[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] CollingCoil:DX inputs





What is the autosized value for Rated Air Flow Rate? Compare that number to these and you will answer your own question.

Vinay Devanathan wrote:
 

Mr. Raustad,

I obtained 11.1 tons as the Cooling Capacity on auto-sizing. But, the air flow rate used for that cooling capacity (obtained from the HVACSizing for Cooling) is only 2110 cfm. In that case, am I doing anything wrong with the model? or is it usual?

At the same time, the air flow rate (obtained from the HVACSizing for Heating) is around 3910 cfm.

Could you please tell me what is right.

Thank you very much.

Regards,
Vinay

On Thu, Jul 8, 2010 at 12:06 PM, Richard Raustad <RRaustad@fsec.ucf.edu> wrote:
Enter the flow rate that was used for the Rated Cooling Capacity. For
example, for a 10-ton air conditioner (the Rated Cooling Capacity), the
air flow rate would be around 4000 cfm (400 cfm/ton).

Vinay Devanathan wrote:
>
> Hello All,
>
> While I auto-size a run period and obtain values from that simulation
> and plug it into the simulation next time, I come across a situation
> which I would like to clarify.
> I auto-size and obtain the values of Rated Cooling Capacity. And the
> problem I am facing is in inputting the Rated Air Flow Rate. What
> value should go in this field? Is it the max. air flow rate or the air
> flow rate that satisfies the cooling load? When I use the air flow
> rate that satisfies cooling load, I see that the Rate Vol Flow rate
> (m3/s) per Watt of the Rated Cooling Capacity is less than the minimum
> specified in the I/O reference (0.000040).
>
> Any help would be great.
>
> Thank you.
>
> Regards,
> Vinay
>
>

--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@gard.com

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
   http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
   Individual Email | Traditional

<*> To change settings online go to:
   http://groups.yahoo.com/group/EnergyPlus_Support/join
   (Yahoo! ID required)

<*> To change settings via email:
   EnergyPlus_Support-digest@yahoogroups.com
   EnergyPlus_Support-fullfeatured@yahoogroups.com

<*> To unsubscribe from this group, send an email to:
   EnergyPlus_Support-unsubscribe@yahoogroups.com

<*> Your use of Yahoo! Groups is subject to:
   http://docs.yahoo.com/info/terms/



-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___