Emissivity is not the same as absorptance/absorptivity. Not
even close. Emissivity is measured in Far IR range (thermal radiation),
while asbortptivity is measured in Solar (UV, VIS, Near IR) range. Big
difference, since solar radiation is at approximately 5600K, while thermal
radiation is at approximately room temperature (plus/minus 40K). BTW, this is a common misconception and very often these
quantities are confused, leading some to believe that white painted surface has
low emissivity, which is not true. Unless the paint is specifically designed
to be low-emissivity (not easy), all paints have emissivity of 0.9 regardless
of color or appearance. However, shiny white paint will have very low
absorptivity, while dull black paint will have very high absorptivity. This
behavior is utilized in the design of cool roofs, where low solar absorptivity is
sought. Since all surfaces in buildings are painted, it is safe to
assume that emissivity is always 0.9, which is probably the reason that there
is no field to enter it, however this should change as we see more and more
specially designed low-e paints, even in window frames. D. Charlie Curcija From:
EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On
Behalf Of Linda Lawrie At 03:39 AM 6/2/2010, ifigeneiat wrote:
__._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |