[EnergyPlus_Support] Re: ASHRAE Compliant Fans and Pumps



Thank you Mr Dirkes,

I really appreciate your help and your time investment for a good reply. You've cleared some issues for me...and cleared my head a bit. 

1) Like you say, one can set schedules to OFF for both cases, but that's exactly why the criteria for unmet load hours is there.

2) The baseline case must meet 62.1 Ventilation minimums (I didn't know that)

Based on this I think I will use the autosized (with factor 1.25 for heating and 1.15 for cooling) supply air maximums from eplus to use in the ASHRAE fan power calculations as the input for supply air. Then I've met 62.1 and the heating and cooling loads. This should ensure keeping unmet load hours to a minimum, if not zero.

Regards,

Jean

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "James V Dirkes II, PE" <jvd2pe@...> wrote:
>
> Dear Jeannie,
> 
>  
> 
> First, a qualifier: I am not familiar with modeling of naturally ventilated
> buildings, so what I say below is my opinion based on what I know about
> mechanically ventilated systems and may need more research. (That means YOU
> may be more knowledgeable than I!)
> 
>  
> 
> Second, a few thoughts:
> 
> .         The baseline system is "imaginary".  It is used as an efficiency
> reference and I suspect that it was not envisioned by its ASHRAE authors to
> be a reference for a non-mechanical comfort control system. 
> 
> .         Baseline systems share a few common aspects with the "real"
> (proposed) system.  These common aspects include schedules for occupancy,
> lighting and equipment.  They also include operating setpoints for comfort.
> 
> .         You do not need to turn on a baseline cooling or heating system.
> For example the Availability Schedule for the chiller or cooling coil could
> be "OFF" continuously.  If it is "OFF" for the Baseline, though, the
> identical schedule must be used for the Proposed system.
> 
> .         Similarly, I think that you are not required to maintain the
> building within, say, the ASHRAE comfort window, but the control setpoints
> must be identical for Baseline and Proposed models.  Of course, the design
> engineer's responsibility is to make sure the client's comfort requirements
> are met (whatever they may be).  This means that you can, for example,
> define the cooling setpoint at 40C for both systems, resulting in the
> cooling system never operating.
> 
> .         You ARE required to meet the ventilation minimums of ASHRAE 62.1.
> That's fairly easily done for mechanically ventilated systems; I trust that
> you have a good idea how to model and verify it for a naturally ventilated
> system!
> 
>  
> 
> So far, I have not addressed your question about fan power! I wanted to "set
> the stage" a bit, though.  Now on to fan power:
> 
> .         I think that every Baseline system's fans should be defined with
> reasonable fan efficiency and pressure rise.  The definition for
> "reasonable" is not provided anywhere in ASHRAE 90.1.  My own definition is
> that I will be able to confidently explain and defend my choices in front of
> a group of my peers.
> 
> .         In addition, as defined by 90.1 the fan system Delta T must be 20F
> / 11.1C (as mentioned in an earlier post)
> 
> .         Your (autosized) Baseline fan system probably provides both
> ventilation air and space heating. Depending on the amount of heating that
> is required, the flow rate may still be the same as the ventilation amount.
> Regardless, it's "autosized" and autosizing accounts for minimum
> ventilation, heating and cooling loads, uses the 20F delta T and also uses
> "reasonable" fan efficiency and Delta P.  The purpose of Baseline autosizing
> in the Standard is (I think) to minimize the "game-playing" and make sure a
> Baseline represents a fairly constant standard.
> 
> .         I'm not quite sure what you mean by "These air flow rates
> obviously don't also meet the heating and cooling loads." .  A Baseline
> system MUST meet the heating and cooling loads defined by your heating and
> cooling setpoints.  So must the Proposed system.  Both systems must meet the
> "unmet load hours" requirements in G3.1.2.2.
> 
> .         The Proposed fan system does not need to meet the heating loads on
> its own if the radiant floor provides enough heat to maintain the heating
> setpoint.  Similarly, the Proposed fans should not use the efficiencies and
> unloading coefficients specified for Baseline systems; they should use the
> actual efficiency and unloading coefficients.
> 
>  
> 
> E-mail discussion are difficult!  Nonetheless, I hope I've helped.
> 
>  
> 
> Here's a summary:
> 
> BOTH BASELINE and PROPOESED:
> 
> .         Identical schedules for occupancy, lighting and equipment.
> 
> .         Identical comfort setpoints
> 
> .         Identical ventilation minimum requirements
> 
>  
> 
> BASELINE:
> 
> .         Autosized for 62.1 ventilation, 20F delta T, "reasonable"
> efficiency and delta P,  and providing all heating and cooling loads
> 
>  
> 
> PROPOSED:
> 
> .         Assure 62.1 ventilation minimums are met (however that's done for
> naturally ventilated systems)
> 
> .         Actual efficiency, delta P and delta T for all fans and pumps
> 
>  
> 
> The Building Performance Team
> James V. Dirkes II, P.E., LEED AP
> 1631 Acacia Drive NW
> Grand Rapids, MI 49504
> 616 450 8653
> 
>  
> 
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of jeannieboef
> Sent: Monday, September 06, 2010 6:27 AM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Re: ASHRAE Compliant Fans and Pumps
> 
>  
> 
>   
> 
> Dear Mr. Dirkes,
> 
> I'm modelling a building with ventilation purely for ASHRAE 90.1 code
> compliance as it is in reallity 100% Naturally ventilated with just heating
> (radiant floor). As you know the mechanical system takes the shape of the
> baseline model which I gave as design supply air flow rates as per the
> minimum rates outdoor air rates of ASHRAE 62.1. These air flow rates
> obviously don't also meet the heating and cooling loads when all the heating
> and cooling loads are met with the AHU systems, meaning that e+ has sized
> the needed air flows and fan flow rates larger than the fan flow rates that
> I have thus far used in the fan power calculation as per ASHRAE G3.1.2.5 &
> G3.1.2.8.
> 
> I'm busy assigning deltaP to achieve the desired fan powers given in by the
> ASHRAE fan power calcualtion in e+, and wanted to ask your oppinion if this
> methodology is correct. Because the input in the fan power calculation uses
> the air flow purely for minimum outdoor air rates and not also to meet the
> heating cooling load.
> 
> I've not found anything in Appendix G that would make me think that I
> couldn't make the design air flow rate for the fan power calculation ZERO.
> E+ would still calcualte the larger rate to meet heating and cooling loads,
> but I could leave all my fan deltaPs at zero.
> 
> What is the best approach here? What should I use for design Air Flow Rates
> for the baseline building (as the naturally ventilated proposed design
> building doesn't have any requirement)?
> 
> Regards,
> 
> Jean.
> 
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com> , "James V Dirkes II, PE"
> <jvd2pe@> wrote:
> >
> > Dear Vinay,
> > 
> > 
> > 
> > While .6 fan efficiency is within normal range, the goal is to define a
> > combination of fan efficiency and pressure rise which results in the
> > acceptable fan power. You start with known air flow, make a reasonable
> > estimate of fan efficiency and then derive the pressure rise.
> > 
> > 
> > 
> > For a "Proposed" system, the derivation is not needed; you use the actual
> > fan and motor efficiencies, actual airflow and actual pressure rise.
> > 
> > 
> > 
> > For your information (just in case it's helpful), the derivation of fan
> > power is shown below in IP units.
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > The Building Performance Team
> > James V. Dirkes II, P.E., LEED AP
> > 1631 Acacia Drive NW
> > Grand Rapids, MI 49504
> > 616 450 8653
> > 
> > 
> > 
> > From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com> 
> > [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com> ] On Behalf Of Vinay
> Devanathan
> > Sent: Wednesday, July 07, 2010 9:32 PM
> > To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com> 
> > Subject: Re: [EnergyPlus_Support] ASHRAE Compliant Fans and Pumps
> > 
> > 
> > 
> > 
> > 
> > Mr. Dirkes,
> > 
> > 
> > 
> > Thanks for your reply. So, is 0.6 Fan Efficiency (including motor
> > efficiency) acceptable? or does it depend on any other variable? I am
> > assuming there are no set specifics for Fan Efficiency value. So, with
> this
> > procedure, we can calculate Fan Power from Appendix G formula and adjust
> > Pressure difference. Am I right on this?
> > 
> > 
> > Thank you.
> > 
> > Regards,
> > 
> > Vinay
> > 
> > 
> > 
> > On Wed, Jul 7, 2010 at 9:25 PM, James V Dirkes II, PE <jvd2pe@>
> > wrote:
> > 
> > 
> > 
> > Dear Vinay,
> > 
> > 
> > 
> > ASHRAE 90.1-2007 specifies Baseline system fan power in Table G3.1.2.9.
> For
> > VAV systems, also use Table G3.1.3.15 for part load performance. A sample
> > object for the VAV fan is shown below.
> > 
> > 
> > 
> > For all baseline fans, I made a spreadsheet which, based on anticipated
> > motor and fan efficiency, calculates the pressure rise which will result
> in
> > the correct ASHRAE 90.1 fan power. Remember that E+, when asking for "fan
> > efficiency", really wants (Fan mechanical efficiency x Motor efficiency).
> > For example, if the fan mechanical efficiency = .60 and motor efficiency =
> > .90, the E+ "fan efficiency" = .54.
> > 
> > 
> > 
> > 
> > 
> > 
> > Fan:VariableVolume
> > 
> > 
> > Name
> > 
> > SFan_MainBldg
> > 
> > 
> > Availability Schedule Name
> > 
> > SchCpct_FanOpern
> > 
> > 
> > Fan Efficiency (incl. motor)
> > 
> > 0.6
> > 
> > 
> > Pressure Rise (Pa)
> > 
> > 498
> > 
> > 
> > Maximum Flow Rate
> > 
> > Autosize
> > 
> > 
> > Minimum Flow Rate
> > 
> > 0
> > 
> > 
> > Motor Efficiency
> > 
> > MT
> > 
> > 
> > Motor In Airstream Fraction
> > 
> > 1
> > 
> > 
> > Fan Coefficient 1
> > 
> > 0.0013
> > 
> > 
> > Fan Coefficient 2
> > 
> > 0.147
> > 
> > 
> > Fan Coefficient 3
> > 
> > 0.9506
> > 
> > 
> > Fan Coefficient 4
> > 
> > -0.0988
> > 
> > 
> > Fan Coefficient 5
> > 
> > 0
> > 
> > 
> > Air Inlet Node Name
> > 
> > NodeOut_ClgCoilAir_MainBldg
> > 
> > 
> > Air Outlet Node Name
> > 
> > NodeOut_SFan_MainBldg
> > 
> > 
> > End-Use Subcategory
> > 
> > 
> > 
> > 
> > 
> > 
> > 
> > The Building Performance Team
> > James V. Dirkes II, P.E., LEED AP
> > 1631 Acacia Drive NW
> > Grand Rapids, MI 49504
> > 616 450 8653
> > 
> > 
> > 
> > From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com> 
> > [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com> ] On Behalf Of Vinay
> Devanathan
> > Sent: Wednesday, July 07, 2010 5:53 PM
> > 
> > 
> > To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com> 
> > 
> > Subject: Re: [EnergyPlus_Support] ASHRAE Compliant Fans and Pumps
> > 
> > 
> > 
> > 
> > 
> > Alan,
> > 
> > In regards to your reply,
> > 
> > Does ASHRAE specify any efficiency value for the fans? If yes, could you
> > please direct me to the same.
> > 
> > Thank you.
> > 
> > Regards,
> > Vinay
> > 
> > On Tue, Jun 29, 2010 at 11:33 AM, Jackson, Alan <ajackson@>
> > wrote:
> > 
> > 
> > 
> > You're going to want to adjust your Static Pressure DeltaP. Once you
> > have your Watts for the Baseline from auto sizing the flow you can use
> > DeltaP[Pa] = Power[W]*Eff/Flow[m3/s]
> > 
> > Since ASHRAE is telling you Flow and Power you have to solve for static.
> > 
> > Alan Jackson, LEED AP
> > KlingStubbins
> > 
> > 
> > 
> > -----Original Message-----
> > From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com> 
> > <mailto:EnergyPlus_Support%40yahoogroups.com> 
> > [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com> 
> > <mailto:EnergyPlus_Support%40yahoogroups.com> ] On Behalf Of eddiecorwin
> > Sent: Tuesday, June 29, 2010 11:13 AM
> > To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com> 
> > <mailto:EnergyPlus_Support%40yahoogroups.com> 
> > Subject: [EnergyPlus_Support] ASHRAE Compliant Fans and Pumps
> > 
> > I am curious as to how people have gone about modeling ASHRAE compliant
> > pumps and fans. 
> > 
> > The pumps seem relatively strait forward, run the model, see what the
> > flow is, then enter in a wattage that equates to 22W/GPM. The fans,
> > however, do not have an input for the rated wattage. The only option I
> > see is to alter the fan's Motor Efficiency until you get close to the
> > correct W/CFM. 
> > 
> > Are these the same methods people have applied in the past, or is there
> > a better way to the the correct W/GPM and W/CFM?
> > 
> > ------------------------------------
> > 
> > 
> > 
> > Primary EnergyPlus support is found at:
> > http://energyplus.helpserve.com or send a message to
> > energyplus-support@ <mailto:energyplus-support%40gard.com> 
> > 
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> > 
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> > 
> > Attachments are currently allowed but be mindful that not everyone has a
> > high speed connection. Limit attachments to small files.
> > 
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under
> > the Documentation link and press the "search" button.
> > 
> > Yahoo! Groups Links
> >
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/