[EnergyPlus_Support] FindRootSimpleController: Controller error
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] FindRootSimpleController: Controller error
- From: "eplusven" <eplusven@xxxxxxxx>
- Date: Fri, 07 May 2010 15:36:25 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Fri, 07 May 2010 09:36:39 -0600
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=lima; t=1273246598; bh=YxeMz/yu0C2BF+WtdbYlrtRvjS2u62W0g2rYLIW6Dq0=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:User-Agent:X-Mailer:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=c5Lez0IB6DW9/g82i4/Og0v3QOF4ioaLyqKfypFHskCEoTcjapKx7hfqJlzvJ6MlAi202Oz9iRm+xNrKzqjOqtaGCHg5W+2Adg8vHFcO4iJCYWUUY9BGxag7idRZ0BiN
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=lima; d=yahoogroups.com; b=Lh6ZrUwkiqbyDO80Xg4cso100JGsBDqHA8DpAQzWNfZrTGni2cBCy/ybWB+uRnzPiZl2xbKYt8vgl1uyggm6rGsdH+oHRZgTLOdUxYsDbsX4RhEOqk/BWY4u9KWh4IJF;
- Envelope-to: linda@xxxxxxxxxxxxxx
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
Hi all,
Could you please help how do i resolve this. Actually i wanted to model AHU air supply always 24C, becasue my Fancoil units will further does cooling or heating. For this reason I set the controller as
SetpointManager:OutdoorAirReset,
Supply Air Temp Manager 1, !- Name
Temperature, !- Control Variable
24, !- Setpoint at Outdoor Low Temperature {C}
-9, !- Outdoor Low Temperature {C}
24, !- Setpoint at Outdoor High Temperature {C}
35, !- Outdoor High Temperature {C}
Supply Air Temp Nodes 1; !- Setpoint Node or NodeList Name
This si giving problem only for one month i.e May. But rest of teh months the simulation going well with lot of warnings
** Severe ** FindRootSimpleController: Controller error for controller = CENTRAL COOLING COIL CONTROLLER 1
** ~~~ ** Occurrence info=MonSIM, 05/02 06:15 - 06:30
** ~~~ ** Controller function is inconsistent with user specified controller action = Reverse action
** ~~~ ** Actuator will be set to maximum action
** ~~~ ** Controller control type=Temperature
** ~~~ ** Controller temperature set point = 11.89 [C]
** ~~~ ** Controller sensed temperature = 23.56 [C]
** ~~~ ** Controller actuator mass flow rate set to 116.44 [kg/s]
** ~~~ ** Controller actuator temperature = 24.81 [C]
** ~~~ ** Note: Chilled water coils should be reverse action and the entering chilled
** ~~~ ** water temperature (controller actuator temperature) should be below the setpoint temperature
Thanks
-Ven
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/