All,
I tried to run a parametric run -- in M$-Windows this time. What I want
to do is to change the material so that it will have different values of
thermal mass. The snippet is as follows:
*********************
Material,M01,MediumRough,0.1016,0.89,1920,790;
Material,M02,MediumRough,0.1524,0.49,512,880;
Material,M03,MediumRough,0.2032,0.5,464,880;
Parametric:SetValueForRun,
$floorMaterial, !- Parameter Name
M01, !- Value for run 1
M02, !- Value for run 2
M03; !- Value for run 3
Construction,
Mass Floor, !- Name
=$floorMaterial; !- Layer 3
*********************
If I run that, the simulation will stop after the parametric
preprocessor with a pop-up window that says:
"No runs are enabled in the parametric input file"
Of course, the error message is wrong. There are parametric runs defined.
Solution: Just move the material objects below the parametric object.
The simulations will then run smoothly.
I would never have guessed that this is the solution because the manual
says that the order of parametric objects (as with the other objects in
EnergyPlus) is not important. Any object can be located anywhere in the
IDF file.
Nope, as it turns out, not in the case of parametric runs. Bug?
Cheers,
Ery
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/