[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

RE: [EnergyPlus_Support] Controlling Heating Discharge Temperature



Well this situation is a little more complex, because this is a direct fired gas heater.  The air flow remains constant, but I have data showing that the unit can't heat to the rated capacity.  If I mess with efficiency (don't know where to poke to change it anyway, the field equipment derating is not constant but varies with outdoor temperature) I loose total gas used and no longer have a simple relationship for added moisture. 

Ned Lyon, P.E. (MA)
Staff Consultant

Simpson Gumpertz & Heger
781.907.9000 main
781.907.9350 direct
781.907.9009 fax
www.sgh.com
-----Original Message-----
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Richard Raustad
Sent: Monday, August 23, 2010 5:15 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] Controlling Heating Discharge Temperature

To answer your question, the sensible load request is independent of 
equipment efficiency. But shouldn't you be changing the equipment 
performance to match what you see in the field instead of modifying the 
load to be met? If you reduce the load on a "non-defective" equipment 
model, the equipment PLR will be reduced and you will not get what you 
are finding in the field. If you are not getting the rated heating 
capacity in the field, lower the capacity while holding the energy use 
of the equipment at the rated energy use (i.e., lowering the efficiency 
while reducing the capacity will give the same energy use of the rated 
equipment while simulating a loss of capacity).

Edward G. Lyon wrote:
>
> Ok, so what I have to do is calculate my own load and apply that as a 
> "Sensible Load Request" to a "Unitary HVAC" object. This reduces 
> heating and lowers the supply air temperature so I can simulate the 
> defective operation of the field equipment I am looking at. The 
> question now is does this "Sensible Load Request" include or exclude 
> the efficiency of the equipment?
>
> *Ned Lyon, P.E. (MA)**
> *Staff Consultant
>
> *SIMPSON GUMPERTZ & HEGER** *
> 781.907.9000 main
> 781.907.9350 direct
> 781.907.9009 fax
> www.sgh.com
>
> *From:* EnergyPlus_Support@xxxxxxxxxxxxxxx 
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] *On Behalf Of *Don Shirey
> *Sent:* Monday, August 23, 2010 2:51 PM
> *To:* EnergyPlus_Support@xxxxxxxxxxxxxxx
> *Subject:* Re: [EnergyPlus_Support] Controlling Heating Discharge 
> Temperature
>
> This object is controlled by the thermostat setpoint and the 
> calculated cooling/heating load for the control zone .... a setpoint 
> manager is not used to control its operation.
>
>
> Edward G. Lyon wrote:
>
>     I'm trying to control the heating discharge temperature of a
>     Unitary:Furnace:HeatOnly. I'm having a hard time identifying the
>     right node to control. I assume that it should be the Air Loop
>     Outlet Node, but that does not seem to be working. Could it be the
>     Zone Equipment Inlet Node?
>
>     *Ned Lyon, P.E. (MA)**
>     *Staff Consultant
>
>     *SIMPSON GUMPERTZ & HEGER*
>     *|* Engineering of Structures and Building Enclosures
>
>     41 Seyon Street, Bldg. 1, Suite 500
>     Waltham, MA 02453
>
>
>     781.907.9000 main
>     781.907.9350 direct
>     781.907.9009 fax
>     www.sgh.com <http://www.sgh.com>
>
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links





------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/