Great schematic! I always do the same when I am modeling with E+.  Has anyone ever compiled schematics for all of the example files?  It would be EXTREMELY helpful in understanding how the systems are set up if schematics were included with the example files.  If there is no one on the E+ team that can do this, it could be crowed-sourced and done in a very short time.  Does anyone else think that HVAC system schematics for the example files would save a lot of time?Â-Eddie
From: "James V Dirkes II, PE" <jvd2pe@xxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx; "Morss, Greg" <gmorss@xxxxxxxx>
Sent: Wed, June 2, 2010 8:25:53 PM
Subject: [EnergyPlus_Support] Hospital with 100% OA and heat recovery
Â
Dear Greg,
Â
Itâ??s very possible! Iâ??m completing a model which uses the Heat Exchanger in the configuration shown on the schematic, and it is working well. My particular model does not use 100% OA, but I think all youâ??ll need to do is set up the Controller:OutdoorA ir object to have a minimum fraction which is always = 1 (something like what Iâ??ve shown below).
Â
p.s., The example files are helpful, but you have to wade through all of the node names to figure out whatâ??s connected to what. I always make a schematic to help keep them straight.
Â
Â
Â
Â
Controller:OutdoorA ir
Name
OAController_ Aquatics
Relief Air Outlet Node Name
NodeOut_EA_Aquatics
Return Air Node Name
NodeIn_RA_Aquatics
Mixed Air Node Name
NodeOut_MA_Aquatics
Actuator Node Name
NodeIn_OA_Aquatics
Minimum Outdoor Air Flow Rate
2.50132
Maximum Outdoor Air Flow Rate
13.21452
Economizer Control Type
FixedDryBulb
Economizer Control Action Type
ModulateFlow
Economizer Maximum Limit Dry-Bulb Temp (C)
29.4
Economizer Maximum Limit Enthalpy (J/kg)
82939
Economizer Maximum Limit Dewpoint Temp (C)
MT
Electronic Enthalpy Limit Curve Name
MT
Economizer Minimum Limit Dry-Bulb Temp (C)
-40
Lockout Type
NoLockout
Minimum Limit Type
FixedMinimum
Minimum Outdoor Air Schedule Name
Minimum Fraction of Outdoor Air Schedule Name
SchCpct_AlwaysOn
Maximum Fraction of Outdoor Air Schedule Name
SchCpct_AlwaysOn
Mechanical Ventilation Controller Name
Time of Day Economizer Control Schedule Name
High Humidity Control
Humidistat Control Zone Name
High Humidity Outdoor Air Flow Ratio
Control High Indoor Humidity Based on Outdoor Humidity Ratio
Heat Recovery Bypass Control Type
Â
Â
Â
It is contradictory to insist that future generations respect the natural environment when our educational systems and laws do not help them to respect themselves. (Let's do both.)
Â