Airflow for a DX cooling coil has a typical range. System efficiency and
performance is impacted at both ends of the range. If the air flow is
too low, the coil can freeze. If the air flow is too high, there is a
high pressure drop. The typical range is 0.00004027 - 0.00006041 m3/s/W
(300 - 450 cfm/ton). These are the "rated" air flow rates. However, the
operating flow rate is allowed to fall to 0.00002684 m3/2/W (200
cfm/ton) during the simulation. This lower range is sometimes used for
systems with very good dehumidification performance. This is range that
manufacturers typically provide for their systems. In addition, the DX
cooling coil model has been tested within this range and without data to
verify performance, the model accuracy may be compromised when operating
outside this range.
Abdul Murad Zainal Abidin wrote:
>
> Hello,
>
> In the EnergyPlus input output reference, there is this statement: The
> rated air volume flow rate should be between .00004027 m3/s and
> .00006041 m3/s per watt of rated total cooling capacity (300 to 450
> cfm/ton).
>
> Is this a rule-of-thumb based on a certain guideline? Where are these
> figures derived from?
>
> Thank you.
>
> Murad
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/