Dear Matt, It looks like you’ve got inappropriate off cycle losses
(100% in two locations) and no schedule for water use. I’ve attached a new version of your IDF with two new
objects (a Water Heater:Mixed and a Compact Schedule for water use) that work
properly. I think I grabbed the water use fractions from ASHRAE 90.1’s
User Manual. The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of matt youngblood
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.