Re: [EnergyPlus_Support] Coil:Heating:DX:SingleSpeed in AirLoop
The Coil:Heating:DX:SingleSpeed objet can only be used in an
AirloopHVAC:UnitaryHeatPump:airToAir object. But you should be able to
place the Coil:Heating:Desuperheater object upstream of the heat pump.
Use a SetPointManager:SingleZone:Heating object to control the
desuperheater so the DX cooling coil and desuperheater to not fight each
other. The heat pump DX heating coil should turn on when the
desuperheater can not meet the entire heating load.
Xavier Garcia Casals wrote:
>
> Although the I/O reference doesn't state it, it seems that the
> Coil:Heating:DX:SingleSpeed can not be implemented in an AirLoop
> outside of the AirLoopHVAC:UnigtaryHeatPump:AirToAir object (error:
> Invalid Air Loop Component Type = "COIL:HEATING:DX:SINGLESPEED"). Is
> it right that the Coil:Heating:DX:SingleSpeed can only be used within
> the AirLoopHVAC:UnigtaryHeatPump:AirToAir? If so, is there a
> fundamental reason for this restriction?
> I was trying to combine the Coil:Heating:DX:SingleSpeed with a
> AirLoopHVAC:UnitaryCoolOnly in order to be able to have the
> Coil:Heating:DX:SingleSpeed downstream of a Coil:Heating:Desuperheater
> to recover waste heat from a compressor rack (the
> Coil:Heating:Desuperheater can not be implemented into a
> AirLoopHVAC:UnigtaryHeatPump:AirToAir). Is there a way to combine the
> Coil:Heating:Desuperheater and Coil:Heating:DX:SingleSpeed in the same
> AirLoop?
> Thanks,
>
> --
> * *
> *Xavier García Casals*
>
> Tel: (+34) 91 843 19 85
> Móvil: 660 22 94 45
> xgcasals@xxxxxxxxxxxxxx <mailto:xgcasals@xxxxxxxxxxxxxx>
>
> * *
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/