[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Equipment Capacity Problem



The example files are meant to help you understand the specific object 
requirements for assembling and using that object in E+. In most cases, 
the example files represent "good practice" design. However, there are 
still some example files that simply show the input requirements and 
connection scheme. You are correct, the AC system is over-sized. I also 
recall that it is critical that the inputs to the parameter estimate 
model be correct for a given size AC and GLHE. So be careful to 
correctly size this system's components when changing inputs to this model.

O. Tugrul Karaguzel wrote:
>
> Hi guys,
> I was analyzing energy Plus sample model (named as GSHP-GLHE.idf) for 
> Ground Source Heat Pumps, and I realized that this model has 
> HeatPump:WaterToWater:Parameter:Estimation:Heating and Cooling 
> equipments with nominal capacities of 50,000 and 45,000 W, 
> respectively. I also checked sample building's design heating and 
> cooling loads which were about 14,000 and 16,000 W respectively (these 
> are loads calculated using a sizing factor of 1.2).
> How come does a GSHP equipment have a nominal capacity which about 3.5 
> times greater than design heating load of a building? Isn't this 
> equipment significantly over-sized? or is there any other explanation 
> for such a relationship between loads and system capacities?
> Thanks.
> Omer T. Karaguzel PhD Candidate
> Center for Building Performance & Diagnostics (CBPD)
> Carnegie Mellon University
> Pittsburgh U.S.A.
>
>
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/