Recent listed first
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[290 - CHILLER1 CHW DEMAND OUTLET]
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[262 - HWLFORFANCOILS HW DEMAND OUTLET]
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[285 - CHILLER1 CHW DEMAND INLET]
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[257 - HWLFORFANCOILS HW DEMAND INLET]
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[290 - CHILLER1 CHW DEMAND OUTLET]
> > ** ~~~ ** Plant Flow Tolerance Values, Most Recent listed first
> > ** ~~~ ** PlantFlowFlowTol=0.000
> > ** ~~~ ** PlantFlowFlowTol=0.000
> > ** ~~~ ** PlantFlowFlowTol=203.720
> > ** ~~~ ** PlantFlowFlowTol=0.000
> > ** ~~~ ** PlantFlowFlowTol=0.000
> > ** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at NEXTDAYSIM, 04/01 18:00 - 18:01
> > ** ~~~ ** SimFlags=[TFFFFFFF] AirLoops[T],ZoneEq[F],NonZoneEq[F],PlantLoops[F],CondLoops[F],ElecCircuits[F],PlantDemandLoops[F],CondDemandLoops[F]..F=ok,T=fail
> > ** ~~~ ** HVAC Tolerance Flags=[1000011] Enthalpy[1],MassFlow[0],HumRat[0],Pressure[0],FlowQual[0],Energy[1],Temp[1]..0=ok,1=fail
> > ** ~~~ ** HVAC Tolerance Values, Most Recent listed first
> > ** ~~~ ** HVAC EnthalpyTol=1664.041, MassFlowTol=0.000, HumRatTol=6.2533E-008, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=799499.376, TempTol=1.65
> > ** ~~~ ** HVAC side outlet node=[425 - ZONE EQUIPMENT OUTLET NODE]
> > ** ~~~ ** HVAC EnthalpyTol=1664.041, MassFlowTol=0.000, HumRatTol=6.2533E-008, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=799499.376, TempTol=1.65
> > ** ~~~ ** HVAC side outlet node=[1 - AHU SYS 1 OUTLET NODE]
> > ** ~~~ ** HVAC EnthalpyTol=1668.417, MassFlowTol=0.000, HumRatTol=6.2698E-008, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=801601.941, TempTol=1.66
> > ** ~~~ ** HVAC side outlet node=[425 - ZONE EQUIPMENT OUTLET NODE]
> > ** ~~~ ** HVAC EnthalpyTol=1668.417, MassFlowTol=0.000, HumRatTol=6.2698E-008, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=801601.941, TempTol=1.66
> > ** ~~~ ** HVAC side outlet node=[1 - AHU SYS 1 OUTLET NODE]
> > ** ~~~ ** HVAC EnthalpyTol=1672.805, MassFlowTol=0.000, HumRatTol=6.2862E-008, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=803710.036, TempTol=1.66
> > ** ~~~ ** HVAC side outlet node=[425 - ZONE EQUIPMENT OUTLET NODE]
> > ** ~~~ ** Plant Tolerance Flags=[00000000] Enthalpy[0],MassFlow[0],HumRat[0],Pressure[0],FlowQual[0],Energy[0],Temp[0],PlantFlowMassFlow[0]..0=ok,1=fail
> > ** ~~~ ** Plant Tolerance Values, Most Recent listed first
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[290 - CHILLER1 CHW DEMAND OUTLET]
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[262 - HWLFORFANCOILS HW DEMAND OUTLET]
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[285 - CHILLER1 CHW DEMAND INLET]
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[257 - HWLFORFANCOILS HW DEMAND INLET]
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[290 - CHILLER1 CHW DEMAND OUTLET]
> > ** ~~~ ** Plant Flow Tolerance Values, Most Recent listed first
> > ** ~~~ ** PlantFlowFlowTol=0.000
> > ** ~~~ ** PlantFlowFlowTol=0.000
> > ** ~~~ ** PlantFlowFlowTol=0.000
> > ** ~~~ ** PlantFlowFlowTol=0.000
> > ** ~~~ ** PlantFlowFlowTol=203.720
> > ** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC loops, at NEXTDAYSIM, 04/01 18:01 - 18:02
> > ** ~~~ ** SimFlags=[TFFFFFFF] AirLoops[T],ZoneEq[F],NonZoneEq[F],PlantLoops[F],CondLoops[F],ElecCircuits[F],PlantDemandLoops[F],CondDemandLoops[F]..F=ok,T=fail
> > ** ~~~ ** HVAC Tolerance Flags=[1000011] Enthalpy[1],MassFlow[0],HumRat[0],Pressure[0],FlowQual[0],Energy[1],Temp[1]..0=ok,1=fail
> > ** ~~~ ** HVAC Tolerance Values, Most Recent listed first
> > ** ~~~ ** HVAC EnthalpyTol=1663.649, MassFlowTol=0.000, HumRatTol=4.5510E-008, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=799325.284, TempTol=1.65
> > ** ~~~ ** HVAC side outlet node=[425 - ZONE EQUIPMENT OUTLET NODE]
> > ** ~~~ ** HVAC EnthalpyTol=1663.649, MassFlowTol=0.000, HumRatTol=4.5510E-008, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=799325.284, TempTol=1.65
> > ** ~~~ ** HVAC side outlet node=[1 - AHU SYS 1 OUTLET NODE]
> > ** ~~~ ** HVAC EnthalpyTol=1668.024, MassFlowTol=0.000, HumRatTol=4.5630E-008, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=801427.341, TempTol=1.66
> > ** ~~~ ** HVAC side outlet node=[425 - ZONE EQUIPMENT OUTLET NODE]
> > ** ~~~ ** HVAC EnthalpyTol=1668.024, MassFlowTol=0.000, HumRatTol=4.5630E-008, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=801427.341, TempTol=1.66
> > ** ~~~ ** HVAC side outlet node=[1 - AHU SYS 1 OUTLET NODE]
> > ** ~~~ ** HVAC EnthalpyTol=1672.410, MassFlowTol=0.000, HumRatTol=4.5750E-008, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=803534.926, TempTol=1.66
> > ** ~~~ ** HVAC side outlet node=[425 - ZONE EQUIPMENT OUTLET NODE]
> > ** ~~~ ** Plant Tolerance Flags=[00000000] Enthalpy[0],MassFlow[0],HumRat[0],Pressure[0],FlowQual[0],Energy[0],Temp[0],PlantFlowMassFlow[0]..0=ok,1=fail
> > ** ~~~ ** Plant Tolerance Values, Most Recent listed first
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[290 - CHILLER1 CHW DEMAND OUTLET]
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[262 - HWLFORFANCOILS HW DEMAND OUTLET]
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[285 - CHILLER1 CHW DEMAND INLET]
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[257 - HWLFORFANCOILS HW DEMAND INLET]
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[290 - CHILLER1 CHW DEMAND OUTLET]
> > ** ~~~ ** Plant Flow Tolerance Values, Most Recent listed first
> > ** ~~~ ** PlantFlowFlowTol=0.000
> > ** ~~~ ** PlantFlowFlowTol=203.720
> > ** ~~~ ** PlantFlowFlowTol=0.000
> > ** ~~~ ** PlantFlowFlowTol=0.000
> > ** ~~~ ** PlantFlowFlowTol=0.000
> >
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/