Yes, that is correct. Collapse all the condenser loops into one
loop. The individual towers are then on separate branches inside the supply
side splitter/mixer and get mixed before going to the one supply side outlet. From: So It would not work if I gave all of my
supply-side condenser loops the same outlet
node because each loop needs its own supply-side outlet node.
Is that correct? From: " It won’t work to connect multiple loops using some tricky
configuration. In general, nodes and connectors need to be unique across
different plant loops; you are not allowed to use splitter/mixers to cross-wire
loops. Certain types of component models do “connect” separate loops but
it is usually pretty clear from the node input fields that they are intended
for that purpose. You can use a single condenser loop to serve multiple chillers and
multiple towers. The splitter/mixer for the towers will mix cooled
condenser water before returning to the chillers. From: EnergyPlus_Support@ yahoogroups. com [mailto:
EnergyPlus_Support@ yahoogroups. com ] On
Behalf Of eddiecorwin Is is
possible to put the same connectors (connector list) on multiple loops? __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.